Dear Friends, We are constructing a (3 x 11)MW hydro power plant for which a 220kV Double circuit line of Zebra conductor(length 18km) is proposed. Now the problem is the link line (35km long, also at 220kV with Zebra) substation is not going to be ready within time. My question is: Can we charge this 220kV line (for a combined length of 53km) at 33kV bypassing the 220kV substation for transmission of our power? Kindly give the limitations or changes required at our existing 220kV set-up. We have 220kV outdoor switchyard and we may to use the existing switchgear (other than CT/PT & GSU Transformer). Thanx
Re: CHARGING OF 220KV LINE AT 33KV
09/01/2009 9:46 AM
At much reduced power, maybe, though the voltage drops might not be acceptable at the lower supply voltage, perhaps.
09/01/2009 11:17 AM
Using the TL at 33 kv should be no problem. Did that once. Are you installing a neutral? Calculate the voltage drop for the load you have. 53 km is a long way.
09/01/2009 7:47 PM
Just convert it to miles. Then you only have to go about 34 of them!
Ask NASA how that works!
09/02/2009 1:07 AM
Thanx for the response guys. Yes, we'll have 8%(approx.) voltage drop and we'll have to absorb it at our end. But I suppose its better to sell some power than wait for the entire duration (6-8 months)for commissioning of the new substation??? Can someone throw some light about the line charging requirement?
09/02/2009 5:01 PM
You can install some pole mtd regulators to correct the 8%.
Re: Charging a 220-KV Line at 33-KV
09/02/2009 12:59 AM
Charging 220 kV line at 33 kV, will enable you to transmit a max. of 4.95 MW power. Is it worth the call, after having to change the CTs, PTs, costly transformer too?
Calculations as follows, for 33 MW of total power -
P=sq.rt.3*V*I
At 220 kV, I = 3*1100/(1.7321*220*0.9), I have presumed 0.9 pf. = 96.222
Therefore, at 33 kV, P = 1.7321*33*96.222*0.9 KW = 4950 kW = 4.95 MW.
Thanks and regards
Ashok Toshniwal, Bangalore, India
09/03/2009 10:37 PM
Rajfab Quote " Can someone throw some light about the line charging requirement?"
Take all the load off the line and go for it.
09/05/2009 9:32 AM
I believe you do not need to spend much to cater to this temporary measure.Perhaps some short length cables 220kv terminals to 33kv switchgears.You can sellect the tap changer position (OLTC)on the primary sides of 33kv or 11kv transformer to correct the voltage drop without extra cost.CT metering at 33kv panels will be accurate. The live transmission line will make cable theft more difficult.