Surge Arrester

09/01/2009 9:52 AM

Hello everyone.I have a doubt regarding surge arrester.The surge arrester in switchyard is copnnected with rthe incoming line and it is always in open ckt. condition.For 220kv system the phase to neutral voltage is 127kv.

Why the rated voltage of surge arrester for 245(max.) system is 198kv and maximum operating voltage is 168kv?

9max.)

__________________
partha sarathi pattanaik
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
4
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#1

Re: Surge Arrester

09/01/2009 11:16 PM

Although you don't define define the type of station class arrester, it is not an open circuit because regardless of construction, a grading current flows through the arrester as long as it is connected between line and ground. If it is a gapped type silicon carbide, grading current flows through the grading circuit and if gapless, grading current flows through the metal oxide varistors (MOV). The arrester rating may be based on the maximum phase to ground operating voltage (probably assuming 10% regulation), the maximum temporary overvoltage that can exist at that location, system grounding, etc.

Remember, surge arresters are designed to protect against impulse overvoltages not power frequency overvoltages. They have a TOV rating which is essentially a volt-time curve that defines the magnitude and duration of power frequency voltage above their maximum continuous operating voltage (MCOV) they can be expected to survive without damage.

Register to Reply Good Answer (Score 4)