Capacitor-Excited Generators

09/16/2009 2:20 PM

Hi All,

Has anyone out there got a definitive explanation of how a capacitor regulated alternator (generator) works? I have repaired dozens of these little beasts, the biggest being about 20kW but I have never seen any explanation of their actual working principle.

I have always thought that the residual magnetism generated a current in the capacitor circuit, phase shifted from the main winding, and this resulted in the current being induced into the rotor. When more load is drawn from the output then more current is generated in the rotor, I presumed by a shift in phase, similar to that seen in the current in a loaded and unloaded induction motor.

(The member who's signature line is " if you cannot explain it simply you don't understand it well enough" is never more apt!)

Have I got it right, if so is there a better explanation? Or, if totally wrong then please explain.

I am actually having problems with one at this moment. The unit is a 3600rpm, 2p 60Hz 10kVA belt driven shaft generator.(see diagram)

tests carried out:-

Output windings______Pass 4Amps through both windings in series, Vgrep across each is 5.9V and 6.2V. Is this sufficient imbalance to conclude shorted turn(s)?

Diodes, OK, tested in situ with a 12V 50W lamp, as an ohm meter cannot read them in parallel with the windings.

VDRs______Untested, but these do not come into play until the rotor has current in it and are there to dissipate the reverse voltage spikes. They are not short circuit.

Rotor windings,______ about 6 Ohms each, taken as being good due to equality.

Capacitors, 2 x 30uF, tested ok

Capacitor winding,_______ 0.6 Ohm

spin to 3600rpm,_ 1.7V residual from each of the 110V terminals. conclusion, output windings are OK (It is improbable that they have equal faults)

Add 60uF to output terminals, unit loads prime mover (in our test case a powerful electric drill). Output rises to 40V

Attempt to add a resistive load of 500W, output reduces to zero

remove capacitor, voltage drops to residual and loading ceases.

All windings megger clear of contact with the frame.

Visual inspection, no signs of burning, water damage or other cause of failure.

Having written the above I have come to the conclusion that the output windings MUST have some shorted turns. Can anyone confirm my diagnosis?

Regards

Chas

__________________
En la casa del herrero, cuchillos de palo!
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#1

Re: Capacitor-Excited Generators

09/16/2009 6:40 PM

Hi capacitor winding unexpected ohm value (too low). Is this with capacitor disconnected? If not disconnect and check again. Any change noticed discard capacitor Any local discolorations on this winding?

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Guru

Join Date: Jul 2008
Location: Mallorca, Spain
Posts: 567
Good Answers: 15
#3
In reply to #1

Re: Capacitor-Excited Generators

09/17/2009 5:31 AM

Hi,

All windings look new, I think this may have been recently rewound, if that is the case then almost anything could be wrong. It looks very neat though, not badly done

I agree on the cap winding seeming low Ohms. I would have expected a few Ohms, between 3Ω and 10Ω say.

Regards

Chas

__________________
En la casa del herrero, cuchillos de palo!
Register to Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#2

Re: Capacitor-Excited Generators

09/17/2009 1:31 AM

Check connections once again. Correct start & end termination is very important. Winding with capacitor ensures constant voltage with varying loads. You can interchange each winding terminal (hit & try method)

__________________
Subramanyam
Register to Reply
Anonymous Poster
#4
In reply to #2

Re: Capacitor-Excited Generators

10/08/2009 6:19 AM

Maybe the rotor has lost its magnetism and needs to be re-flashed?