safety of man while working with a machine

06/19/2009 6:29 AM

ELCB & RCCB are being used to prevent a person from electrocution due to leakage current. How do they differ from each other? What is the working principle? How effective is good earthing (grounding to earth) to protect a person/persons from electric shock? Want for a discussion.

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: safety of man while working with a machine

06/19/2009 6:35 AM

They are two terms for the same thing.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2
In reply to #1

Re: safety of man while working with a machine

06/19/2009 8:31 PM

Well, technically one is a subset of the other, but in practicality they are the same. ELCB stands for Earth Leakage Circuit Breaker, which generically means it is checking to see how much current is flowing to earth (ground for us Americans). RCCB stands for Residual Current CB, meaning that this type of ELCB is using the Residual Current method of calculating the amount of flow to earth. Measure all three currents out, the current returning on opposing phases should be the same. Any residual value means some of it is going somewhere else, and that must be earth.

The other way to do it is called a Zero Sequence (ZS) method. That requires a Core Balanced CT (Current Transformer) and a different type of relay with a circuit that looks at the voltae created in the CT if the amount of curent flowing through it does not balance out between all 3 phases and Neutral (if applicable). The ZS method is better for some types of systems, i.e. those with resistance earthing, but requires more hardware than RC and is more expensive, thus making it impractical for all but the largest systems, i.e. the entire plant, not just one tool or machine..

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply