Tank Calculations

08/06/2009 11:44 AM

how to calculate the range of a DP Tx for closed tank

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Mar 2008
Location: Mumbai
Posts: 250
Good Answers: 2
#1

Re: Tank Calculations

08/07/2009 1:14 AM

Ref SHELL DEP 32.31.00.32 Appendix 01, they have provided detailed Caln

Regards

Jose

Register to Reply
Anonymous Poster
#3
In reply to #1

Re: Tank Calculations

08/07/2009 4:01 AM

Copyrighted publication - make sure you have permission to use it first!

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Tank Calculations

08/07/2009 3:21 AM

With a tape measure, and in the knowledge of the density of the fluid.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#4

Re: Tank Calculations

08/08/2009 7:34 AM

Density x gravity x height of the liquid You will need to connect the low pressure side of the tx to the top of the tank for a dry leg setup.

Bear in mind that you will have to compensate for any distance the DP TX is above or below the 0 point of the tank level.

Register to Reply