Earth Fault Problem in 260 KVA VFD

07/30/2009 6:17 AM

Hi frnds....

i m facing earth fault problem in 260KVA vfd. I m using 200KW motor with this drive for slurry pump application. proper earthing is provided for both motor and drive panel. while drive runs on load, after running 10 to 12 hours VFD trips on Earth fault. but after reseting again drive runs properly. VFD has been checked and cards have been replaced and I have meggered the motor and cable, it was found ok, around 500 mega ohm with respect to earth. so can you tell me what are the causes and remedy?? Please give suggestion with justification.....

RAMESH

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: EARTH FAULT PROBLEM IN 260KVA VFD

07/30/2009 6:42 AM

Is there an earth loop, i.e. something is earthed at more than one place?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#2

Re: Earth Fault Problem in 260 KVA VFD

07/30/2009 1:18 PM

If the system works for 10 to 12 hours and fails, and the problem is repeatable, then most likely the problem is overheating.

Has the system worked for a long period of time with no problem?

Has the air temperature been hotter than usual?

Are any of the air vents obstructed?

What was changed just before the problem started?

Is the slurry thicker or thinner than usual?

Is more slurry being processed than usual?

Do any parts show indications of overheating?

If none of the preceding correct the problem, you may have to try either increasing or decreasing the amount of cooling to differents parts of the system.

Good Luck

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#3

Re: Earth Fault Problem in 260 KVA VFD

07/31/2009 2:10 AM

What are your trip thresholds?

VFD's tend to be intrinsically electrically noisy. I have seen too sensitive settings cause nuisance tripping. However, I have also seen the power conversion section start leaking current through the devices, especially as they get hot. With junction temperatures at 100C they will often have 10 x the leakage cold. With an imbalance in devices you may get asymmetrical phase loading and this erroneously picked up as a ground fault.

You can often help isolate the problem by using independent metering on the ground returns to actually measure the ground current and move through the system until you find its origin.

And then there was the system where the isolation transformer ground fault kept alarming and the VFD kept tripping. It was thought the transformer only fed the drives, but there was a high pressure lamp on the system that had gone to ground. The transformer alarmed, and the drive shutdown on its ground fault detection.

Happy hunting gremlins.

Register to Reply
Participant

Join Date: Apr 2009
Posts: 4
#4

Re: Earth Fault Problem in 260 KVA VFD

07/31/2009 4:08 AM

You could have a problem with wire degridation or insulation overheating during operation. Have you tried to use earth leakage monitoring?

Register to Reply
Anonymous Poster
#5

Re: Earth Fault Problem in 260 KVA VFD

07/31/2009 8:27 AM

Pls check your cable inside the motor terminal box, there's a posibility that the cable insulation is leaking.

Suggestion:

1. insulate motor cable which is directly touching the terminal block

2. run and observed unit operation, check parameters and temperature etc.

Register to Reply
Anonymous Poster
#6

Re: Earth Fault Problem in 260 KVA VFD

07/31/2009 1:22 PM

Dear,

there are always a faults behind every trippings.

earth fault means one of your phase is touching the earth. If you assume that motor & drives are ok even in hot conditions, ( does tripping occure after a definite time of operations ? ) check for the connections - of cable. - near cable gland, there might be a cut.

Register to Reply
Anonymous Poster
#7

Re: Earth Fault Problem in 260 KVA VFD

08/01/2009 4:49 AM

I agree with the answers mentioning current leakage / current unbalance due to heating for about 10-12 Hrs as in your case. We faced similar problem with our VFDs. We provided a separate fan to cool the enclosure to overcome heating which solved our problem. Another problem we faced was dust entry into VFD panels. When we cleaned the cards properly, we could avert tripping without any reason for a much longer time.

Register to Reply
Anonymous Poster
#8

Re: Earth Fault Problem in 260 KVA VFD

08/04/2009 5:21 PM

hv u checked the connection of ur CT cos if ur CT is connected in reverse order it can cause ur equipment to trip on earth fault

Register to Reply
Anonymous Poster
#9

Re: Earth Fault Problem in 260 KVA VFD

10/07/2009 5:50 AM

Wheather the cooling system in proper in drive room if not then first of all check the cooling system.In zinc plants mostly there dust is cunductive in nature. so provide the separate room arrangement for the drive panels .then this type of problem will rectify.

Register to Reply
Anonymous Poster
#10
In reply to #9

Re: Earth Fault Problem in 260 KVA VFD

08/09/2010 8:46 AM

if ur drives tripped earth fault so its not started.how at any cost.

May be some where is wrong.chcked ur earthing its proper or not.

if any control circuit in loop that may be chance to triped the drives.

checked the gland of Motor cable.May be its due to vibration and noise spikes.

that welding Machine was connected neare the area with out pricosion.

checked the insulation of inside termination.

Register to Reply
Power-User

Join Date: May 2011
Location: Chennai, TAMIL NADU, INDIA
Posts: 108
Good Answers: 1
#11

Re: Earth Fault Problem in 260 KVA VFD

07/10/2011 11:01 AM

Dear Mr.rameshchandsharma1

I want to supplement for the details furnished by Mr.Carl Pugh, pertaining to EARTHING.

I also faced a similar problem. In your case the system has worked for 12 Hours. In my case NOT even 30 Minutes. Every expert I called, came and checked and declared installation is OK, but the problem continued.

Finally other expert came and after checking, he advised to remove 6 swg. G.I., Earth wire and provide EARTHING FLAT 3 TIMES OF THE RECOMMENDED CAPACITY - then the problem did not arise or repeat.

It cannot be concluded that the problem is solved, siince at that point of time load reached was 60% only and it is to be seen at full load.

Now after increasing the EARTHING FLAT to 3 times of the Recommended value - HOW the Problem GOT REDUCED/SOLVED - IS TO BE UNDERSTOOD.

I request the CR4 MEMBERS to share their Experience in this matter, and can explain how increasing earth flat size helped to solve the problem.

Rajeswari.