Connecting Two Batteries (Old and New) with UPS

08/13/2009 5:36 AM

I have a UPS in my home for fans and etc. I connected a lead acid battery 80AH for back up. After 6 months usage, when I felt that the back up time was not enough, I connected another new 80AH battery parallel with old. I want to ask if this practice is better connecting two batteries one new and one old with the UPS?

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Connecting two batteries (old and new) with UPS

08/13/2009 6:03 AM

The manufacturer's instructions for the UPS will probably require ordering more/replacement batteries from themselves if the product warranty is to be sustained.

If the either battery were to fail for whatever reason, then the other battery might discharge into it causing untold mayhem that might make the user unpopular with his/her fire indemnity insurers. If no other option were available, then it would be worthwhile taking the precaution of isolating the batteries' charge and discharge circuitry with suitable rectifiers so that this potential tragedy could not happen.

The other option is to cascade-out the 80AH battery for a larger, purpose-built, single unit.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#2

Re: Connecting Two Batteries (Old and New) with UPS

08/14/2009 7:45 AM

This is a two sided question. People who are not skilled in electrical maintenance of batteries and UPS technology should not be experimenting with said systems. On the other hand, large UPS systems such as a 500 KVA UPS, batteries are added for time and duration. If a battery goes bad, it is replaced but you don't replace the entire battery bank.

I hope this helps, good luck.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3
In reply to #2

Re: Connecting Two Batteries (Old and New) with UPS

08/14/2009 10:04 AM

Good Answer GHOG,

Many UPS systems have connection points for adding a secondary larger battery bank. Since the OP asked if this could be done, no external battery connection exists in the OP's system. Adding steering diodes to correct the possible problem of one failed battery bank prematurely discharging the good battery bank will cause a bigger problem, one or both battery banks will never be recharged by utility power.

So to get longer operation during a loss of power the OP has two choices. Either reduce the load on the UPS circuit by using more efficient loads (fluorescent or LED lighting instead of filament) and removing unnecessary loads from the UPS circuit. Do you really need fans running when power is lost? Most UPS have some load monitoring capability so a systematic approach to identify improvements can be done. Or the OP must increase the amount of reserve power. This can be done by either replacing the existing UPS or adding a second UPS and moving some of the loads to the other UPS circuit.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

GRAY HAIRED OLD GOAT (1); PWSlack (1); redfred (1)

Previous in Forum: Thermocouple Signal Reading   Next in Forum: Lumen Outputs from Lamps
You might be interested in: Industrial Batteries, Battery Packs and Assemblies

Advertisement