Starting Current for Star Delta and DOL Starter

06/19/2009 2:47 AM

Can anyone tell me how to calculate starting current for the loads which has star delta starter & Dol starter.

I have to calculate current to put a circuit breaker for a load of 4kW which has DOL starter and current to put a circuit breaker for a load of 12kW with star delta starter.

In usual practice for a load of 12kW without starter, 3phase we calculate the current as below,

I=Power in kW/(sqrt of 3 x voltage x power factor)

I=12/(1.732 x 415 x 0.80)

I=21A

Kindly let me know the current with starters.

__________________
Thanks, Mago
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#1

Re: starting current for star delta & DOL starter

06/19/2009 4:28 AM

As standard in motor starting current, the DOL starter will start the motor with 7.5 time of the rated motor full load current or FLC. Where, the Star Delta Starter will start the motor with 1/3 of the motor full load current of that DOL starter.

For 4 KW motor with DOL motor starter, your starting current is 49.1 Amp and your running current is 6.547 Amp. MCB or MCCB will be 15 Amp at 35KA.

For the Star Delta of 12KW motor, the starting current is about 52.17 Amp (1/3 of the motor with DOL) and your running current is 20.868 Amp. MCB or MCCB will be 35 Amp / 35KA

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Anonymous Poster
#10
In reply to #1

pl complete the monkey story

07/10/2010 11:52 PM

pl complete the monkey story, pl........

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #1

Re: starting current for star delta & DOL starter

08/14/2024 5:43 AM

<...MCB or MCCB will be 15 Amp at 35KA...MCB or MCCB will be 35 Amp / 35KA...>

The rating of the circuit protection device, the ambient temperature, the circuit conductor size and the method of installation of the proposed cables are interrelated under BS7671, and nothing has been stated about the cables in this thread!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Feb 2008
Posts: 59
#2

Re: starting current for star delta & DOL starter

06/19/2009 5:10 AM

Hello mago,

I would get a circuit breaker for the current in the 12 kw load. If you have a Wye Delta starter you will soft start your load (btw is it a motor?) so the current draw won't be as high as with a DOL unit. Size your breaker for the normal load (most CB's have a time element anyway for LRA). For your DOL unit the LRA (locked rotor amps) is your starting current, you should find it on the data plate if it's a motor. Again it's very short time duration so most CB's won't see it. I calculate your 12kw current at:

I = 12000/415 x sq rt 3 or 16.69 amps (3 phase pwr = I x V x sq rt 3). Since the load is in kilowatts the pf is already considered (KW = KVA X pf). Good luck.

hughes838

Register to Reply
Member
Philippines - Member - New Member

Join Date: May 2009
Posts: 6
#3

Re: Starting Current for Star Delta and DOL Starter

06/21/2009 2:43 PM

Any motor as far as I know will depend on the type of lock rotor where the starting current be calculated it is found in every nameplate and depend whether it is an induction squirel cage or wound rotor type:

a) Induction squirel cage type rotor: 250%-300% of FLA as per NEC and NEMA Standard on Code Letter

b) Wound rotor type rotor : 125%-250% of FLA as per NEC and NEMA Standard on Code Letter

This is where your starting current based intended for Circuit breaker is calculated and the interrupting capacity depend on the type of load continuos or intermitent duty.

Register to Reply
Power-User

Join Date: May 2008
Location: San Jose, CA, USA
Posts: 121
Good Answers: 2
#4

Re: Starting Current for Star Delta and DOL Starter

06/22/2009 1:16 PM

Under normal feed ( 415V delta) the nominal (rated) current has been given as 21A, with a starting current of (assume) 600%, that is 126A.

When starting in star (Y, wye), the current is 1/3, thus 7A and the starting current (assumed also 600%) will be 42A.

Since under normal start (delta) the breaker shall withstand the starting process (select 60A for a short-time start with 126A), in the case of a star start you can select 30A. Be careful that after the starting period you have to reverse the connection from start to delta thus 21A(I assume the motor has been manufactured for delta operation), otherwise the torque will be also only 33% of the rated torque.

Please see also for additional clarifications

http://library.abb.com/global/scot/scot235.nsf/veritydisplay/b065a29b8762f021ca2574bc0024c057/$File/1VGA677022%20-%20ZVC-SD%20Star%20Delta%20Motor%20Starter.pdf

__________________
Scientes et audaces fortuna juvat !
Register to Reply
Member
Philippines - Member - New Member

Join Date: May 2009
Posts: 6
#5
In reply to #4

Re: Starting Current for Star Delta and DOL Starter

06/22/2009 4:55 PM

Dear Mr. Tomad,

The principle of 3phase in star connection the rated ampere is 21A since it is already along the line current (DOL) only the voltage is reduce 415V/sqrt 3=240V per phase but in delta the voltage (DOL) 415V the current is reduce per phase( I = I rated /sqrt 3) 21A/sqrt 3 = 12.12A( assume of power factor of 80%). The starting current are based on the lock rotor type of motor that this size of motor is of wound type with High torque. Or to proved what you are trying to convey why dont you experiment in your own way or simulate the same. To see is to believe, lucky are those who can't see but can visualize.

