I have paralal runing two catapillar C4.4. 85kw sets when these set runing paralal one is reading more amps than other.I have set their voltages equal.AVR type is R438.Any reason for this trouble.(governor is L seris ) please send me quick answers

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: electricain

08/27/2009 5:14 AM

The reason is that the two pieces of equipment and their wiring are not exactly identical.

Why is this perceived as "this trouble"? It is to be expected.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Active Contributor

Join Date: Jan 2008
Posts: 18
#2

Re: electricain

08/27/2009 7:07 AM

Dear

There would be always difference in two generator because of their charecteristics.Based on the charecter there would be load sharing so practically both Generator can not share equal loading and never.

Regards

Reply
Anonymous Poster
#3

Re: electricain

08/28/2009 12:33 AM

THERE IS A DROOP SETTING THAT WILL ENABLE THE GENERATORS TO PICK UP LOAD TOGETHER OR ONE BEFORE THE OTHER, SET THEM THE SAME AND SEE IF THEY WORK BETTER TOGETHER. EVERY GENERATOR IS UNIQUE AND YOU WILL HAVE TO PLAY WITH THE ADJUSTMENTS OF GAIN. GET A MANUAL OF THE VOLTAGE REGULATOR, SPEED CONTROLLER AND LOAD SHARING MODULE AND READ UP ON THE ADJUSTMENTS. THE SENSITIVITY ON THE VOLTAGE REGULATOR MAY NOT BE SET CORRECTLY TOO.

GOOD LUCK

Reply
Member

Join Date: Jun 2009
Posts: 5
#4

Re: electricain

09/01/2009 6:21 AM

try to tune the speed ,HZ (Gevernor)of the both DG and the Dropp at the Alternator AVR.

does your Synchronizing system in Automatic or Manual ? , and does the system have any load share module ? if yes, tune the Load Share Module.

Reply
Reply to Forum Thread 4 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); C.S.PANT (1); minsaram2974 (1); PWSlack (1)

Previous in Forum: Formula to design 120KV 0r 220KV transformer   Next in Forum: Ct Burden-Electrical Engineering
You might be interested in: Die Sets, Conveyor Rollers, Contract Packaging Services

Advertisement