Earth Ground Tests

08/06/2009 7:40 AM

I am a central office tech for a telephone company in GA, and I have been tasked with "checking the grounds" that our customers provide at cell sites to bond our T1 data circuit equipment to. The boss handed me a new Megger DET10C clamp on tester and said, "Here, check the sites and let me know what is bad." Great... I need to know what readings I need to be looking for. We are trying to cut down on lightning destruction of our equipment, and costly after hours callouts. I have the general knowlege of grounding theory, but this digital meter gives a LOT of information... any suggestions would be greatly appreciated. thank, Chris

__________________
Life is a grinder, whether it wears you down or sharpens and polishes you up depends on what you're made of.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Earth Ground Tests

08/06/2009 7:55 AM

Would it matter whether the work equipment were a shovel, a Megger test box, a motor car, a fighter aircraft or an ocean-going cruise ship?

  • If training is required in the use of workplace equipment, always ask for it.
  • The organisation must have accept/improve criteria for this sort of thing. Ask for them.

It is in the organisation's best interests to ensure that employees have the correct training for the equipment to be used. To do otherwise is foolhardy, and in some jurisdictions can open the door to prosecution of the 'controlling mind' in the event of some mishap.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Dec 2005
Posts: 39
#2
In reply to #1

Re: Earth Ground Tests

08/06/2009 8:01 AM

Thanks... you could not possibly be management with that mentalilty...

__________________
Life is a grinder, whether it wears you down or sharpens and polishes you up depends on what you're made of.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Earth Ground Tests

08/06/2009 8:05 AM

Give 'em what for!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Dec 2005
Posts: 39
#4
In reply to #3

Re: Earth Ground Tests

08/06/2009 8:20 AM

I am using this venue, experience, and a couple of books to get the concrete essentials of this task... i have this at the bottom of my company e-mail signature: I have done so much with so little for so long, I am now qualified to do absolutely anything with absolutely nothing." Unknown Marine, Khe Sanh have a great day.

__________________
Life is a grinder, whether it wears you down or sharpens and polishes you up depends on what you're made of.
Register to Reply
Guru
Engineering Fields - Manufacturing Engineering - New Member Hobbies - Target Shooting - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Dec 2006
Location: Charlotte, NC USA
Posts: 791
Good Answers: 17
#5
In reply to #1

Re: Earth Ground Tests

08/06/2009 9:59 AM

Gee PW,

The more I read your posts, the more differences I see between GB and US. Here in the US we don't have the laws that GB has to protect workers from being fired.

The boss should provide training, but when he doesn't have a training budget, you don't get trained. I had one boss almost fire me because I asked for training. (If safety is the issue, our laws say we HAVE to get the training, but training on how to use a meter would not fall under that protection, nor would pass/fail subjectivity)

I have friends in GB that tell me about how the laws protect them, laws that we don't have here in the US.

Laby

__________________
Be careful of what you wish for .....
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Old New Member

Join Date: Jul 2005
Location: South east U.K.
Posts: 3695
Good Answers: 93
#6

Re: Earth Ground Tests

08/07/2009 4:30 AM

You could always take the readings & hand the list to your boss saying you don't know the criteria for a good or bad earth then let him make the decision.

Just out of interest, the ground earth on our storage container is checked every year & must be less that 1 ohm.

__________________
I didn't have a really important life, but at least it's been funny (Lemmy Kilminster 1945-2015)
Register to Reply
Commentator

Join Date: Jun 2009
Posts: 58
Good Answers: 1
#7

Re: Earth Ground Tests

08/07/2009 4:54 AM

Don't know anything about the Digital Megger, sorry.

I have heard about this problem with lightning strike and cell sites for a while now. I thought that there was some kind on consensus on what can be done to minimize the effects. It strikes me (pun intended) as odd that planes get hit by lightning all the time without any damage. From what I've heard, the last plane to go down because of lightning was in 1967! Surely there must be a way to protect cell sites.

Most of the issues I have heard about where from the generator control boards blowing up. A company is always replacing controller boards because one of the microcontrollers get's zapped and you can't just buy the micro, you have to buy the entire board. Have you been able to pin point what component is being destroyed? If it's a microcontroller, then the board needs a revision to protect it from spikes or switch to a more robust chip that can handle larger ESD and EMI.

My theory is that the power lines from the generator to the cell site are the problem. They usually go out from the generator above ground level, then go underground (not sure how deep), then back up above ground level and into the cell site. Not sure if eliminating the exposure of the power lines to the "outside" of both cabinets would have any effect. Just a theory nothing more.

They always seem to blame the installers for the problems anyways.

Check out this site though. Cell site damage

Register to Reply Score 1 for Good Answer
Associate

Join Date: Dec 2005
Posts: 39
#9
In reply to #7

Re: Earth Ground Tests

08/10/2009 8:08 AM

THIS was the type of informatation I was looking for--the link you provided "cell site damage" was just what the doctor ordered. You seem to have the same theory that I have except that the commercial power is fed via underground cable. The antenna towers have all been under 1Ω and in the star configuration. It is only when we get to the Telco Cabinet that we start running into issues of 10-15+Ω readings. I have printed the information from that link and it will give me a better idea of what I am looking for...Have a great day, Chris

__________________
Life is a grinder, whether it wears you down or sharpens and polishes you up depends on what you're made of.
Register to Reply
Anonymous Poster
#8

Re: Earth Ground Tests

08/07/2009 7:59 AM

According to the recommendations in MIL-STD-464, the contact resistance between the outer screen between connector back-shells shall be below 2.5 milliOhms. In an protected area like a shelter, this value is attainable, whereas in an external environment as described above and together with ageing, this value easily can rise to 100 milliOhm or more. With assumption of a direct lightning strike, the residual transient voltage beneath the cable shield grows rapidly to values much higher than stated in presented evaluation document, which was 2.500 volts.

EWC(SW) USN (Ret)

Register to Reply Off Topic (Score 5)
Member

Join Date: Nov 2008
Posts: 6
#10

Re: Earth Ground Tests

08/17/2009 12:23 PM

Buy a Fluke Multifunction tester Type 1653 and follow the instructions. No I dont work for Fluke or sell their products I am a practicing Domestic electrician.

"If all else fails do the job correctly with the correct tools"

Register to Reply
Associate

Join Date: Dec 2005
Posts: 39
#11
In reply to #10

Re: Earth Ground Tests

08/17/2009 1:07 PM

This seems like the ticket, however, I am not the guy that writes the checks to buy tools... believe me, 'cause, if that were the case, I would have a 401k with Fluke!

__________________
Life is a grinder, whether it wears you down or sharpens and polishes you up depends on what you're made of.
Register to Reply
Associate

Join Date: Dec 2005
Posts: 39
#12
In reply to #10

Re: Earth Ground Tests

08/18/2009 6:24 AM

Hey Mac9, I called Fluke about the 1653 and it can't be purchased in the colonies . Apparently there are a couple of European tests that are required there but not here... at any rate, thanks again...Chris

__________________
Life is a grinder, whether it wears you down or sharpens and polishes you up depends on what you're made of.
Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Greenja (1); Labyguy (1); LocTest Chris (5); Mac9 (1); Nigh (1); PWSlack (2)