Axial Fans

06/18/2009 2:09 AM

Dear sirs i have a questiion regarding how to operate an axil fan direct on line in reating 0.5kva though a cable (4x6) cu/xlpe/pvc is it will work though a disconnect switch or through mcb with over load device or contactor with over load

i was toled that it will work through some thing caled fan starter.

waiting to your answers.

regards

__________________
wafaa
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: May 2009
Location: Centurion, South Africa
Posts: 87
Good Answers: 5
#1

Re: OPERATING OF AXIAL FAN

06/18/2009 2:59 AM

You may start and operate the motor via various electrical equipment, such as: Variable speed drive (vsd), soft starter (ss) and a direct on line starter (DOL)

On each of these units you will have to install a main circuit breaker (mcb) to protect the starter (vsd,ss or dol).The vsd option you will use if you want to vary the speed of the motor/fan (increase or decrease the air flow). The ss option will be used if you want to limit mechanical stress on the driven equipment and also limit the start up current to acceptable limits.

The dol starter (what you refer to as fan starter) may be used when no speed control or current limit are required (normally beter priced than the other 2 options). The dol (integral part of vsd and ss) should have an overload relay (sized according to the full load current of the motor) to protect the motor.

__________________
R T F M .......
Register to Reply
Anonymous Poster
#2
In reply to #1

Re: OPERATING OF AXIAL FAN

06/18/2009 3:09 AM

In fact i will use the direct on line while it is simple fan for ventilation but i asking about how i will connect this fan in this case am i use mcb with over load or contactor with overload my bose say a contactor with over load.

regards

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: OPERATING OF AXIAL FAN

06/18/2009 3:10 AM

<...a contactor with over load...>

...is correct.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Jan 2008
Location: Egypt-Cairo
Posts: 17
#4
In reply to #3

Re: OPERATING OF AXIAL FAN

06/18/2009 3:23 AM

i appreciate if leading me to how to select the contactor rating is it right to be 1.25 of the rated current.

i=.5*1000/.8*380*1.72

i=0.95 a

so i of contactor =1.18

what is its rating in this case

__________________
wafaa
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: OPERATING OF AXIAL FAN

06/18/2009 3:40 AM

Open a dialogue with the suppliers.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#6

Re: OPERATING OF AXIAL FAN

06/18/2009 7:30 AM

You may try to read this article,

http://www.sea.siemens.com/step/pdfs/cc_3.pdf

or

http://www.pacificcoastbreaker.com/files/Moeller%20contactor%20selection%20catalog.pdf

But the advise is always, do not do it unless you are competent of course you are working on a low load only 0.5KVA but check up with the service man and then only go ahead.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches