disconnect power

08/22/2009 9:50 PM

Hi all,i will need to replace main electrical breaker on my panel but need first to disconnect power from meter (ring style) to the panel.who can tell me how to do it.

__________________
ZORANDODO
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: disconnect power

08/22/2009 9:57 PM

Your local power supplier?

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#2

Re: disconnect power

08/22/2009 10:01 PM

How brave or lucky do you feel?

I do mains breaker swaps live but I have experience in working with live power.

I would recommend contacting your utility company and having them come by and pull the meter for you. Arond here they dont charge anything for doing it.

If you have everything set up and ready a breaker swap only takes a few minutes. The utility service person will likely just wait while you do it.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Jul 2008
Location: CHELSEA,MA
Posts: 39
#3
In reply to #2

Re: disconnect power

08/22/2009 10:15 PM

thank you for reply,i do all the time live but will lern how to do

__________________
ZORANDODO
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4
In reply to #3

Re: disconnect power

08/23/2009 12:53 PM

Good luck with that...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Commentator

Join Date: Oct 2007
Location: Bass Lake, California
Posts: 62
Good Answers: 1
#5

Re: disconnect power

08/24/2009 12:39 AM

just pull the meter. no meter, no power TO the main breaker.

__________________
Some days you're the pigeon, some days you're the statue.
Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#17
In reply to #5

Re: disconnect power

08/24/2009 9:44 AM

Some power companies impose stiff penalties for "just pulling the meter". Around here an electrician can have his license suspended for it and a customer may be charged 6 monthes of average use for a penalty plus a re-connect fee. At least check with your power company first. -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#6

Re: disconnect power

08/24/2009 2:04 AM

Don't pay the bill they will cut it off for you.

__________________
If you never do anything you never have problems.
Register to Reply
Associate

Join Date: May 2008
Posts: 32
Good Answers: 5
#7

Re: disconnect power

08/24/2009 2:42 AM

This really falls into the "get a professional to do it" category. There are folks who do this stuff all the time. They know what to expect when they open up the box. They can even tell if there were previous mistakes. To top it off, they will get it right the first time. In electrical systems, the second chance may not exist, or it could be an expensive one. Also, there are occasions where the failure of the first try is not evident until the whole thing goes up in smoke in a few years.

This particular task is probably not the best introduction to electricity.

Register to Reply
Guru

Join Date: Dec 2007
Location: Mumbai, India
Posts: 1983
Good Answers: 25
#8

Re: disconnect power

08/24/2009 4:46 AM

If you are not licenced electrician then you should not work on live cables, it is very risky.

Suresh Sharma.

__________________
"Engineers should not look for jobs but should create jobs for others" by Dr.Radhakrishnan Ex President of India during my college graduation day
Register to Reply
Member

Join Date: Jun 2009
Posts: 5
#9

Re: disconnect power

08/24/2009 5:59 AM

it's very good servent, but very bad master

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - Hentoyk Philippines - Member - BRUTUS Saudi Arabia - Member - Brutus United Arab Emirates - Member - Brutus

Join Date: Aug 2009
Location: Gulf Region, IIEE_CRCSA
Posts: 113
Good Answers: 2
#10

Re: disconnect power

08/24/2009 7:02 AM

Why insist of doing it by yourself... may be because you don't like to spend a single penny?.. its a job of a license electricians... Telling you what to do in the air is not effective way of learning. Why waist your time?

Well.. if you to shake your brain and hardened your hair... do it by yourself... if you don't.... please leave it to yhe expert to do a job for you.

Ony birds has a guts and dared to rest and singing on HT transmission line...Find out what happen to bird then...

P.S.

Live elect. wires and bullets respect no boss.

__________________
If there is a will... there is a way... No pain / No gain.
Register to Reply
Participant

Join Date: Aug 2009
Posts: 3
#11

Re: disconnect power

08/24/2009 7:22 AM

This type of meter has a screw in the ring that goes around the meter and the housing.In most states it has A nunbered seal on it.The wright thing to do is call your power co, they will send a serivce man out and pull the meter out for you.In my state there is no charge for this.

Register to Reply
Power-User

Join Date: Jan 2009
Location: Currently on break at home in Houston, Texas USA
Posts: 268
Good Answers: 20
#12

Re: disconnect power

08/24/2009 7:45 AM

I've pulled meters before. It's a simple task.

Remove the ring clamping the meter

Turn OFF the main breaker

Pull the meter out (it plugs in).

