Cable Losses

06/20/2009 7:00 AM

I got the following question :

Many consumers want a 12 VAC Lighting system in their garden with different kind of fixtures Incandescent and LED etc. How do I determin which cable they can use best.

Suppose You have a AWG14 cable with a certain resistance. And for the ease of calculation several 10 Watt Halogen Lamps attached to this cable. The first lamp sits on 10 metres from a transformer, the second and the rest each on 10 Metres too from the forgoing lamp.

How do I determin

a: what my voltage drop would be at the last lamp on the cable. This to advise the customer to use a thicker cable AWG12 or AWG10.

b: what my total consumed power would be at the transformer. Simply adding up the consumed power of all installed lamps isn't the right thing.

Each of the lamps of 10 Watt at 12VAC will consume different from their respective distance from the transformer. The difference between 10 Watt Halogen lamps and 5 Watt LED Lamps is not only the consumed power but also the Power Factor.

I could setup a characteristic diagram of each type of lamp used, measure power at different voltages from 8 - 12 VAC in steps of 0.5V and use these values to determin what the consumed power would be at a certain distance from the transformer in relation to the voltage on that specific point in the cable. But the next lamp after the forgoing lamp behaves different because of the voltage drop which still increases.

Is there any form of other calculation to determin which cable could be used best f.i. 12AWG or better 10AWG and what the expected voltage drop would be at a certain length of the cable.

thnx already for taking the time to read my question.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: May 2009
Location: CORDOBA ARGENTINA
Posts: 157
Good Answers: 4
#1

Re: Cable Losses

06/20/2009 3:03 PM

Just get the Amperes to handle, and calc it as ever and forever is done.

A 5% drop voltage is admited.

As far as I know , leds have to be connected to a DC system.

__________________
devitg
Register to Reply
Active Contributor

Join Date: Jun 2009
Posts: 21
#2

Re: Cable Losses

06/20/2009 9:30 PM

You will get some voltage drop but like a strand of Christmas lights the last will be as bright as the first, if you use a parallel circuit. Series will drop the last to almost no voltage,hence no illumination.So the resistance is figured differently in a series than a parallel. You can also have a series-parallel circuit. Best get an Electrician to hook it up for a few $ now will be well spent.

Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#3
In reply to #2

Re: Cable Losses

06/21/2009 12:39 AM

You did not say how many lights of 10 watts each is in the whole circuit.

Do not exceed the total wattage of the transformer supplying the whole circuit.

Why make it difficult. Use the maximum current and the maximum lenght. That will give you worst case end of line voltage. Allowing a 5% drop will tell you what gauge is required.

FWIW all the garden lights I have seen use 14 Ga wiring and they limit the number of lights to 10 with a 100 watt transformer LED typically draw so little you can safely double the number even if they are supposed to be 4 watts each.

If you really want to be finicky break each section betwen each light into a seperate circuit. But this is almost over doing it.

__________________
Elnav
Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#4

Re: Cable Losses

06/21/2009 4:14 AM

a: Use kirchhoff's theorems and Ohm's law to calculate the losses in the circuit, for both voltage and power. This is basic electrotechnics for highschool. For the ease in calculus you can consider a current density of about 0,8 to 1 A/mm2. In this way the maximum current for tha cable should be arround Imax=Pmax/U where: Imax =the maximum current Pmax = the maximum power consumed by the load U = the voltage (12V in your case) Knowing the max current and the current density for the cable you can choose the section of the cable. b:right. You should also add the cable losses. Also consider a power factor for the transformer, say 0,9 or 0,85 for the load is resistive. The rated power of the transformer would be the next standard value superior to the value obtained with the following formula: S=P/pf where: S= the calculated power for the transformer (VA) P= the active power consumed by the lamps (Watts) pf= power factor

__________________
The time is ......now
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#5

Re: Cable Losses

06/21/2009 7:37 AM

Halogen is old and a heavy power user. CFLs and LEDs have good brightness and take far less current as well as having longer lives, far longer.....

Get them to be modern and also eventually save on electricity costs.....

For the voltage drops on cable size/lengths there are good calculators on the web....

Always use a thicker cable than needed, use double the maximum total current to get the cable size. Make sure it is armoured for garden usage and put in proper safety equipment.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#6

Re: Cable Losses

06/21/2009 9:19 AM

Andy G. is right run a standard voltage drop calculation for AC circuits. Run your lighting in parallel.

Register to Reply
Register to Reply 6 comments