CT Polarity and HT Panel Charging

08/07/2009 7:27 AM

I would like to know what is the importance of testing the polarity of the CT before charging a HT (22 KV) panel.

CT ratio 100/5 A

I came to know that even if we dont check the polarity and if it is reverse, even then only the KWH meter will read wrongly, and all other measurements and protections will work normally.

Please clarify

Regards,

PG

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: CT Polarity and HT Panel Charging

08/07/2009 11:31 AM

I would suggest you to test the polarity and mark it appropriately. Even if it doesn't affect you now; it will help to do the future maintenance job or modification work. You can do the test with a simple method (see the thread http://cr4.globalspec.com/thread/33197 ).

The incorrect polarity will affect the Watt meter, Energy meter, pf meter, Differential protection, Reverse power protection etc. (if the CT is used for these purpose).

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#2

Re: CT Polarity and HT Panel Charging

08/07/2009 1:43 PM

Guest,

Even though it is possible to reverse the secondary CT connections to the correct polarity after energizing the panel, you must respect the high element of danger involved, especially at 22kV.

Since extremely high voltages are developed if an energized CT secondary circuit opens, and some very bad accidents have occurred, in the interest of safety I would highly recommend verifying all details, including the polarity before energizing 22 kV.

Regards, CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Reply
Anonymous Poster
#3

Re: CT Polarity and HT Panel Charging

08/08/2009 12:16 AM

Since ct is used for protection purpose also, it is required to test polarity when used for Restricted E/F protection,differential protection. Otherwise for faults within and beyond the protection region, the sum values ( when multiple cts are used) will be erratic& may cause false tripping or even worse, will not trip at all

regards

E ANANDAN

Reply