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - Hentoyk Philippines - Member - BRUTUS Saudi Arabia - Member - Brutus United Arab Emirates - Member - Brutus

Join Date: Aug 2009
Location: Gulf Region, IIEE_CRCSA
Posts: 113
Good Answers: 2
#13

Re: disconnect power

08/24/2009 8:39 AM

In my locality all KW-H meters are sealed with metal strip by the electric company. Once you pulled it out without informing them it will immediately alarm. If in your case... your elect. meter is not sealed by any means.. then its easy to remove the meter by removing the ring around, if it is done just turn-off the main breaker for safety... then start working to change your damaged circuit breaker... Hallelujah!!!

Replace the circuit breaker with similar configuration so that it will fit in.

__________________
If there is a will... there is a way... No pain / No gain.
Register to Reply
Power-User

Join Date: Jan 2009
Location: Currently on break at home in Houston, Texas USA
Posts: 268
Good Answers: 20
#14

Re: disconnect power

08/24/2009 8:56 AM

Some electric companies use a locking ring around the meter. I've never tried picking the lock on one but, a set of universal keys can be had on eBay for a couple of bucks.

Register to Reply
Anonymous Poster
#15

Re: disconnect power

08/24/2009 9:02 AM

If you pull the meter without utility around here they will fine you heavily. Do it right and call them out.

Register to Reply
Power-User

Join Date: Jan 2009
Location: Currently on break at home in Houston, Texas USA
Posts: 268
Good Answers: 20
#16
In reply to #15

Re: disconnect power

08/24/2009 9:25 AM

That might work but there will be two service charges involved. But we are talking about a fifteen minute job so, what they don't know won't hurt them?

Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#18

Re: disconnect power

08/24/2009 12:14 PM

Call a licensed electrician. If you remove the meter to turn off power you will have to break the seal. In breaking the seal the fine the utility company may impose on you most likely will exceed the cost of the electrician. If you just call the utility company they mostly will want one there anyway or the will call an inspector and more fines.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#19

Re: disconnect power

08/24/2009 1:31 PM

Zorandodo, before you condemned your main circuit breaker, did you check the FLA(full load amperage) on the CB? If I remember right,(years ago), as a rule of thumb, your FLA should not exceed 80% of what the CB is rated at, 100 amp CB = no more than 80 amps under full load. Ive seen 40 year old main breakers work just fine until a microwave oven was put on line, then the problems started. Also do you have aluminum wire feeders from the meter to the main breaker? If you do, check and make sure that the wire is not oxidized and the lug connections on the CB are tight. Very common problem with aluminum wire, why it was outlawed here in the states for use in side residential homes, but you still see it feeding the main panels and still causing heart aches. And while you have your main panel open, you might want to do a little PM work and re-torque all of your circuit breaker lugs. you'd be surprised even copper wire works loose over time. The heat generated by loose connections could thermally trip a breaker.

If you don't already have a clamp on amp meter, invest in a cheap one and check your amp draw at the main CB. You may find you've exceed the limits of the main CB and need to change out your main panel or make adjustment's on your electrical loads inside the building

Either way, have your power company pull the meter and stand by for 15 minutes, so there's no question about liability if you do change the main CB. If they give you any gruff about needing a licensed electrician, tell them go sit in their truck while you do a little preventive maintenance work! dj

Just don't let it be a "SHOCKING EXPERIENCE" for you

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply Score 1 for Good Answer
Anonymous Poster
#20

Re: disconnect power

08/24/2009 2:58 PM

Go for it, Dude.You have all the nescessary qualifications:An insulated brain, and a grounded butt.Just make sure your life insurance is paid up.

Register to Reply
Anonymous Poster
#21

Re: disconnect power

08/24/2009 3:51 PM

Why do you want to change the main in the first place?

Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#22
In reply to #21

Re: disconnect power

08/24/2009 4:12 PM

That was the question I was getting at, "Why"

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - Hentoyk Philippines - Member - BRUTUS Saudi Arabia - Member - Brutus United Arab Emirates - Member - Brutus

Join Date: Aug 2009
Location: Gulf Region, IIEE_CRCSA
Posts: 113
Good Answers: 2
#23

Re: disconnect power

08/25/2009 12:44 AM

Comments #19 is a good point... Changing the main CB it is not just like changing clothes you wear. Meaning that before changing the main CB into next higher rating(for example), it needs to figure out the existing connected load first, also check the size of the main feeder cable if it still at the ample size and capable to carry such loa or else after changing the main CB , the next headache is possible is feeder cable... Like other said... the smart move you gonna do is coodinate with the power company in your locality to avoid heavy penalties. One thing is under the international Law particularly U.S.A., only a qualified licensed master electrician can perform such job...violating this Law and protocol of a Power Company as well... means its your liabilty... imposing heavy penalties or might be landed behind the bars.

