Faults in 132-KV Transmission Lines

09/01/2009 10:53 AM

We are located in the eastern part of India and the area under discussion is very thunder-prone. In our 132 KV transmission Lines, in many case some earth wires are missing at different spans for different lines. During stormy weather, a no. of line trippings are occurring. Can we attribute it for absence of Earth wires? Incidentally, shattering of Insulators are not reported subsequent to such faults.Line patroling does not yield any findings.What may be the reasons for such trippings?

mridul chanda

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Aug 2009
Location: Glen Mills, PA.
Posts: 2385
Good Answers: 114
#1

Re: Faults in 132-KV Transmission Lines

09/01/2009 7:23 PM

The purpose of the overhead "earth wire" is to shield the transmission lines so it probably is. You would have to check where the strikes take place and see if they match the line sections where the protection is missing.

__________________
In a time of universal deceit, telling the truth is a revolutionary act. George Orwell
Register to Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#2

Re: Faults in 132-KV Transmission Lines

09/01/2009 11:23 PM

You can certainly attribute a major part of the trips to missing earth wires. Assuming there is an overhead shield or sky wire, properly located to shield the phase conductors, missing earth wires would render it ineffective. In order to be effective the shield wire must be solidly grounded through low footing resistance. The situation you describe will also cause backflashover and an abnormal number of shielding failures.

Register to Reply
Active Contributor

Join Date: Aug 2009
Location: India
Posts: 12
#3

Re: Faults in 132-KV Transmission Lines

09/02/2009 1:11 AM

We also call this as gaurd wire running between tower to tower and as far as I know, it is for lightning protection only. This need be earthed at frequent intervals to dissipate the energy. Hope i am in line with your point.

__________________
Mind is like a parachute, no use if you do not open it
Register to Reply
Commentator

Join Date: Nov 2007
Location: Third Rock from the Sun (?)
Posts: 76
Good Answers: 8
#4
In reply to #3

Re: Faults in 132-KV Transmission Lines

09/02/2009 2:19 AM

Yes, you are right. It is a shield (guard) wire formerly for lightning protection only and it should be grounded at every structure to less then 25 ohms resistance. The reason that I say it was "formerly for lightning protection only" is that there are now overhead shield wires that have a fiber optic core that can be used to transmit data.

BTW, this is a great forum and I'd like to thank everyone for their participation.