Waste Heat

07/15/2009 7:19 PM

Hello

I have a blower exhausting 116000 cu. ft. per hour of 157 degree F. air into the area and would like to know about how many btus' so I can compare this to something that my managers will understand. I want to convince them this needs to be exhausted to outside. Tried googling, but formula is longer than politicians speech. Any help will be appreciated.

__________________
John 3:16
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#1

Re: Waste heat

07/15/2009 7:34 PM

I sense a Stirling engine heat recovery / turbine powered electrical generation system in the works .

__________________
Don't believe everything you read on the Internet!
Register to Reply Off Topic (Score 5)
4
Anonymous Poster
#2

Re: Waste heat

07/15/2009 7:38 PM

Assuming dry air and an ambient temperature of 80 deg F, the calculation would be (someone please verify...):

BTUH = 116,000 * 0.075 * 0.24 * (157-80) = 160,776 BTU where:

116,000 is your stated exhaust rate in cfh,

0.075 is weight of one cf of dry air in pounds,

0.24 is specific heat of dry air in BTU/lb,

(157-80) is the assumed temperature drop.

Hope this helps.

Register to Reply Good Answer (Score 4)
Active Contributor

Join Date: Aug 2006
Posts: 18
#3
In reply to #2

Re: Waste heat

07/15/2009 10:46 PM

Guest

Thanks for your time and knowledge.

__________________
John 3:16
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#5
In reply to #2

Re: Waste heat

07/16/2009 4:59 AM

I go along with that.

Strictly speaking specific heat of air is in BTU/lb/°F, but result is OK

Cheers........Codey

__________________
Give masochists a fair crack of the whip
Register to Reply
Anonymous Poster
#9
In reply to #2

Re: Waste heat

07/16/2009 11:43 PM

Here's a question to a question. Why would you exhaust this heat? Can't you re-use it for some energy generation...heating hot water at the least?

Register to Reply
Active Contributor

Join Date: Aug 2006
Posts: 18
#22
In reply to #9

Re: Waste heat

07/17/2009 5:09 PM

Guest

Thanks for response. To shed a little light on the subject. My Blower is actually vaccuming flour from an exterior silo and exhausting in the building. To be more precise it is exhausting in a large room occupied by 4 pasta dryers which alone give off a great deal of heat. This heat finds its way to other parts of the building making it very uncomfortable for production team. I would like to exhaust to exterior of building in summer and to warehouse for heat source in winter. My thinking is sometimes to " outside the box " for my managers, which results in opposition. Thanks to your first response, I can now compare it to our warehouse heaters. This converted to $ may result in favorable response.

Thanks again for your responses!!

__________________
John 3:16
Register to Reply
Member

Join Date: Jul 2007
Posts: 8
#24
In reply to #22

Re: Waste heat

07/17/2009 5:27 PM

The heat is valuable and the first step is to determine if the air flow has entrained flour and moisture. These will need to be considered in any system design..

Many dryer processes have been improved with waste heat recovery systems. The key is to use the heat recovered to reduce energy consumption. In your case, you can reclaim the heat prior to exhausting it outside. The heat can be introduced into replacement air in winter to make up the air loss from the building. In summer or winter the heat can be introduced into the dryers as combusion air, if you have burners, or process air if you have a steam heated dryer.

The main concern is in cleaning the exhaust air so that the system does not create

fouled duct work etc. By removing the heat, any moisture in the flow may combine with any dust or flour in the exhaust and clog the system. If the exhaust flow is cleanable, a well desinged system can last for twenty years paying back with saved

heat energy.

rlphaywards@hotmail.com

Register to Reply
Active Contributor

Join Date: Jul 2009
Posts: 15
Good Answers: 2
#4

Re: Waste heat

07/16/2009 1:09 AM

I don't have a thermo book with me, but equation is Q=m*h, where Q=heat released (kJ/s), m=mass flow rate of air (kg/s) and h=enthalpy (kJ/kg). You need an Air Table or HVAC Book to find the enthaply of air at your temperature. Convert your cubic feet per hour to kg/s from knowing the density of air at T=157F. Then, your home free. Also, convert your final answer (kJ/s) to BTU/s or BTU/hour. To put it in terms your boss understands, a standard natural gas burner for a home stove is rated in BTUs per hour, something like 5000 BTU/hour. Compare your number to leaving a burner on a stove on for so many hours per day. Your water heater might also have a BTU/hr rating.

Good Luck!

Register to Reply Score 1 for Good Answer
3
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#6

Re: Waste Heat

07/16/2009 9:42 AM

116000 cu. ft. per hour of 157 degree F. air into the area
If they can't understand the above, then they are plain thick, and no amount of formulae or expressing it as btus or anything else will help them.
Slap them about the face with some wet fish, or better still duct that air into their offices, they will soon get the idea.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Good Answer (Score 3)
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#7
In reply to #6

Re: Waste Heat

07/16/2009 11:18 AM

Ha! Ahhhh... Always a Gas Del.

Although I must say, I have learned not to attempt to slurp my Java while reading your posts in fear of it escaping through my nose.

__________________
Don't believe everything you read on the Internet!
Register to Reply
Guru

Join Date: Nov 2007
Posts: 519
Good Answers: 11
#17
In reply to #6

Re: Waste Heat

07/17/2009 7:13 AM

Everyone understands $$$.

Convert your BTUs to dollars saved.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#18
In reply to #6

Re: Waste Heat

07/17/2009 8:28 AM

Ah, yes Del. But lets be fair now. These are managers (likely lawyers or others of that ilk that control the $$$), not people with any brains. Please dont confuse their abilities.

Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Aug 2006
Posts: 18
#23
In reply to #6

Re: Waste Heat

07/17/2009 5:16 PM

If they can't understand the above, then they are plain thick.

Del you hit the nail square on the head. I use to wonder how people like this got promotions, now I know. The secret is proper placement of lips on derriere.

Have a great one!!

__________________
John 3:16
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#8

Re: Waste Heat

07/16/2009 11:32 PM

little off topic. so where is the air in this room being displace, is there a return, or is this room open.

Do you have any alternatives. such as what part of the coutry is this, northern?where the heat may hekp or southern

and your comment

so I can compare this to something that my managers will understand.

How do these morons manage, if they can not understand. Get thier chair buffed a$$es in the room,

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Member

Join Date: Jun 2009
Posts: 5
#10

Re: Waste Heat

07/17/2009 12:43 AM

Similar question on a slightly different situation;

PArt 1:

I am adding a solar thermal domestic hot water system to the house and want to estimate the number of panels I need to put in the system to heat 40 gallons of water from ambient temp of 75 degrees to 120 degrees F. The panels measure 4 x 8 feet and I have been told a rough rule of thumb that two panels (64 SQ Feet) will heat 40 gallons of water to 120 F in Colorado but I would like know how to figure it.

Part 2:

Once I know how to heat water I need to figure how to calculate the heat in BTU needed to heat a house using hydronic (floor) heating. I know that there are two heat transfers taking place; a transfer of heat to the flooring and radiation into the space to be heated. That space needs to be heated from ambient of 55 degrees to 75 degrees as an example. Do I just consider the air mass to be heated in the space? What is the basic equation involved?

Thanks,

John

Register to Reply Off Topic (Score 5)
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#11
In reply to #10

Re: Waste Heat

07/17/2009 2:30 AM

You need to open your own Thread.

This one is about Waste Heat.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#13
In reply to #11

Re: Waste Heat

07/17/2009 3:18 AM

I agree with kudukdweller9: just cut (Ctrl+C) and paste (Ctrl+V) your post into notepad: go to the top of this thread click on Ask A Question

follow the instructions, and, cut and paste your question into the new thread.

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#12
In reply to #10

Re: Waste Heat

07/17/2009 3:07 AM

There is loads of stuff on solar hot water on the web.. I did a blog on d.i.y. solar hot water panels (click on my user name, there is a link in my profile). It's generally worked on so many square meters per person... but there are plenty of variables, climate and panel position being just two.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Off Topic (Score 5)
Anonymous Poster
#14

Re: Waste Heat

07/17/2009 3:28 AM

total heat this air carries will be 11,600x0.24x(157-room temp)BTU.You are diascharging this heat in the area. If you dotn need to hea tthe area, it is predwerred to discharge in to outside .Or else, you could use this eha tfor many purposes.

Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#15
In reply to #14

Re: Waste Heat

07/17/2009 3:39 AM

I think someone has rearranged the key tops on your keyboard

__________________
health warning: These posts may contain traces of nut.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#16
In reply to #15

Re: Waste Heat

07/17/2009 4:31 AM

Some idiot just spat coffee all over mine.

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#19

Re: Waste Heat

07/17/2009 8:59 AM

You need to speak in terms the bean counters, managers, and accountants can understand. And then you need to speak slowly.

Today they get by with dumping the heat in the immediate area of production. As far as they know the equipment still is working and producing a benefit to them. Why should they spend money to fun ductwork, cut a hole in the roof or wall, and expell the heat elsewhere?

Will OSHA or other government regulator come in and fine the company for unsafe practices?

Will a cooler environment for the machine help it be more productive? Will increase productivity pay for the installation of the exhaust?

Will a cooler environment help the workers make fewer mistakes and reduce scrap rates? Will better quality parts pay for the exhaust system?

Have the manager come and watch the machine operate for two or three hours. Perhaps feeling the heat for an extended time frame may convince him it would be a good idea to install the exhaust. Or maybe it could be ducted within the plant for use in a different area.

In short WIIFM! (What's In It For Me!) If I need to spend money, what is the benefit for making the expenditure. A caveman was smart enough to know he needed a hole in his ceiling or wall to let the smoke and excess heat out, so there might be some hope a manager or accountant could figure that out.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Anonymous Poster
#20

Re: Waste Heat

07/17/2009 10:28 AM

Two other notes.......why are you generating all that wasted heat in the first place, when perhaps some better insulation or "closing the windows/doors" would heat the thing you are heating with less fuel/power. Second, another example to provide your managers is that that amount of lost energy (BTUH) is enough to heat two full sized 4 bedroom homes in a Michigan winter. You can figure the cost by using local utility rates for that number of BTUH.

Register to Reply
Member

Join Date: Jul 2007
Posts: 8
#21

Re: Waste Heat

07/17/2009 10:33 AM

BtuH= 1.08 x scfm x ( T2- T1) see www.isothermics.com

exhausting this volume will create negative draft on building and sepage into building to replace it. design can be made to use this waste heat for other purposes and reduce cooling loads which i assume is your problem.

Register to Reply
Member

Join Date: Jul 2007
Posts: 8
#25

Re: Waste Heat

07/18/2009 11:12 AM

FLASHLIGHT,

If you contact me at rlphaywards@hotmail.com, I can get you the calculations you need on your waste heat.

Rlphaywards

Register to Reply
Register to Reply 25 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!