AC Motor Operation in High Electro-Magnetic Fields

07/23/2009 9:56 PM

G'day guys...

Firstly is there a Std on using AC motors in this environment, & what if any precautions would be regarded as essential, before we get too far down the track?

Our Customer would like to run an electric driven loader in an Aluminium smelter, in an area which has a high electro-magnetic field, due to the smeltering process.

the AC motor will be approx 20kw in size, & will operate some hydraulic functions, (drives & lift operations). The AC motor will be supplied via a cable direct to the unit. the unit will be mobile

I am in the process of getting some spec's on the strength of the Mag' field (Tesla rating if applicable).

Will post spec's as I receive them.

Any ideas on this matter are most appreciated.

Cheers for now

Joe with the LOIQ.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: AC MOTOR OPERATION IN A HIGH ELECTRO-MAGNETIC FIELDS

07/23/2009 10:55 PM

Since the magnetic fields outside of a gap change by the inverse square of the distance, you will probably not change the motor dynamics itself by much. This does assume that the motor itself will not be going into the gap of the high magnetic field. However, frequently designers will forget this inverse square relationship and forget that magnetic materials placed into these fields will enter quite easily, but the forces required to extract will require considerably more than anticipated.

This has happened more than once with beam steering magnets with adjustable gaps of permanent magnets. "Close the gap just a little more. Darn that didn't adjust the beam right. Close it just a little bit more. (Repeat as desired.) This is not getting us anywhere, open the gap back up. What do you mean it won't move." Sometimes a scientist won't believe it's a bad idea until they break something.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2009
Location: BUNDABERG - Queensland - Australia (That big Island just above Tasmania)...
Posts: 22
Good Answers: 1
#12
In reply to #1

Re: AC MOTOR OPERATION IN A HIGH ELECTRO-MAGNETIC FIELDS

07/26/2009 7:03 PM

Hi Redfred...

Thanks for your input, it was much appreciated & has brought some light onto the situation for me.

From what I can understand from the feed back is this...

The AC motor operation is not adversly affected in this type of application.

So, what my main concern would be now though is, "How to we control the unit as in forward/reverse motions & with the up/down operations. I feel that simple relays & switch gear might be comprimised by the Magnetism". your thoughts on this area?

Thank you again

LOWIQJO..

__________________
Be the best you can offer..... Be yourself.... by LOWIQJO
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#13
In reply to #12

Re: AC MOTOR OPERATION IN A HIGH ELECTRO-MAGNETIC FIELDS

07/27/2009 7:50 AM

Same rules apply about field strength with relay and control circuit locations as with AC motors. But you are quite correct that relays will be more sensitive to the effects of these fields. So placing the relays in a suitable NEMA class steel box instead of a plastic box should shield the relays for the most part. It would also be a good idea that all cabling outside of the shielding box be twisted pair cables with the signal and return twisted together.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Active Contributor

Join Date: Jun 2009
Location: BUNDABERG - Queensland - Australia (That big Island just above Tasmania)...
Posts: 22
Good Answers: 1
#14
In reply to #1

Re: AC MOTOR OPERATION IN A HIGH ELECTRO-MAGNETIC FIELDS

07/27/2009 6:40 PM

Morning Redfred,

Thanks again for the feedback. You have given us some things to run with.

We are still endeavouring to get the Tesla spec's on the magnetic field strength in the area concerned. Once I have these I will post them for some further comments & let everyone know the outcome of the machine trials.

cheers again..

LOWIQJO

__________________
Be the best you can offer..... Be yourself.... by LOWIQJO
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: AC MOTOR OPERATION IN A HIGH ELECTRO-MAGNETIC FIELDS

07/23/2009 11:06 PM

One thing I forgot to mention though. If you must place the motor inside the field itself you will not get the expected forces produced. For the rotor or stator magnetically permeable material will prematurely saturate. Careful analysis and/or wide torque reserves will be required to determine if feasible. Likely it will be easier to not permit the motors themselves to sit in these fields.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#3

Re: AC MOTOR OPERATION IN A HIGH ELECTRO-MAGNETIC FIELDS

07/23/2009 11:41 PM

I don't think there is much effect on the motor. In my plant, I have two equipments that installed just beside the Electric DC Arc Furnace slagging door. The 1st equipment is for the supply of oxygen to our furnace and the other equipment is for sample and temperature measurement. Both equipment are driven by electrical motor.

The magnetic field is really strong and it can really damage the "Peace maker" if someone having it, and goes near the furnace. Even normal gear hand watch will get magnetized.

