Bonding Jumper in Cable Trays

10/09/2009 3:25 AM

We are installing powder coated MS sheet perforated
cable trays in our plant. We wanted to know how important is the electrical
continuity between the cable tray sections. Is electrical continuity more
important for power cables trays or control cable trays or both.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Bonding Jumper in cable trays

10/09/2009 6:11 AM

Why are these trays powder-coated? If it is to withstand atmospheric corrosion, then scratching through the powder coat to obtain electrical contact nullifies the corrosion resistance!

  • Why not use a different tray, such as glassfibre, that doesn't need corrosion protection?
  • What can be done about the containment problem that requires corrosion protection for equipment outside the process lines?

Electrical continuity is important for personnel protection, so the answer is "both".

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Mar 2009
Location: O'er looking the silvery Tay
Posts: 255
Good Answers: 18
#2

Re: Bonding Jumper in cable trays

10/09/2009 7:25 AM

Hi,

The benefit of the bonding of the cable tray besides providing the physical support to the cables is the prevention of power induced emfs into sensitive circuitry in close proximity to the power cables.

It is an approximation to the principle of the Faraday Cage which creates zones of minimal electromagnetic interference.

Therefore in a busy plant room environment it is permissible to put control cables on the some tray as say motor drive circuits without jeopardising the reliability of the more sensitive circuits. I prefer to use fairly wide tray 300mm+ and put the dissimilar ciruits as far apart as possible. This is over and above using cables spec'd as per manufacturers requirements.

The bonded tray should also be taken back,if possible, to a 'clean earth' terminal; this will also help to ensure that the Faraday principle is applied in practice.

It all depends on how sensitive and potentially interactive the respective circuits are thought to be.

Good luck,

Massey.

Good luck

__________________
If it ain't broke,leave it well alone .........until it comes looking for you!
Register to Reply
Active Contributor

Join Date: Dec 2008
Posts: 19
Good Answers: 2
#3

Re: Bonding Jumper in Cable Trays

10/09/2009 10:36 PM

It is absolutely essential that unless you can maintain equivalent to double insulation that your cable tray must have good reliable earth bonds beteen each and every section back to the main earth. Under our rules, all metal in an install is normally held at earth potetial. This includes such things as water pipes, pool reinforcing, building frames etc. This would depend of course on the wiring rules in your country, but in Australia, I believe that bonding must be maintained. This should be able to be done by bonding straps of a suitable size or simply by the screws or material making the joins. ELectrical continuity is of equal importance for all parts of an installation, for both safety and for reliability

Regards

Bill Pilgrim, Queensland, Austalia

Register to Reply
Anonymous Poster
#4

Re: Bonding Jumper in Cable Trays

10/14/2009 5:00 PM

Please refer to the NEC Article 392.7 metallic cable trays must be grounded and electrically continuous