3rd Harmonics

10/05/2009 4:37 PM

Will odd harmonics (3, 5, 7, etc) flow in a 2000 kva 400 volt grounded wye generator to a delta (ungrounded 400 volt) / grounded wye (11000 volt) 2500 kva transformer? Generator has .6667 pitch. Two generators (same capacity) may be required to generate simultaneously on the same 11kv bus via separate 2500 kva delta/wye transformers (.05% Z).

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Nov 2007
Posts: 19
#1

Re: 3rd Harmonics

10/06/2009 9:06 AM

I'm no expert in harmonics, but if you have balanced loads, the currents in the generator neutral point should sum to zero. Since that's the ideal case and not reality, some current will flow on the neutral. I think since the generator is connected in grounded wye, some harmonic current will make its way to your transformer primary, where they will circulate in the delta and generate additional heat.

Better wait for a person more familiar with harmonics to weigh in on the issue.

Register to Reply
Associate

Join Date: Feb 2009
Posts: 35
#2

Re: 3rd Harmonics

10/06/2009 6:14 PM

Currents flow in connections across different potentials.

Odd harmonics are neutral displacements.

The Generator Island has no neutral connection between Generator to Delta Transformer winding, however the connections (Busbars) have different capacitive reactances & this may result in neutral displacement potential, the impedances are very high & the current therefore negligible.

The two star & grounded 11kV windings are however connected in what is commonly known as a "multiple earth" situation & current will flow in the neutrals.

Only one point of neutral earth should be made at any one time on the parallel 11kV sytem.

Register to Reply
Active Contributor

Join Date: Jul 2009
Posts: 17
#3

Re: 3rd Harmonics

10/06/2009 7:33 PM

Any harmonics on the system will be reflected in the generator supply. Because of the Delta /wye comnnection zero sequence currents will only circulate in the delta of the transformer and will not be seen by the Generator.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: 3rd Harmonics

10/07/2009 11:08 AM

Any 2/3rd (0.6667) pitch generator offers a very high zero sequence impedance. As such there will not be any zero sequence voltage generated by the generator. So, there is no question of 3rd harmonic current flowing from generator to the transformer.

Register to Reply
Commentator

Join Date: Feb 2008
Posts: 59
#5
In reply to #4

Re: 3rd Harmonics

10/07/2009 11:32 AM

I appreciate all the great comments to my post! Sometimes, "school book" technology just doesn't add up to what's out in the real world. I will now be able to set my protective relays with more confidence. Thanks all.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#6

Re: 3rd Harmonics

10/29/2009 7:21 AM

Dear Hughes,

The 3rd HARMONICS will be eliminated owing to STAR CONNECTION OF THE GENERATOR.

IN THE OLDEN DAYS DESIGN OF ALTERNATORS, THE 5th HARMONICS INTENSITY OR MAGNITUDE IS REDUCED BY SHORT PITCHING of the WINDING/COIL of the ALTERNATOR.

7th HARMONICS WILL BE PRESENT.

DHAYANANDHAN.S,

INDIA.

Register to Reply