Armored Cable and Earthing

07/24/2009 7:00 AM

why 1 core cable armour shall not be earthed on both ends

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: 1 core cable armour earthing

07/24/2009 7:03 AM

To eliminate ground loops.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Power-User

Join Date: Aug 2007
Location: N.E. Alberta 55.6329 N Lat. 111.0729 W Long. Canada
Posts: 216
Good Answers: 7
#2

Re: Armored Cable and Earthing

07/25/2009 3:24 AM

Single conductor armoured cable does not contain a ground wire. The sheath is for protection only. Grounding a both ends would make the sheath a grounding source. Interconnection to ground. The idea behind grounding only one end is to bleed any voltage that might be induced into the sheath without creating a circulating current or have the sheath as a ground.

__________________
Could be worse, it could be me. :)
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3

Re: Armored Cable and Earthing

07/25/2009 2:43 PM

Because...

In single core armoured cables, you do not have the magnetic fields generated by the other two phases. In a three phase cable, the sum value of the three magnetic fields is zero. In a single core cable, there is no "cancelling" effect, so... a voltage will be induced in the armour by the magnetic field surrounding the conductor.

The impressed voltage is directly tied to the size of the magnetic field generated by the current flowing in the cable. The impressed voltage can be quite high. When both ends are grounded, a "circulating sheath current" can flow between the armour, to ground then back to the armour. The magnitude of the circulating current is a product of the impressed voltage and the impedance of the sheath.

This circulating current can cause considerable heating in the armoured cable and will require a de-rating of the cable ampacity be applied.

To prevent this from being a problem. Single conductor metallic armoured cable (armoured with lead, aluminum, stainless steel, steel or copper) are bonded to ground, usually at the source end, then isolated from ground along its length.

If such isolation can not be done, under the Canadian code, a de-rating down to 70% of original ampacity is required.

For further reading... see CEC rules 4-008 and 10-304.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply Score 1 for Good Answer
Anonymous Poster
#4
In reply to #3

Re: Armored Cable and Earthing

11/03/2010 8:29 AM

How about a 3C cable + 1grnd is it also required to ground at both ends the armoured wire?. Load is most likely unbalanced. The distance is ~ 400meters of cable armoured 3.5C (directly buried) between two substation (Main and distribution substation). It was a switchgear to switchgear connection with the same voltage level. We are suspecting heating of cable in the source (MV swithcgear 34.5KV). Can anyone give some ideas or experience on how they handle the problem.

Reply
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); mayt2u (1); North of 60 (1); PWSlack (1)

Previous in Forum: Salvage Value of Electric Motor   Next in Forum: Heat vs. Harmonics on Motor Starter
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement