i have 415 vac 50 hz supply ( 70 kva) from mains .
i want to make a device which provides 220vac single phase supply
for spot weld m/c ( which may take 100 amp current)using abovesaid input.
how can i do that ?
Re: single phase supply
08/18/2009 4:28 AM
Phase, neutral and earth. If in doubt, consult a qualified electrician locally.
Engineering Fields - Electrical Engineering - Hentoyk Philippines - Member - BRUTUS Saudi Arabia - Member - Brutus United Arab Emirates - Member - Brutus
08/18/2009 7:23 AM
You can not get 220V out of 415V but 240V. If your welding machine nameplate rating voltage range is 220-240V then line to neutral scheme will works(415V divide by sq. root of 3 = 240V in any phase-to-neutral. Suppose your machine rated only or marked 220V, Other option is to use autotransformer (415/380/220)with ample capacity to carry your machine load. Consult your local manufacturer/dealer and electrical engineer/s (if any).
If there is a will... there is a way... No pain / No gain.
Re: Single Phase Power Supply
08/21/2009 8:30 PM
What you can do, is to use a step down transformer to convert from 3 phase to single phase voltage.
So what will be your step down transformer capacity? It a very simple calculation.
You have 415V at 70KVA. …. From your mains
You need single phase 240 at 100 amps…
Your step down transformer will be …..100 Amps x 240V x 1.732 = 41.568 Kva …. So you get a 45KVA or 50KVA step down transformer
Reverse back the calculation to the transformer primary calculation will be ….45KVA/(415/1.732) is only 62.6 KVA from your mains ….. Or….
For 50 KVA will be about 69.56 KVA from your mains.
08/22/2009 1:42 AM
of course you understand the principle of tranformers... you are really an engineer, because you know how to get single supply out of three phase... congrats!