Tight connections..... no sparks....no fires... no fire fighters.....Do what is legal and right job.

__________________
If there is a will... there is a way... No pain / No gain.
Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#25
In reply to #23

Re: disconnect power

08/25/2009 9:15 AM

In most areas it is not illegal to do the job for yourself (your own home that you live in, not rental property). There is usually a provision for a home owner to do his own work. Some authorities require some sort of test or quiz by an inspector to see that one has sufficient knowledge to do the job safely. What is illegal is cutting the the seal on the meter. The power company looks at that as stealing power and thus the penalties before they will re-connect. -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Power-User
Hobbies - Musician - New Member Engineering Fields - Manufacturing Engineering - New Member

Join Date: Sep 2007
Location: Endless Mountains of NE Pa, USA
Posts: 298
Good Answers: 20
#24

Re: disconnect power

08/25/2009 6:13 AM

ZORANDODO

You haven't responded as to WHY you need to change your main breaker...? Also, if you need to ask how to pull your power meter it would seem that your residential electrical knowledge may be little shaky..? I would recommend that you solicit the skills of a qualified electrician. Better safe then sorry.

Check with your local code enforcement officer or authority for details. Even if you know how do it yourself, local laws may require a licensed electrician. This is quite often the case especially in urban areas. You may also be required to have an inspection before power can be restored. Get ALL of the details before you start.

If you're allowed to perform the work yourself, let your power supplier pull the meter for you. There is usually a coded seal that needs to be replaced so let them do it so you can't be accused of tampering with the meter. This will save you the heartache of paying fines or worse! Plus, if you drop the meter and break it guess who pays for the replacement...?

At the very least, buy a book like "Practical Electrical Wiring" - The book is well worth the price. It may also be available at a public library. (Of course the usual disclaimers apply to my recommendation and the actual use by you of the information contained there-in.)

__________________
Courage is not the absence of fear, but the inner resolve to rise above it....or the inane lapse in judgement brought on by copious imbibitions....Egre Flagrus
Register to Reply
Active Contributor

Join Date: Aug 2009
Location: Maryland USA
Posts: 24
#26

Re: disconnect power

08/26/2009 10:40 PM

In addition to the other comments...

1 - Check the fault current interrupting rating of the circuit breaker. Your utility can tell you the approximate fault current at your location. This is not load current but available fault current. Do not go by the existing breaker rating, it may or may not be rated for the presently available fault current.

2 - Pulling and re-installing the meter is not a job for the un-trained or inexperienced. I witnessed a 120/240 volt meter fly across the meter room along with a blue streak of light in an apartment complex. The electrician claimed the fault in the apartment wiring had been corrected! If the utility crew member had not properly installed the meter by following procedures and been wearing the required safety equipment he would have bee seriously injured.

3 - Utilities are increasingly installing the "smart meters". If your meter is unplugged, the system may report the meter missing on the next scan. So if you are foolish enough to do pull your own meter, work fast before the utility crew shows up. Even so, they will note the missing or broken seal and do an investigation. Realistically, the meter probably will need to be missing on several scans before anyone is dispatched.

Safety First

Register to Reply
Associate

Join Date: Jul 2008
Location: CHELSEA,MA
Posts: 39
#27
In reply to #26

Re: disconnect power

08/27/2009 6:25 PM

thank you to all for comments and wories,special thanks for bobrog for good advice.

i did do work and all went well

__________________
ZORANDODO
Register to Reply
Active Contributor

Join Date: Aug 2009
Location: Maryland USA
Posts: 24
#28
In reply to #27

Re: disconnect power

08/27/2009 10:22 PM

I am glad to hear that all went well

Register to Reply
Register to Reply 28 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); bobrog (2); Circuit Breaker (2); dadw5boys (1); dj95401 (2); DJSAVAGE (1); gadgetman (1); hentoyk (3); JRaef (1); lyn (1); minsaram2974 (1); ozzb (1); Slowpoke (1); snygolfgs (1); suresh sharma (1); tcmtech (1); tropicalspeed (3); ZORANDODO (2)

Previous in Forum: Solid State Relay 16A 250V T70   Next in Forum: Inverter Efficiency Errors

Advertisement