what is Ultimate Breaking Capacity (Icu) & Service Breaking Capacity (Ics)?

Register to Reply
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: mccb

10/21/2009 3:46 AM

Ultimate Breaking Capacity means that the MCCB can break the rated ultimate breaking current for two times and after that the MCCB is useless (It cannot even be used for carrying rated current); The duty cycle is: O-t-CO

Service Breaking Capacity means that the MCCB can break the rated service breaking current for 3 times (The Duty Cycle is: O-t-CO-t-CO) and after that it can still be used as a switch - that is, to make, carry and break normal rated currents and overload currents. However, it cannot any further be used for making or breaking any short circuit currents. So, till replacement comes, this MCCB can be used as a Switch - of course, with some back-up Short Circuit Protective Device such as a Fuse.

Standards specify that Ics can be a percentage (25% or 50% or 75% or 100%) of Icu.