Motor Won't Run at Rated RPM

09/16/2009 11:02 AM

I have a 70hp 480 volt motor that is rated at 1800 rpm that will only run at about 450 rpm. The contactors for the Y start and Delta Run seem to be functioning correctly. The Motor was just rewound. Any ideas?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#1

Re: Y Start, Delta Run, motor not at rated rpm

09/16/2009 12:36 PM

I assume you are with a 3 phase motor.

An 1800RPM at 450 RPM will stall. Only possibility that I can see is (you are at 60Hz right?) the windings leads are all brought out and by mistake these are connected as an 8 Pole motor (450 = 3600/8) and then the synchronous speed is 450 and not 1800.

There may be a bit of winding reversal too but then it would have hunted / drawn excessive current so that is not a likely possibility.

Ask your electrician to check the winding connections.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply Score 1 for Good Answer
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#2

Re: Motor Won't Run at Rated RPM

09/16/2009 4:54 PM

Naw... It's just that little gremlin hard at work.

__________________
Don't believe everything you read on the Internet!
Register to Reply Off Topic (Score 5)
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#3

Re: Motor Won't Run at Rated RPM

09/16/2009 7:36 PM

Actually it should be winded 16 poles to run 450(not 8 SB at 8 poles it would run 900 at 60Hz) which is very difficult by the way or internal connections messed. (one phase reverced.) Make 3 tests reversing the leads of each phase that go to the 6 screw connector and if not OK reverse again and go to next.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply Score 1 for Good Answer
Anonymous Poster
#4
In reply to #3

Re: Motor Won't Run at Rated RPM

09/17/2009 8:17 AM

Sorry should have said pole pairs .

Register to Reply Off Topic (Score 5)
Anonymous Poster
#8
In reply to #4

Re: Motor Won't Run at Rated RPM

10/06/2009 11:29 AM

Still the gratest !

Register to Reply
Participant

Join Date: Sep 2009
Posts: 2
#5
In reply to #3

Re: Motor Won't Run at Rated RPM

09/17/2009 9:48 AM

Thanks for the tip. We uncoupled the motor and it did reach the rated rpm (no Load) It is an air compressor that we have comfirmed not to be the issue through inspection at the vendors facility. If one of the windings were reversed does it make sense that it could reach rated rpm with no load?

Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#7
In reply to #5

Re: Motor Won't Run at Rated RPM

09/18/2009 11:02 AM

No It doesn.t. I assumed the mesurement was unloaded. But there is a chance of half pole reversal in winding that can give low torque such as your case. Still do the test but if zill make another 3 tests (unloaded) and only briefely in star:Completely disconnect one by one the phases (one at a time) to find which if disconnected allows to start. If this applies to all then have to open up and check if internal windig to winding connections are accessible and verifiable..In a good quality winding they should.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#6

Re: Motor Won't Run at Rated RPM

09/17/2009 12:56 PM

It is not a wound rotor induction motor by chance? though it does not seem likely by other data.

Even then stable speed at 25% synch is a surprising phenomenon.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9

Re: Motor Won't Run at Rated RPM

10/06/2009 1:38 PM

it could still be a connection issue however. If the motor is a dual voltage AND set up for Y-Delta starting (12 lead), and if you connected to the high voltage windings but are supplying low voltage, there will be insufficient torque from the motor. It will run at the normal speed when uncoupled, but the extreme torque loss will cause it to stall with any appreciable load: torque varies by the square of the voltage reduction.

The reason why I bring this up is that some motors, especially Weg, are sold as "480V" for use in North America, but are actually dual voltage motors for use in Brazil where they use 760V. So the motors are actually 440/760V wound, and if you are using them in North America, you MUST connect them to the LOW VOLTAGE pattern, which is counter-intuitive to what most electricians do every other day of their lives. Here is a direct quote from the Weg Crusher Duty motor manual.

STAR-DELTA STARTING
It is fundamental for star-delta starting that three phase motor have
the required number of leads to allow connection on both voltages,

that is, 220/380V, 380/660V or 440/760V...

So if your motor is one that is wound for 760V and you are supplying 480V, your motor is only producing roughly 40% of it's rated torque and when you couple the compressor, it will stall. Double check your connections again.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); JRaef (1); RVZ717 (1); sb (2); shawn1234 (1); SimpleMind (2)

Previous in Forum: UPS Enclosure   Next in Forum: Capacitor-Excited Generators

Advertisement