Both electrical motor does not have any problem so far. It been operating for a few years now.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2009
Location: BUNDABERG - Queensland - Australia (That big Island just above Tasmania)...
Posts: 22
Good Answers: 1
#15
In reply to #3

Re: AC MOTOR OPERATION IN A HIGH ELECTRO-MAGNETIC FIELDS

07/28/2009 11:54 PM

G'day Simon... Thank you for your imput Simon.

Will keep you posted with what the outcome is if/when we do go down that track. We are still waiting on magnetic strength data to see what we are actually up against...

Cheers & thanks again

LowIQJo.. :)

__________________
Be the best you can offer..... Be yourself.... by LOWIQJO
Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#4

Re: AC MOTOR OPERATION IN A HIGH ELECTRO-MAGNETIC FIELDS

07/24/2009 2:08 AM

Normaliy shoud not have any effect.However if u want to be safe you can enclose the motor in a enclosure of non magnetic material .but ensure ventillation is available could be a forced ventillation which will blow the air over the motor continuously.

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#5

Re: AC MOTOR OPERATION IN A HIGH ELECTRO-MAGNETIC FIELDS

07/24/2009 3:16 AM

Depending on the strength of environmental magnetic field it is going to effect motor performance, unless motor is shielded with some nonmagnetic cover.

Environmental magnetic field will offer a bias to the internal magnetic path,and it will enter in more magnetic saturation.however this all will depend on how strong is outer field.

Reply
3
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #5

Re: AC MOTOR OPERATION IN A HIGH ELECTRO-MAGNETIC FIELDS

07/24/2009 8:26 AM

Non-magnetic covers will do nothing, they're non-magnetic! If non-magnetic material worked to shield magnetism then air would do the job. To shield an object placed inside a magnetic field one places the item inside a magnetic box so that the field lines are directed through the box walls around the shielded object. Magnetic permeability can be compared to conductivity not resistance.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Good Answer (Score 3)
Guru
Engineering Fields - Electrical Engineering - New Member

Join Date: Oct 2007
Location: Sour Lake, TX 30°08'59.68"N 94°19'42.81"W
Posts: 675
Good Answers: 13
#7
In reply to #6

Re: AC MOTOR OPERATION IN A HIGH ELECTRO-MAGNETIC FIELDS

07/24/2009 8:59 AM

Ha, ha, it is exactly what I wanted to say:. GA

__________________
Bridge rule #1: Nobody is as good as he thinks about himself nor as dumb, as his partner thinks...
Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#8
In reply to #6

Re: AC MOTOR OPERATION IN A HIGH ELECTRO-MAGNETIC FIELDS

07/24/2009 9:03 AM

Yes you correct indeed, Thank you very much,

Reply
3
Power-User

Join Date: Aug 2006
Location: Adirondacks of NYS
Posts: 136
Good Answers: 7
#9

Re: AC Motor Operation in High Electro-Magnetic Fields

07/25/2009 7:01 AM

At the smelter in Massena NY we had to change to ceramic bearings and add a grounding brush to the rotor shaft. In a high magnetic field, the rotor turning becomes generator and arks across the motor bearings destroying them in a short time. Don't bother with smaller motors that are easy to replace. Just the larger expensive ones that are hard to remove, repair & replace.

__________________
If I hear hoofbeats, why don't I ever think a Zebra might be around?
Reply Good Answer (Score 3)
Guru

Join Date: Jul 2008
Location: Anywhere I may be at the time
Posts: 661
Good Answers: 16
#10
In reply to #9

Re: AC Motor Operation in High Electro-Magnetic Fields

07/25/2009 7:15 AM

That makes perfect sense from a mechanics point of view

Reply
Anonymous Poster
#11
In reply to #10

Re: AC Motor Operation in High Electro-Magnetic Fields

07/25/2009 9:00 AM

Not only from a mechanics point of view, but also from an electronics design engineer's point of view and all serious motor manufacturers.

The phenomenon is caused by eddy currents being induced into the motor core either from external magnetic field or from magnetic surges induced by the windings due to the use of a VFD (VFD duty motors are designed to withstand this).

The resulting voltages into the rotor core try to arc to the motor shell thru the bearings, so in order to avoid them, you need to: Either conect the rotor shaft to the shell with a brush, thus eliminating the arcing path (think of a gas truck dragging a ground strap) or use ceramic housed bearings.

Yahlasit

Reply Score 1 for Good Answer
Reply to Forum Thread 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: