Anonymous Poster

230 vs 480

07/08/2009 7:59 AM

Fellas, I dont understand everything I know about electricity. However I have an air compressor and the starter says it can be wired either 240 three phase or 480 three phase. The name plate on the motor states 15 hp 200 volts 44.8amps. My question is which is the best way to wire this. I have the 240 and 480 close by. I also have 208 in the plant, but at the opposite end of the plant.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#1

Re: 230 vs 480

07/08/2009 8:12 AM

Working at 240V means 20% above the rating. It may work but motor manufacturers forbid more than ±10%.

BTW I hope you are working on the 60Hz frequency as mentioned in the name plate.

Check whether you can change the motor or put a step down transformer- all options are costly.

The starter is a different ball game. Don't go by its rating.

For final wiring use an electrician.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply Score 1 for Good Answer
Anonymous Poster
#2
In reply to #1

Re: 230 vs 480

07/08/2009 8:21 AM

The wiring is already in place for the 240 and 480 and yes it is 60htz is one more optimal than the other

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: 230 vs 480

07/08/2009 8:38 AM

Given the choice, go for the higher voltage, as the wiring, if not already purchased and run-in, will be smaller and maybe cheaper.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#4
In reply to #3

Re: 230 vs 480

07/08/2009 10:02 AM

The problem here is the motor is rated for 200V ie it is likely a 120/208V 3 phase motor.

The supply of 240V is a bit too high for it.

I had some literature on it let me google and get the link.

Got it

see

http://www.baldor.com/pdf/manuals/PR2525.pdf

page 62 and around.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply Off Topic (Score 5)
Power-User
United States - Member - New Member

Join Date: Aug 2008
Location: KY, USA
Posts: 367
Good Answers: 18
#5

Re: 230 vs 480

07/08/2009 11:45 AM

The first thing I would do is call the motor manufacturer (not the same as the air compressor manufacturer). The motor may have ratings for higher voltages that are just not included on the nameplate. Ask the manufacturer if it is OK to run the motor at a higher voltage if you install different overloads in the starter. My company recently purchased a mixer whose nameplate rating is 1725 rpm at 60hz, but the manufacturer told me that it is OK to run 3450rpm at 120hz. (I'm glad that I called the manufacturer instead of the contractors who installed it this way. )

Does the nameplate on the motor say 50hz or 60hz? Some motors are rated for both frequencies, but at different voltages. If 200v, 60hz is on the nameplate, then 208v, 60hz is fine, but, as SB said, consider that you can get a 15hp motor rated for 240/480v for about $350 - $450 before you run power all the way across the plant. If you opt to buy a new motor, consider what PWS said about higher voltage.

__________________
The most valuable of all talents is that of never using two words when one will do. ~Thomas Jefferson
Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#6

Re: 230 vs 480

07/08/2009 3:12 PM

Something doesn't quite jive here. You state that the motor has a nameplate that says 15 HP, 200 V and 44.8 A. The power at 200 V and 44.8 A yields 8,960 VA, which is nowhere near 15 HP. At 100% efficiency, you would only get 12 HP.

Also, like sb says, don't go by the starter rating.

You can get a buck transformer to reduct the voltage (probably less expensively than running 208 V from the other end of your plant), and it's power rating only has to be the percentage of the voltage reduction. e. g. the motor's rated at 9 kVA, the 230 V needs to be reduced by 30 V, so the worst-case power rating of a buck transformer needs to be 30/200 X 9kVA = 1.35 kVA. Choose a 1.5 kVA minimum buck transformer, and you'll need three single phase or one 3 phase.

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Power-User
United States - Member - New Member

Join Date: Aug 2008
Location: KY, USA
Posts: 367
Good Answers: 18
#8
In reply to #6

Re: 230 vs 480

07/08/2009 4:19 PM

P = √3*E*I

__________________
The most valuable of all talents is that of never using two words when one will do. ~Thomas Jefferson
Reply Off Topic (Score 5)
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#9
In reply to #8

Re: 230 vs 480

07/09/2009 7:51 AM

Oops!

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply Off Topic (Score 5)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: 230 vs 480

07/08/2009 3:31 PM

Some (but not all) motors that have a nameplate stating 200V line are actually wound for 220V, with the understanding that they can accept +- 10% (200 to 240V). But as others have said, you must consult with the manufacturer to be sure, otherwise you need to get a transformer. By the way, you CANNOT connect 480V to that motor, if it were capable of dual voltages it would have said so on the nameplate.

So if the mfr comes back and says it is a dedicated 200V winding, then you must use a transformer. If that's the case, don't get yourself confused with buck-boost transformers unless you plan to hire a qualified electrician who understands these things, Sorry, but it doesn't appear to me that you are going to understand how to do that, you are not even sure how voltage ratings work to begin with. If you want to try to do it yourself, get a 480 to 208V 3 phase transformer, they are very very common and simple to connect. You will need one of at least 20kVA to be able to start that motor, but the nearest standard size will be 30kVA. Buying one of those, along with the fused disconnect to feed it, conduit wire etc., will likely cost you as much or more than running a 208V circuit from somewhere else, but only you can determine that.

By the way, I show a standard NEMA design 15HP 200V motor as having a FLA of 45.1A, so your motor is well within normal for that. Ignore the post that said it was wrong, they don't know what they are doing.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Reply to Forum Thread 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Bill (2); EElectrician (2); JRaef (1); PWSlack (1); sb (2)

Previous in Forum: Oil Conservator...   Next in Forum: Earthing Transformers

Advertisement