Power Factor improvement.

07/13/2009 3:39 AM

I want to connect a power factor correcting equipment with my 591 kva diesel Generator to improve its p.f from 0.8 to 0.98. Then what will I have to do?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Power Factor improvement.

07/13/2009 3:47 AM
  1. Turn the generator off and isolate it.
  2. Raise permit-to-work.
  3. Open terminal covers.
  4. Make an entry into the terminal boxes for the cable between the power factor correction equipment and the generator.
  5. Megger-test the cable to ensure its insulation is undamaged.
  6. Gland-off the cable both ends.
  7. Prepare the conductor tails for conenction, both ends.
  8. Attach the conductors to the generator terminals.
  9. Attach the conductors the power factor equipment terminals.
  10. Close terminal covers.
  11. Relinquish permit-to-work.
  12. Remove isolations.
  13. Re-start generator.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Power Factor improvement.

07/13/2009 11:33 AM

Is this the same generator you asked about in a post located about 22 posts below this one?

Reply