Electric Engines and Number of Starts

07/01/2009 2:23 PM

Hi, I know the electrical engines have a limit of starts by time (hour). NEMA standars say something, but I cant find it, Any body knows which is that value? how many starts can I turn?

The engine datasheet is:

125 HP

60 Hz

460 V

152 A

1185 rpm

Thanks in advance

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#1

Re: Electrical engine - Number of starts

07/01/2009 4:28 PM

Look on the nameplate and see what the "duty" rating is. Then look for duty ratings at NEMA.

P. S. They are not free.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Electric Engines and Number of Starts

07/01/2009 7:57 PM

Duty rating refers to the length of time a motor is expected to operate under full load. The motor may be rated as either Continuous duty or Intermittent duty. Continuous duty rated motors are rated to be run continuously without any damage or reduction in life of the motor. General purpose motors will normally be rated for continuous duty.

Intermittent duty motors are rated to be run continuously only for short time periods and then must be allowed to stop and cool before restarting. It is usually possible to reduce the size, weight, and cost of a motor by purchasing an intermittent duty motor. Intermittent duty motors are available with maximum operating times of 5, 15, 30, or 60 minute duties or times.

These motors are sometimes used on devices like garbage disposals or air compressors where the motor operates for a short period and shuts off after the job is accomplished and will not be needed for an extended time period.

Copied from the web.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Electric Engines and Number of Starts

07/01/2009 8:06 PM

It's not quite as simplistic as a look-up table, but almost. There is a load factor involved and you must take the lesser value of the look-up table OR the load factor and duty calculation. The NEMA document explains it in detail.

Although the official NEMA document (NEMA MG10-2110 Table 7) would cost money to purchase from NEMA, that specific information is not guarded and in fact, NEMA uses that table within other free publications. Here is one. The information you seek starts on page 18.

Oh and by the way, an Engine involves conversion of a fuel source to kinetic energy. You are referring to a Motor, which converts one form of energy, such as electricity, to kinetic energy.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Anonymous Poster
#4

Re: Electric Engines and Number of Starts

07/01/2009 11:02 PM

Too many starts in a short period of time - especially full or heavy load starts will incur very heavy demand charges from your local utility. Edmund

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #4

Re: Electric Engines and Number of Starts

07/02/2009 12:53 AM

Being that he asked about NEMA ratings, he is likely in North America. That would not likely be a factor in demand charges for 99% of the utilities here.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#6
In reply to #5

Re: Electric Engines and Number of Starts

07/02/2009 8:44 AM

Peak demand power meters are in use around here, and the customers are charged for all peak demands beyond their contract allowance. Read some of the fine print in electrical utility contracts for industrial plants.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Power-User

Join Date: May 2008
Location: San Jose, CA, USA
Posts: 121
Good Answers: 2
#7

Re: Electric Engines and Number of Starts

07/02/2009 1:41 PM

The types of intermittent operation of an electrical motor are quantified in the IEC definition of duty cycles. How you operate a motor will fall under one (or more) of the described cycles. If a particular motor has been sold as for a specific duty cycle type, it can be used without damage at any less-stressing cycle.

Please see

http://www.engineeringtoolbox.com/iec-duty-cucles-d_739.html

http://books.google.com/books?id=s1eNoZsEPvsC&pg=PA326&lpg=PA326&dq=duty+cycles+of+electrical+motors&source=bl&ots=xW6YC1f7hM&sig=JYjGR7IVIIMRHq0J8ok4_VVXhC0&hl=en&ei=kvBMSs2TIs2etgfFyu2iBA&sa=X&oi=book_result&ct=result&resnum=10

__________________
Scientes et audaces fortuna juvat !
Register to Reply
Power-User

Join Date: Mar 2009
Location: Northeast corner of the sphere
Posts: 310
Good Answers: 7
#8

Re: Electric Engines and Number of Starts

07/02/2009 6:34 PM

When I was doing work in power stations, most of their larger motors (480 - 1,000 volts and 100 - 2,000 HP) were rated for 2 start attempts in a 10 minute time period. If these attempts were not successful, then a 60 minute cool-down period was called for before the next attempt. This goes back 25 years so it may not be dead-on, but it's pretty close.

__________________
How can you be two places at once when you're actually nowhere at all?
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Electric Engines and Number of Starts

08/25/2023 8:19 AM

The motor manufacturers will have that information. Pick up the phone, and ask directly.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#10

Re: Electric Engines and Number of Starts

08/26/2023 6:55 AM

This will vary according to ambient conditions, load, insulation class and and duty cycle...the windings should be protected from thermal overload with safety devices installed...

https://www.kebamerica.com/blog/motor-thermal-protection/

https://static2.weg.net/medias/downloadcenter/ha0/h5f/WEG-motors-specification-of-electric-motors-50039409-brochure-english-web.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#11

Re: Electric Engines and Number of Starts

12/26/2023 6:07 AM

Generally you can have 3 cold or 2 hot starts but in case large MV motors 2 hot and one cold starts are recommended by manufacturers .

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply Off Topic (Score 5)