I build DCS control panels and I always tie the ground bus bar to the back panel. This new project that we got the specification is asking for a electrically isolated ground bus bar for field wires. Then it states to tie that bus bar to common control ground.
Does not make sense. Its the same thing as a bus bar attached to back panel. Can someone tell me why you would want to do this????
Below is the extract from the specification.
5.2 Each control common ground bus shall be a 1/4-inch by 1-inch copper bus electrically isolated from the panel enclosure and installed near the terminal blocks. It shall be connected to the control common ground system by an insulated conductor (Refer to Section 16A).