Negative Pressure Measurement with a Non-DP Type Pressure Transmitter

10/20/2009 2:38 PM

I am gonna through in a rookie question here ..... is it possible to measure a range of -1 to 1 of pressure kg/cm2 mind u, with a steam service, and a condensate pot on the direct NON DP type pressure transmitter with impulse line. ?????

Hope i make some sense here because i have seen this on a site which has not started up yet .... any insights ???

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Negative Pressure Measurement with a Non-DP Type Pressure Transmitter

10/20/2009 9:56 PM

Here is one way to do this. Some non-DP pressure transducers are made to read in psia (pounds per square inch absolute) rather than psig (pounds per square inch gauge). I think you can get standard outputs such as 4-20 ma, or 1-5 volts DC. If you are dealing with an existing transducer (transmitter), the part number may tell which type the sensor is. Such transducers are frequently used in refrigeration applications that may run in partial vacuum.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Sep 2009
Location: United Arab Emirates, Abu Dhabi
Posts: 50
#2
In reply to #1

Re: Negative Pressure Measurement with a Non-DP Type Pressure Transmitter

10/20/2009 10:05 PM

How to calibrate it with ??? for example if the range of the transmitter is -1 to 1 kg/cm2 then what reading should it show when the vessel is empty before the startup ??

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: Negative Pressure Measurement with a Non-DP Type Pressure Transmitter

10/21/2009 1:02 AM

I will need a day or two to think more about this. Please stay tuned. (For one thing, I usually work in in British/American units rather than SI, so I will need to do some conversions.) Are you actually measuring pressure here, or are you using pressure to correlate to a liquid level measurement? I ask this because you have mentioned condensate in a steam/water system. What is the maximum pressure this system might encounter?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#4

Re: Negative Pressure Measurement with a Non-DP Type Pressure Transmitter

10/21/2009 7:40 AM

I once asked the same question (about calibration) to a Foxboro engineer. According to him, you could calibrate the transmitter at 0 to 2kg/cm² and then rerange it to -1 to +1kg/cm².

It is not practically possible to generate -1kg/cm² so there's no sense trying to generate that much vacuum.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply Score 1 for Good Answer
Register to Reply 4 comments