Lagging and Leading Power Factors

10/15/2009 4:45 AM

Hi, happy to see u here again.

normally, the power factor below 0.85 lagging (inductive) will get penalty from an electricity company.

the question is, if my power factor is 0.5 leading (capacitive), is it good or bad? or will get penalty? my country is in Malaysia.

thanks for you gentlement/lady reply.

__________________
no pain, no gain.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#1

Re: lagging power factor will penalty, how about leading power factor?

10/15/2009 6:33 AM

How in blue blazes did you get a leading pf?

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply Score 1 for Off Topic
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#2
In reply to #1

Re: lagging power factor will penalty, how about leading power factor?

10/15/2009 6:48 AM

TVP45,

I don't know how the OP got a leading power factor, but, leading power factor is a real issue for data centres and what it does to the UPSs that are supposed to be protecting them.

This is caused by all the Switch Mode Power Supplies, usually multiples of two per server.

With all the capacitors and switching, there is usually more leading than lagging and the harmonics can get nasty if not managed properly.

We actually had to put in a PFC to generate a lag PF for when the UPSs are switched to by-passs for maintenance.

For the OP, leading PF is just as bad if not worse that a badly lagging PF due to the effects of Harmonics and while I don't know Malaysia's codes I would expect that the power suppliers would not be happy about that much of a leading PF.

Regards,
Sapper.

__________________
It's all about the Boom! - MythBusters
Register to Reply
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#6
In reply to #2

Re: lagging power factor will penalty, how about leading power factor?

10/16/2009 7:47 AM

Wow! I can see how you get leading pf, but I wouldn't have thought anyone would tolerate that long, except during switching operations when you can't help it. That must tear the &^^%$ out of the electronics??

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Jan 2009
Location: Anpara,sonebhadra,UP
Posts: 14
#3

Re: lagging power factor will penalty, how about leading power factor?

10/15/2009 7:59 AM

Laging power factor will penalty and normaly leading power factor there is no penality beacuse, due to laging power factor the efficiency of all the switch gears( starting from cables ,transformers,switch gears and the transmission line) efficiency goes down. and due to laging power PF low voltage also occures hence current also increases in the whole system. But due to leading power factor the same problems are not happens but. where there is own power House, the performance of Automatic Voltage Regulator (AVR of TG) is decreased or there may be nucence tripping occured.

Normally in long transmission line with no load/ or lesser load there is a leading in power factor. but it never happens any problem.

__________________
Binod Kumar Panda
Register to Reply Score 1 for Good Answer
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: lagging power factor will penalty, how about leading power factor?

10/15/2009 2:42 PM

the question is, if my power factor is 0.5 leading (capacitive), is it good or bad? or will get penalty? my country is in Malaysia.

That doesn't sound right at all. What sort of large capacitive loads are you running to get such a large (and rare) leading power factor?

Is this a hypothetical question or have you actually measured this on your site?

You haven't just oversized your site's power factor correction capacitor banks (or left them switched on when your site loads are off) have you?

Please provide more details as electricity penalty costs due to this excessively large leading power factor may be the least of your sites potential (and expensive) problems.

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Anonymous Poster
#5

Re: Lagging and Leading Power Factors

10/15/2009 11:46 PM

leading power factor too is not good for power system's health, because at low loads and leading power factor the flow of power reverseses and reciving end voltage become more than rated voltage.

Si try to keep it within .90 to .95

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#7

Re: Lagging and Leading Power Factors

10/16/2009 9:49 AM

The answer to regcan80's question depends on what is creating the leading power factor. In the US, some utilities will pay large customers to overexcite their synchronous motors & provide a leading power factor. This helps the utility by reducing the need for power factor correction on a large industrial circuit.

However, if a customer consistently generates a leading pf without arrangement with the utility, he may get disconnected for violating the terms of service. That is because, on more lightly loaded circuits, a leading power factor will result in a higher voltage near the source of the leading pf than that supplied by the substation. It can cause overvoltage problems in your own equipment, as well as other customers on the same feeder.

Sapper has a good point. A leading pf created by switch-mode power supplies creates some really ugly harmonics, which can and will damage electronic equipment such as PLC's, computers, televisions, generator controls, etc. The harmonics can also affect the ability of switches & circuit breakers to interrupt current, because a higher frequency arc tends to sustain itself better than a power frequency arc.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Anonymous Poster
#8

Re: Lagging and Leading Power Factors

10/18/2009 6:42 AM

Power factor indicates displacement between the Voltage and Current Vectors.

With Inductive Loads (Like Motors, Transformers, Tube light choke etc) the Current lags behind voltage and while Capacitive loads (Capacitor, Cables etc) the current leads the Voltage. So we should maintain Power factor Between 0.9 lag - Unity- 0.9 lead.

When Motor is connected to AC supply it draws Active Power(KW) and Reactive Power(KVAR). Active power does the work, while reactive power maintains the Magnetic flux in the circuit. If the reactive power is high the then power factor reduces below unity (UPF). So we should connect Capacitor equivalent to inductive reactive power and thus make it zero.

Drawbacks:

In case the power factor is less than 0.9 (lag or lead) the KVA increases, the current drawn from power source increases. The Power losses in cables increases. In case of lag the terminal voltage drops and in case of lead terminal voltage increases.

Suggestion: Maintain Power factor between 0.9 Lag and 0.9 Lead. This is better.

J.N.Karamchetti, Hyderbad.

Register to Reply Off Topic (Score 5)
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); jack of all trades (1); pandabinod (1); pwr2thepeople (1); Sapper (1); TVP45 (2)