Re: Current on primary side of transformer due to secondary side fault
09/21/2009 7:04 PM
Assumptions:
The transformer is connected to the source of zero impedance (infinite fault level). Practically it is not the case; every source has a finite fault MVA.
The cable reactance is ignored
The transformer secondary neutral is solidly grounded
Transformer Secondary current = 1000 / (1.732 x 0.48) = 1203 A
Transformer Primary current = 1000 / (1.732 x 13.8) = 41.8 A
The maximum secondary side fault current = 1203 / (5.75/100) = 20,921 A = 21 kA
The maximum primary side fault current = 41.8 / (5.75/100) = 727 A
These are the maximum fault currents. With a finite MVA level of the transformer source (or utility), the fault current will be less than this.
Because of the 3rd assumption, the fault current will be same for all three cases.
- MS
09/21/2009 8:19 PM
A correction:
For case 2 (phase to phase fault), the secondary fault current will be 86.7% (1.732/2) of the above calculated fault current. In this case, the L-L voltage is 1.732 times of L-N voltage but the reactance will be doubled (the two phase reactance's will be in series). The primary fault current depends on the transformer configuration. If the transformer is Y-Y connected, the primary fault current also will be 86.7%.
- MS
they have explain the different conditions and differenct type faults here and how much will be the expected primary fault current when there is a fault at secondary side ...
Correct me if i am wrong i am learner