what about the relationship between transformer connections and unbalanced load case? is it possible to have balanced voltages with some kinda transformer connection? or unbalanced load creates always unbalanced voltages ? my second question can we say that neutral to ground potential is related to (with a delta -grounded wye transformer) 1.Neutral wire resistance in case of an unbalanced load and 2. earthing electrode resistance in case there is a earth ground in the system?? if there happens to be both case the neutral to ground voltage is sum of these two one?
etc ..... pls give me a brief and essential explanation of the case of unbalanced loading and earth fault currents.....
jinxnao
Re: transformer connections..
10/22/2009 12:51 PM
1. The transformer at its base (if you want to call it) creates voltage as per primary. Try to visualise the equivalent circuit of the system.
Assume the input grid to be large enough to be infinite. So the unbalanced load (drawing unbalanced current in the phases) will have the unequal voltage drop through the equivalent impedances. Only way too balance these may be to go for unbalance primary voltage to compensate and that may not be practical.
2. Think again from equivalent circuit- for neutral to ground resistance to come in picture there must be a curent flow through to ground. Whether your unbalanced load will generate a current through it (and complete the circuit?)
10/22/2009 3:46 PM
I also ask you of something else, if in a solidly grounded wye system happens a ground(phase to earth) what happens to the neutral point with reference to earth? for example a bolted fault and the voltage that drops in earth electrode will cause the neutral to shift but in some books it shows no shift on vector diagrams, so pls tell me what happens to neutral if a ground fault occurs?