Why do we need neutral contactors for each generators in a group of generators (synchronized generators)? What problem could happen if we connect all the neutrals directly with the ground?
Is your system's neutral grounded through NGR (Neutral Grounding Resistor)?
If yes, then only one generator need to be grounded at a time (see the previous posting http://cr4.globalspec.com/thread/36055 ). This could be the reason of separate neutral grounding contactor for each generator.
-MS