Another Guage question!!

10/24/2009 2:46 PM

I am running a 100 amp circuit to an electric furnace. The panel is 250 feet away from furnace. I am going to put a 125 amp service panel in the location of the furnace. The furnace has an 80 amp draw what guage wire should my electrician be using for this App.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator
Hobbies - DIY Welding - New Member Hobbies - Car Customizing - New Member

Join Date: Jun 2006
Posts: 61
Good Answers: 1
#1

Re: Another Guage question!!

10/24/2009 11:04 PM

I would completely leave that up to the electrician and the code.8

Register to Reply
Anonymous Poster
#2

Re: Another Guage question!!

10/25/2009 7:14 AM

I am away from my desk but minimum for a 125A residential panel would be #2 gauge power conductors and #6 bond cable.

But due to the fact of the sub panel with a (predetermined load of 80A) being approximatly 85m away.

I would size up to a 3/0 conductor & #3 bond. This is a signficant increase as this conductor is rated for 225A. The issue you must remember is voltage lose due to line lose (I^2 x R)..... and to correct this , increase the conductor size decreases the resistance.

You can either pipe this or find a cable that ca meet your application.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#3

Re: Another Guage question!!

10/25/2009 3:01 PM

The typical voltage drop calc is Vd = KIL/Kcmil.

Vd = allowable amount of voltage drop.
K = the constant of your conductor Ohms per mil foot (as they say in the states) de-rated by the operating temperature.
I = the normal current flow of the conductor
L = the length of the conductor to and from
Kcmil = is the cross sectional area of the conductor

In order to answer your question correctly we need to know the allowable voltage drop, the operating temperature, type of conductor material and type of insulation of the conductors.

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#4

Re: Another Guage question!!

10/28/2009 12:20 AM

Maxximus98,

You also left off a significant piece of data--the circuit voltage. Good design will limit total voltage drop to 5% of the circuit voltage, with this being allocated 2% to the service and upstream feeders and 3% to the circuit in question. The higher your system voltage, the more loss is allowed on this panel feeder. Smaller wire sizes can work at higher voltages, when they would be harmful at lower voltages.

--JMM

Register to Reply
Guru
Hobbies - HAM Radio - New Member

Join Date: Oct 2006
Location: Vancouver (not BC) Washington (not DC) US of A
Posts: 1261
Good Answers: 12
#5

Re: Another Guage question!!

10/28/2009 11:15 AM

It would really really REALLY REALLY be nice to know where you are located OP! NEC information might make no sense at all if you are located in China, or India, or Europe, or many other places.

Much Thanks

Bill

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); GRAY HAIRED OLD GOAT (1); jmueller (1); Sciesis2 (1); Swellmel (1)