Hi
The trans former Details given below is Connected for this transformer how to calculate the capacitor rating in idel condition
already we connected 10 KVAr capacitor for compensation of power factor but the power factor is fluctuating to 0.5 to 0.93
Transformer Rating - 500KVA
Volts HV/LV - 11000/433 V
Current HV/LV - 26.24/666.69 A
Vector group DYN-11
| Test | Measured Values | Calculated Values | Guranted Values |
| No-Load Loss | 800 Watts at 433 Volts | 800 W | 1000.00 Watts |
| Mag.Current | 6.25 Amps at 433 Volts | 0.90% | 3.00% |
| Load Loss | 4800 Watts at 26.24 Amps @ 75 Deg C | 5561 W | 6000.00 Watts |
| Impedence | 540 Volts at 26.24 Amps @ 75 Deg C | 4.94% | 4.50% to 5.50% |
please give me the suggestion for improve the power factor and calculating method,formula
Thanking you
Regards
G.Senthilkumar