Mass Flow Meter - Calibration and Commissioning

09/20/2009 11:11 PM

how to do the mass flowmeter calibaration and

comissioning in power plants?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Mar 2009
Posts: 61
Good Answers: 3
#1

Re: Mass flow meter calibration and comissioning

09/21/2009 1:26 AM

For coriolis mass flow meters there is no field calibration or site calibration that can be done.

This calibration is done at the factory using specialized flow proving equipment and simulators (laboratory environment), the average operating company (or service company/contractor) does not have this type of equipment as part of their normal maintenance/service equipment.

The commissioning of these equipment usually entails only verification of wiring, power-up, verification of configured parameters (such as ranges and engineering units etc) using a HHT and if possible verification of measurements obtained from internal sensors (such as temperature) under shelf of ambient conditions (these are usually also obtained from an HHT such as the HART 375).

Usually if problems are suspected or observed the items must be returned to the manufacturer, also given the nature of their intended use (for custody transfer etc) a factory certificate is usually required.

Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Mass flow meter calibration and comissioning

09/21/2009 10:19 AM

Rely on the manufacturer's calibration certificate supplied with the instrument. If it has been mislaid, a call to the manufacturer for a replacement, quoting the serial number, will usually be sufficient for a fax copy of it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Participant

Join Date: Aug 2009
Location: Brasil
Posts: 4
#3

Re: Mass Flow Meter - Calibration and Commissioning

09/24/2009 7:25 AM

Hello,

After you certify that the calibration was done at the factory, you can check in the transmitter if the flow range (ex.: m3/h) is the same of controller (DCS or PLC).

Reply
Commentator

Join Date: Mar 2009
Posts: 61
Good Answers: 3
#4
In reply to #3

Re: Mass Flow Meter - Calibration and Commissioning

09/24/2009 10:58 AM

From comment # 2;

"The commissioning of these equipment usually entails only verification of wiring, power-up, verification of configured parameters (such as ranges and engineering units etc)"

The proper thing to do is to check the configured parameters against the process and/or instrument datasheet for the application/instrument not against what is configured on DCS or PLC, this is particularly important for new projects and installations as there is a higher possibility of there being discrepancies, changes may have been made by engineering companies and information not passed onto system developers and procurement groups in a timely manner.

For existing installations using the ranges on automation systems may be acceptable as the equipment would have been in service already.

Reply
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dabdool (2); PWSlack (1); Salvaterra (1)

Previous in Forum: PID Fine Tuning Reg   Next in Forum: Used Test Equipment - What's Hot Right Now?

Advertisement