Thank you.

Register to Reply
Anonymous Poster
#6

Re: Starting Current for Star Delta and DOL Starter

06/23/2009 2:24 AM

hi friends,

you required the imformation about the starting current.

your calculation is right for resistive connected load. but if load is not purly resistive then we have to go with different calculation.

for example if load is inductive and capacitive then we have to calculate initial current with the help of transient analysis with intial theorem.

for load of motor we have to calculate different way, because induction motor take intial starting current more than 5 to 7 time it's rated value.

so friend starting current is depend on load, according to connected load its vary so which kind of load you connected according to that we can calculate the starting current.

Register to Reply
Anonymous Poster
#7

STARTING MOTOR WITHOUT STAR DELTAL STARTER

03/22/2010 4:32 AM

ON URGENT BASIS ,I WANT TO START A SUBMERSIBLE PUMP OF CAPACITY 50KW WITHOUT STARTER IS IT POSSIBLE?

ANY IDEAS TO START IT?

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8
In reply to #7

Re: STARTING MOTOR WITHOUT STAR DELTAL STARTER

03/22/2010 2:23 PM

YOU WANT TO START IT WITHOUT A STARTER, AND YOU WANT TO KNOW HOW TO START IT????

First learn to type without the Caps Lock key on, it makes your post difficult to read. Humans read words not only by the letters but by the shapes. Using all caps forces us to slow down and read each letter individually. I get bored easily.

A "Starter" is a device for starting, stopping and protecting a motor. How would you start it without starting it? Would you connect the wires to it while they are live? Good luck with that and make sure your wife knows where to find the money stash when you are dead.

If you would plan on using a manual switch to disconnect the motor and turn it on when needed, that essentially becomes part of a "starter", albeit manual. But that does nothing to protect it.

You could add fuses as protection, but unless you get the absolute perfect fuse, you are going to find it difficult to provide adequate protection AND the ability to avoid nuisance clearing of the fuse from the high starting current of an AC motor. The same would hold true for a circuit breaker.

So now if you increase the breaker or fuse size to allow starting without nuisance clearing, then you are too high to protect the windings of the motor.

So if you then add a Motor Overload Relay, it will provide the proper running protection for the motor as well.

But an Overload Relay is not a disconnecting device, and cannot be easily tied into a disconnect or circuit breaker without special trip release mechanisms. So if you add these special trip release mechanisms to a circuit breaker or disconnect switch, guess what you have?

A MANUAL MOTOR STARTER!!!

Now if you get tired of standing there manually connecting this device to start your motor, you use an electromagnetic coil that can be operated remotely sop you can so sit in the office and eat donuts while you push a button to make the motor start.

NOW YOU HAVE AN AUTOMATIC MAGNETIC MOTOR STARTER!!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Feb 2008
Posts: 59
#9
In reply to #7

Re: STARTING MOTOR WITHOUT STAR DELTAL STARTER

03/22/2010 3:29 PM

Did you mean start this 67 hp pump w/o a wye-delta starter or just any starter? If you're trying to save money a frequency controller is out too, so that leaves you with your only two possibilities: DOL (direct accross the line) magnetic starter (safest if it's 3 phase) or use your supply breaker (it better have the capacity for LRA) to turn it on and off. I hope your situation is temporary and your final installation will be according to NEC (or similar). Good luck!

hughes838

Register to Reply
Anonymous Poster #1
#11

Re: Starting Current for Star Delta and DOL Starter

04/13/2017 6:39 AM

Can anyone tell me how to calculate starting current for the motor which has star delta starter, 55 Kw at 415 Volts supply and 0.8 power factor.

I have to calculate current to put a circuit breaker for a load of load of 55 kW with star delta star starter.

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12

Re: Starting Current for Star Delta and DOL Starter

06/01/2023 7:27 AM

The protocols for doing this sort of thing can be found in a range of national electrical standards.

If applicable, the one used in the UK is British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (4); hughes838 (2); JRaef (1); ohmarglen (2); PWSlack (2); Simon Wan (1); tomad (1)

Previous in Forum: Power Factor   Next in Forum: Voltage Drop and Electrical Field Strength

Advertisement