vfd detail

10/05/2009 12:48 AM

can we connect 12.5 HPmoter to 10 HP vfd

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#1

Re: vfd detail

10/05/2009 2:37 AM

Normally, in general thumb of rules it is not possible to run a higher load with a lower load driver.

Just like your car. If you have a small car that is capacity to fit 4 persons, do you think it can fit another 3 persons to it?. Even if you can fit 7 persons in to the small car, your small engine will not able to run with that full load, it had to carry.

But of course, if your car have another additional carrier that attach to the back of your small car where the other 3 person sit at the additional carrier that should not be a problem.

Just like your question asked,

Yes, you can drive the 12.5 Horse Power motor with a 10HP VFD provided that your motor must have 6 lead wire and running in Delta Connection. Yes, we have some ways/methode to do the connection using small VFD to run the big motor.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: vfd detail

10/05/2009 3:58 AM

There will be some issues with it.

  • Don't expect the inverter to supply the full load motor current.
  • Don't expect to be able to set the VFD overload setting for the full load motor current.
  • Don't expect the VFD to be able to supply the full starting current. Some form of slow-speed ramp start program will be needed in the VFD.
  • Don't expect the VFD to operate the motor totally without process interruption due to overcurrent trips.

In summary, it is better to either down-size the motor (provided the process load will allow it), or up-size the VFD, its supply fuses and its supply cables to suit.

Could the output shaft be slowed down by gearing, perhaps (many loads, partuicularly fans for example, have a power draw that is proportional to the shaft speed raised to a power greater than 1.0)?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#3

Re: vfd detail

10/05/2009 7:44 AM

Yes, Yes you can. You have my permission.

Register to Reply Score 1 for Off Topic
Participant

Join Date: Oct 2009
Posts: 4
#4

Re: vfd detail

10/06/2009 4:44 PM

Is the mechanical Load less than 10HP vfd & the motor application?

Register to Reply
Active Contributor

Join Date: Jul 2009
Posts: 17
#5

Re: vfd detail

10/06/2009 9:19 PM

If the load on the motor at 100 % speed is equal to or less than 10 HP and the VFD is never required to operate in excess of 100% speed than you can connect the 15 HP motor to a 10 HP VFD.

Register to Reply
Anonymous Poster
#6

Re: vfd detail

10/08/2009 10:41 AM

Yes just don't start it

Register to Reply Score 1 for Good Answer
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); georgesturge@nl.rogers.co (1); kalliani (1); PWSlack (1); Simon Wan (1)

Previous in Forum: Using Rectifiers in Mobile Phone Chargers   Next in Forum: Blower Energy Saving

Advertisement