DP Level Measurement

08/17/2009 11:40 AM

How can I calibrate a DP type LT, filled with Glycol in the LP and HP side. The closed tank having 50 % of Condensate, The LT HP & LP distance hight is 1.2 mtrs. I need the calibration procedure and formula for the LT.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: DP level measurement.

08/17/2009 11:49 AM

The differential pressure due to level is the liquid density multiplied by the height above the sensor multiplied by the acceleration due to gravity. Just scale the unit between 0%/4mA/minimum level and 100%/20mA/maximum level by following the manufacturer's instructions.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Active Contributor

Join Date: Jul 2009
Location: Western Australia
Posts: 24
#2

Re: DP Level Measurement

08/17/2009 11:28 PM

Please be more specific.

When you say 50% condensate, is that a level or a ratio of mixed liquids (eg condy + water) with a liquid interface?

Do you know your SG or does it vary?

Is the the top diaphragm always in air?

Reply
Anonymous Poster
#3
In reply to #2

Re: DP Level Measurement

08/18/2009 12:10 PM

Actually I need to select range adjustment ( LRV and URV)of the DP Level transmitter of a Test Seperator ( closed Tank). It is showing 50% Level of condensate on level Glass. And the LP and HP side impulse tube of the LT is filled with Glycol.

filled Glycol SG is 1.05.

Reply
Anonymous Poster
#5
In reply to #3

Re: DP Level Measurement

10/15/2009 2:59 AM

SG of Glycol is 1.26 isn't it???

Reply
Associate

Join Date: Oct 2007
Posts: 29
Good Answers: 1
#4

Re: DP Level Measurement

08/20/2009 3:04 AM

As you have not mentioned the hight of LT from HP tapping point, I assume it 100mm then calibration of LT will be as below;

LRV= Effective Pressure on LT= Pressure on High side - Pressure on Low side

= (100 x 1.05) - (1300 x 1.05) = 105 - 1365 = -1260

URV= ((1200 x 1.0)+(100x1.05)) - (1300 x 1.05) = - 60

SPAN = URV - LRV = -60 -(-1260) = 1200 = distance between your HP & LP Points

Hope this clarifies your question.

Regards,

__________________
Best Regards, srzambre.
Reply
Anonymous Poster
#6
In reply to #4

Re: DP Level Measurement

01/13/2011 1:23 PM

what is 1300, 1200 &100

Reply