Recently we have installed an 11KV overhead line for 1.25MVA transformer. the line is being tapped to an existing overhead line which is powered from the power plant switchgear. the new line is protected by using two on-load disconnector switches with fuse rated at 160A installed at the T-off(tapping point) and at the terminal pole near the transformer.
During the initial testing of the line, one surge arrestor failed causing the switchgear at the power plant to trip on earth fault without blowing the line fuses.
our client has asked to replace the fuse with another 80A to solve the problem and hence the new line fuse will blow faster and disconnect the line separately in case of earth fault or s/c without tripping the power plant switchgear.
please help and advise whether this can solve the problem??