Current on Transformer Primary Side

09/21/2009 5:43 PM

I have a question 13.8/0.48 kv 1mva with 5.75 % reactance

what will be the fault current at primary side due to fault at secondary side

1 single phase to ground

2 phase to phase

3 three phase top ground

kindly help

__________________
Correct me if i am wrong i am learner
Register to Reply
Pathfinder Tags: secondary side transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Current on primary side of transformer due to secondary side fault

09/21/2009 7:04 PM

Assumptions:

  1. The transformer is connected to the source of zero impedance (infinite fault level). Practically it is not the case; every source has a finite fault MVA.
  2. The cable reactance is ignored
  3. The transformer secondary neutral is solidly grounded

Transformer Secondary current = 1000 / (1.732 x 0.48) = 1203 A

Transformer Primary current = 1000 / (1.732 x 13.8) = 41.8 A

The maximum secondary side fault current = 1203 / (5.75/100) = 20,921 A = 21 kA

The maximum primary side fault current = 41.8 / (5.75/100) = 727 A

These are the maximum fault currents. With a finite MVA level of the transformer source (or utility), the fault current will be less than this.

Because of the 3rd assumption, the fault current will be same for all three cases.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Current on primary side of transformer due to secondary side fault

09/21/2009 8:19 PM

A correction:

For case 2 (phase to phase fault), the secondary fault current will be 86.7% (1.732/2) of the above calculated fault current. In this case, the L-L voltage is 1.732 times of L-N voltage but the reactance will be doubled (the two phase reactance's will be in series). The primary fault current depends on the transformer configuration. If the transformer is Y-Y connected, the primary fault current also will be 86.7%.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Commentator

Join Date: Aug 2009
Posts: 91
#3
In reply to #2

Re: Current on primary side of transformer due to secondary side fault

09/22/2009 3:44 AM

The transformer is D/y and yes it is solidly grounded ....

__________________
Correct me if i am wrong i am learner
Register to Reply
Commentator

Join Date: Aug 2009
Posts: 91
#4

Re: Current on primary side of transformer due to secondary side fault

09/22/2009 3:55 AM

samad shahab actually it is given in c37.91 but they just mention the configuration

can u explain further or any link how i can analyses..

1 single phase fault on sec side

2 phase to phase fault on sec side

3 three phase fault on sec side

the effect of solid grounding when ground fault occur the ground fault current will travel to neutral in from ground ?

__________________
Correct me if i am wrong i am learner
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#5
In reply to #4

Re: Current on primary side of transformer due to secondary side fault

09/22/2009 6:45 PM

There are a few methods available for short circuit calculation.

They are:

(1) Per Unit method

(2) MVA method

(3) Point-to-Point method

(4) Ohmic Method

I suggest you follow one method first (don't mix up the methods). Here are some links that have step by step approaches for various methods:

https://ecmweb.com/mag/electric_shortcircuit_calculation_methods

https://www.arcadvisor.com/faq/about_mva_method.html

https://www.mikeholt.com/freestuff.php?id=freegeneral

The good software for short circuit calculations is through ETAP (https://www.etap.com), EasyPower (https://www.easypower.com), etc. You can download the trial version.

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Commentator

Join Date: Aug 2009
Posts: 91
#6

Re: Current on Transformer Primary Side

09/23/2009 8:06 AM

Yesterday i just found the very good website specifically for these type of conditions

http://www.skm.com/Shifting%20Transformer%20Damage%20Curves%20for%20Through-Fault%20Current%20Protection.shtml

they have explain the different conditions and differenct type faults here and how much will be the expected primary fault current when there is a fault at secondary side ...

__________________
Correct me if i am wrong i am learner