power saving by capacitor

07/19/2009 12:55 AM

How much power will be saved by 60kvar power capacitor unit for improving power factor from 0.85 to .95 200kw s.c.i.m.motor.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: power saving by capacitor

07/19/2009 11:39 AM

Zero. Improved power factor does not change the KWH used by the motor. If will decrease the Demand Charge if you are being billed for demand.

Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#2
In reply to #1

Re: power saving by capacitor

07/19/2009 4:49 PM

Actually the kW demand will also not be affected, for the same reason. If the kVARh or kVA is recorded, then a charge might be possible from the power supplier.

Zero is still the correct answer to his question.

Regards, CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: power saving by capacitor

07/19/2009 6:15 PM

Quote CJ McGill "Actually the kW demand will also not be affected, for the same reason."

CJ, Thanks for catching that for me. I said "It will decrease the Demand Charge if you are being billed for demand."

I should have said "It will decrease the KVA Demand Charge if you are being billed for KVA demand." It will not reduce the KW demand Charge as CJ pointed out.

Register to Reply
Anonymous Poster
#4

Re: power saving by capacitor

07/19/2009 11:11 PM

Additionaly, improved PF will also reduce stress on the circuit components such as switch, breaker/contactor etc, as the current thru these components will be reduced.

Register to Reply
Participant

Join Date: Jan 2009
Posts: 1
#5

Re: power saving by capacitor

07/20/2009 12:27 AM

How much power will be saved by 60kvar power capacitor unit for improving power factor from 0.85 to .95 200kw s.c.i.m.motor.

None. This is a mis-conception. What the capacitor does is to stop the apparent power being metered and charged and to decrease cable size. Modern electronic meters may overcome this metering anyway. The other factor is that the current is out of phase with the voltage. Cable heating is caused by I2R so cables must be larger to dissipate the extra heat. The power does not change. Beware of snake-oil salesmen.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: power saving by capacitor

07/20/2009 2:54 AM

Very little. The capacitance will reduce cable losses. It will not affect the power consumed by the motor.

The question arises as to the tariff being charged for the electricity. If the tariff is based on kVA, then savings might be made by installing power factor correction [PFC].

If the distribution system is running close to maximum current, then adding PFC might be a better investment than uprating sections or all of the distribution system.

It all depends upon local circumstances, which cannot be seen from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Jul 2009
Location: chennai, India
Posts: 55
Good Answers: 1
#7

Re: power saving by capacitor

07/20/2009 5:14 AM

The Losses in the cable and Transformer will reduce by 20%

__________________
There is nothing either good or bad, only thinking make it so -
Register to Reply
Power-User

Join Date: Mar 2008
Location: MA 01864, USA
Posts: 453
Good Answers: 7
#8

Re: power saving by capacitor

07/20/2009 8:40 AM

Zero saving

__________________
Masyood
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#9

Re: power saving by capacitor

07/20/2009 9:19 AM

Is it me, or does this seem more like a homework question? Oh well, since nobody else brought this up it must be me.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#10

Re: power saving by capacitor

07/20/2009 9:36 AM

Paneer

Would you show me how you came up with the 20% savings.

Register to Reply
Guru

Join Date: Apr 2007
Posts: 3531
Good Answers: 59
#11
In reply to #10

Re: power saving by capacitor

07/20/2009 11:59 AM

It can only be correct where the current from the specific device are not aggregated with currents from other sources. In addition, it is only correct for the resistive part of the loss.

Essentially the power factor is a measure of the ratio of RMS current to what would be needed for the same power in an ideal resistor. So the relative resistive losses in the wiring at 0.95 power factor would be (0.85/0.95)2, or 0.800554 - a reduction of about 20%. Even that is reduction relative to the losses, not to the power used. Once the current is added to other currents of similar magnitudes the effect of changing the phase/power-factor of just one of the contributors becomes much smaller.

BTW, a major reason for the difference in utility costs is the size of the wiring that needs to be provided to avoid overheating etc. In principle that means that the additional cost overhead will depend on whether the equipment is in use at times of peak system loading. (Whether this is reflected in charges is a different matter)

Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#13
In reply to #11

Re: power saving by capacitor

07/21/2009 11:19 PM

I like that answer, very well put together GA for you.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Associate

Join Date: May 2009
Location: Kansas City, Missouri
Posts: 48
Good Answers: 2
#12

Re: power saving by capacitor

07/20/2009 12:00 PM

yeah. i'm still scratching my head about that 20% savings. elaborate please.

__________________
E pur si muove -- Galileo
Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#14
In reply to #12

Re: power saving by capacitor

07/22/2009 2:34 AM

Perhaps this will put the 20% in perspective.

The resistive I2R (heat) losses are the only thing improved. Since this is a very minor factor in a properly designed circuit with properly sized conductors, a 20% improvement of a very minor factor then results in a very very minor improvement compared to the power drawn by the load, which stays the same and is not affected.

Since the power company's distribution system has certain limits and is not always up to the Amp demands of increasing numbers of loads, they are the ones requiring better PF resulting in lower amps, or possibly pay some fee to cover the cost of improving their system to meet the demands.

The consumer's individual load is not where any significant I2R savings will occur with improved PF.

Regards, CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Register to Reply 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); CJMcGill (2); Ed_eng (1); FLIPFLOP (1); JRaef (1); Masyood (1); Panneer Selvam (1); Physicist? (1); PWSlack (1); redfred (1); wareagle (3)

Previous in Forum: Good certification   Next in Forum: booster transformer

Advertisement