09/10/2009 10:57 PM
For NOx reduction in boilers; it was suggested to have a cascaded FGR (Flue Gas Recirculation) from the gas stack to the combustion zone flow with combustion air flow for auto adjusting when boiler load changes.
Had anybody experienced that before? Will that reduce NOx emission?
Re: Boilers NOx Reduction by Control Systems Improvement
09/11/2009 11:43 AM
No, though it will improve boiler thermal efficiency, provided the remaining flue gas temperature is above the dewpoint of sulphuric acid, otherwise the stack will begin to rot away.
09/23/2009 6:11 AM
This was a normal design concept on B&W coal fired boilers for the larger units designed in mid 60's and installed in early 70's. Gas recirc was extablished fro economizer outlet where tem is approximately 650F and recrculated back to combustion zone. The gas flow rate was controlled to control ehat absorption rate of boielr waterwalls. We did not measure NOx at that time but logically, moving heat higher in the boiler would increase NOx.