Blower Energy Saving

10/05/2009 1:27 AM

Hi Friends,

Presnetly iam having a blower running with a closed loop control system with the help of valve at delivery end.Based on the cooling requirement the valve will open or close automatically.

Presently iam planning to provide VFD for the system and to remove the valve.Is there is any therotical formula for calculating the corelation between the valve % opening Vs the RPM reduction of motor.Based on the RPM value reduction acheived i can able to calculate the savings.

Kindly provide me the formula for RPM Vs Valve opening.

Present value:

30 kW Motor, 54% valve opening, Present consumtion (Without VFD) - 25 kW.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Blower energy saving

10/05/2009 3:38 AM

If there is a closed-loop control system then the relationship between blower RPM and former % valve position doesn't matter. The control loop will vary the speed of the blower to achieve the required process parameter setpoint automatically, be it either flow or pressure - provided the loop has been tuned satisfactorily, that is.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Anonymous Poster
#2

Re: Blower energy saving

10/05/2009 4:20 AM

It depends on what valve you are using now. Gate/diaphragm etc. the flow rate change is not a straight line curve. ( see ME hand books). Flow varies in cube with rpm.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#3
In reply to #2

Re: Blower energy saving

10/05/2009 5:43 AM

No - flow varies linearly with rpm. Head varies as rpm2. Power varies as rpm3.

Cheers.........Codey

__________________
Give masochists a fair crack of the whip
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jul 2009
Posts: 17
#4

Re: Blower Energy Saving

10/06/2009 12:09 AM

Throtteling a valve at delivary of blower is a shear waste of energy. Instead you should take feedback of temeprature and than vary the speed of blower with help of VFD.

Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#5

Re: Blower Energy Saving

10/06/2009 1:24 AM

Adjustment with valve is not an energy efficient method. Generally fans run according to variable torque characteristic. Changing the speed of a fan will change the torque demanded by the square of the speed. By changing say the speed of the fan to 80% of the nominal value the torque demand will only be 64% of the nominal value and the power consumption is according to cube law. By reducing speed the power consumption can be reduced to about 50 % of the nominal value. What is the supply & return conditions of the air

Register to Reply
Guru

Join Date: Jun 2009
Location: Bangalore, India
Posts: 725
Good Answers: 24
#6

Re: Blower Energy Saving

10/06/2009 5:36 AM

The pressure drop across the valve is a measure of the energy lost. Depending on the type and design this can vary a lot. As the valve closes the blower sees an increase in the delivey pressure and the flow decreases along the performance curve of pressure versus flow rate for that blower. When the blower is under VFD, the output of the blower itself varies because of RPM variation. There is no simple way one can relate the two unless the manufacturer gives you a curve relating rpm and power for that blower. For full analysis youwill also need RPM versus flow rate also.

__________________
bioramani
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #6

Re: Blower Energy Saving

10/06/2009 1:07 PM

I think this is the best answer. Many people, especially those selling VFDs, bring up the cube law and use that as justification for energy savings. But they fail to mention that the cube law applies to the "valve" (damper or vanes) in the exact same way!

So the ONLY extra energy that is saved by selecting a VFD over a mechanical restriction is in eliminating the losses across the restrictive device, i.e. the "valve". Mind you, that is often significant enough to warrant the VFD, but it is NOT automatic, and in fact if the amount of time the system is running under restricted flow is very low in comparison to running at full flow, the VFD may actually COST you money in the addidtional losses in the VFD itself.

Bottom line, there is no substitute for doing a proper engineering evaluation. Many many people have been disappointed in VFD energy savings for this very reason.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#8
In reply to #7

Re: Blower Energy Saving

10/06/2009 1:51 PM

In my experience (fitting and advising on VFD use) if the valve is in operation there is normally a significant 'loss' at the valve which converts to heat, of course. So there is not the saving on valve operation you claim because of all the (turbulence) losses, mixing up the molecules rather than delivering in the desired direction. This is similar to throttling a pump where at no flow the water literally boils!!! as the wasted energy turns to heat and isn't moved along.

Electrically, the saving using VFD is normally very significant and where I have come across tables relating flow to damper / valve position (the question in the first place), the decrease in flow is more than linear i.e. half closed is less than half flow.

The true difference in operating cost depends on whether using electricity for heating is useful if not the most cost effective.

Many simulators take account of typical valve losses but this is non specific, so they will show reduced energy useage at lower flow on the valve and compare to VFD operation. Some of these are independent of VFD suppliers so are not presented as a sales vested interest. If a vendor is presenting the simplistic inverse cube law in all situations then you are right to query the accuracy of their claims but the opportunity for energy saving may still be there.

__________________
Something new every day!
Register to Reply
Active Contributor

Join Date: Jul 2009
Posts: 17
#9

Re: Blower Energy Saving

10/06/2009 6:52 PM

I had a similiar problem on a diesel generator cooling fan. What you need is a Typical daily CFM requirement for the fan based on cooling requirements. Once you determine this you can use the fan formulas to calculate the energy savings.The motor load requirements at 100 % RPM and new RPM can be used to calculate the energy savings. You may have the motor operate at several RPM' during a typical day for several hours. You can use this to estimate the savings

George

Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".