I have paralal runing two catapillar C4.4. 85kw sets when these set runing paralal one is reading more amps than other.I have set their voltages equal.AVR type is R438.Any reason for this trouble.(governor is L seris ) please send me quick answers
Re: electricain
08/27/2009 5:14 AM
The reason is that the two pieces of equipment and their wiring are not exactly identical.
Why is this perceived as "this trouble"? It is to be expected.
Re: electricain
08/27/2009 7:07 AM
Dear
There would be always difference in two generator because of their charecteristics.Based on the charecter there would be load sharing so practically both Generator can not share equal loading and never.
Regards
Re: electricain
08/28/2009 12:33 AM
THERE IS A DROOP SETTING THAT WILL ENABLE THE GENERATORS TO PICK UP LOAD TOGETHER OR ONE BEFORE THE OTHER, SET THEM THE SAME AND SEE IF THEY WORK BETTER TOGETHER. EVERY GENERATOR IS UNIQUE AND YOU WILL HAVE TO PLAY WITH THE ADJUSTMENTS OF GAIN. GET A MANUAL OF THE VOLTAGE REGULATOR, SPEED CONTROLLER AND LOAD SHARING MODULE AND READ UP ON THE ADJUSTMENTS. THE SENSITIVITY ON THE VOLTAGE REGULATOR MAY NOT BE SET CORRECTLY TOO.
GOOD LUCK
Re: electricain
09/01/2009 6:21 AM
try to tune the speed ,HZ (Gevernor)of the both DG and the Dropp at the Alternator AVR.
does your Synchronizing system in Automatic or Manual ? , and does the system have any load share module ? if yes, tune the Load Share Module.