Flame Detector / Combustible Gas Detector

07/31/2009 1:32 PM

Hi,

We have one Installation of Cent Pump with product as Petrochem Naptha

with Gas detector mounted near mechanical seal plus flame detector installed in the

beam with line of sight covering the pump

What is the purpose of having both flame detector & Combustible gas detector for such application ?

Regards

Jose

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#1

Re: Flame Detector / Combustible Gas Detector

07/31/2009 2:03 PM

Probably there is gas passing in installation,these both items can detect any leakage of gas and any event of fire in advance, and will avoid any loss of life and money.

My guess,

Register to Reply
Commentator
Hobbies - Fishing - New Member but not a new fisherman Hobbies - Target Shooting - New Member

Join Date: Apr 2008
Location: Formerly from NJ USA Planet Earth. Relocated to Space Coast FL
Posts: 79
Good Answers: 9
#2

Re: Flame Detector / Combustible Gas Detector

08/01/2009 10:45 AM

josej,

You really do need both detectors. It is possible that the gas detector will not detect a leak because of air currents or wind that carry the vapors away from the detector.

Given this chain of events a fire could exist while the gas detector sees nothing. A good UV flame detector is a must.

A good number of refineries (in the USA) will have an array of nozzles around packings, seals and critical flanges that are piped to a steam supply with a valve located upstream. This allows the operators to apply snuffing steam to a fire while staying at a safe distance form the fire. The cost of the piping to do this is minimal considering the benefits.

Ed

__________________
If you understand no explaination is necessary. If you don't understand no explaination is possible.
Register to Reply
Anonymous Poster
#3

Re: Flame Detector / Combustible Gas Detector

08/01/2009 3:59 PM

Combustible gas detector (based on LEL, Lower Explosive Limit) tells you that you have a small problem now and possibly a big one in the near future. These are usually set to alarm at 10% of the LEL so you have another 90% to go before you have the big problem of an explosion or flame. Flame detector tells you that you now have the big problem and had better do something about it real quick.

Combustible gas meter- find out whats wrong; Flame detector- real high pucker factor time.

Register to Reply
Anonymous Poster
#4

Re: Flame Detector / Combustible Gas Detector

08/02/2009 10:52 AM

the pump installation with the product neptha ,neptha is a product with gives up flamable gases which is under the flamibilty ranges of flamibilty diagram.gas detector detects the gases and the flame detector really not requried as such as it detects falme not requried as really

Register to Reply
Commentator

Join Date: Jun 2008
Posts: 77
#5
In reply to #4

Re: Flame Detector / Combustible Gas Detector

08/03/2009 8:58 PM

Can the flame detector be useful for short circuiting problems?

Register to Reply
Register to Reply 5 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); ed fuzzyE kedz (1); pokalasrao (1); rakesh_semwal (1)

Previous in Forum: caplary transmitter calibration method   Next in Forum: Guide Me to do a Project in Instrumentation
You might be interested in: Gas Instruments, Gas Sensors, Flame Photometers

Advertisement