06/24/2009 11:19 AM

how clog happen in pipe ignitor for flare front generator and how to unclogged? this all about the in the refinery (oil and gas). i need to solve this prob..and before that i need to know how prob happen

Register to Reply
Pathfinder Tags: flare pipe
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Aug 2007
Posts: 1790
Good Answers: 87
#1

Re: Clogged Pipe Ignitor at Refinery

06/24/2009 7:53 PM

Some details on the ignitor design would be helpful. Flares get naturally dirty and nasty so a clogged ignitor is not necessarily unexpected... Did someone send a bunch of liquid or other contaminants to the flare recently?

It may not be clogged but rather flat out damaged. Another possiblity is that part of the flare time has melted or otherwise been damaged and is now blocking the ignitor. Has anyone done an actual inspection or are you just assuming it is clogged?

Register to Reply
Active Contributor

Join Date: Jun 2009
Posts: 17
#2
In reply to #1

Re: Clogged Pipe Ignitor at Refinery

06/25/2009 6:48 AM

yup..we already done do the actual inspection...3 pipelines are clogged..

1st, the input for ignition chamber are fuelgas and instrument air..the output of cos flame.

so this flame in pipelines are brought to the pilot to the flare. the clogged is at pipeline that brougth the flame.. so can you explain more how this clogged happen..

Register to Reply
Guru
Engineering Fields - Piping Design Engineering - New Member Egypt - Member - Member since 02/18/2007

Join Date: Feb 2007
Location: Cairo, Egypt
Posts: 1733
Good Answers: 248
#3

Re: Clogged Pipe Ignite at Refinery

06/25/2009 7:04 AM

I have a very well experience related to flare system concerned with the design, construction and operation of that type of piping systems. The first trail was in 1985 when I was responsible to furnish a new 2 flare stacks with a new one Flame Front Generator, FFG using air/fuel ratio to create a flame to propagate through a pipe to ignite the flare tip which provided with a separate fuel line for igniting the pilots.

After erection completion of piping, and after adjusting air/fuel ratio used to make the flame propagation inside the pipes, I found that there was such damping to the flame, and inturn the tip still not ignited. After many trials, I discovered that the main causes of damping was the moisture due to ambient air located inside the pipes, and another cause was the sagging in that low size piping 3/4" & 1" in its midspan.

I dried the lines by purging a dry air, and I add an additional supports to avoid sagging, and at hence the system started to work.

Therefore the clog at your system may be due to moisture, sagging, or rust inside pipe, and I prefer to renew that piping.

__________________
It is better to be defeated on principles, than to win on lies!
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2009
Posts: 17
#5
In reply to #3

Re: Clogged Pipe Ignite at Refinery

07/08/2009 11:54 AM

cant we just unclog?

Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member

Join Date: Apr 2007
Location: Austin, TX
Posts: 367
Good Answers: 10
#4

Re: Clogged Pipe Ignitor at Refinery

06/25/2009 11:05 AM

Could it be clogged from sooting? If you had a rich mixture in that line and a slow combustion taking place, you could get a lot of carbon formation. Do you think this could be a possible mechanism?

__________________
Money doesn't talk, it screams in your face.
Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Abdel Halim Galala (1); betomachine (1); chelah (2); Steve S. (1)

Previous in Forum: Reusing Ammonium Nitrate in Nitric Acid Absorption Columns   Next in Forum: Water Pressure Calculations

Advertisement