Anonymous Poster

11KV overhead line

10/25/2009 1:33 AM

Recently we have installed an 11KV overhead line for 1.25MVA transformer. the line is being tapped to an existing overhead line which is powered from the power plant switchgear. the new line is protected by using two on-load disconnector switches with fuse rated at 160A installed at the T-off(tapping point) and at the terminal pole near the transformer.

During the initial testing of the line, one surge arrestor failed causing the switchgear at the power plant to trip on earth fault without blowing the line fuses.

our client has asked to replace the fuse with another 80A to solve the problem and hence the new line fuse will blow faster and disconnect the line separately in case of earth fault or s/c without tripping the power plant switchgear.

please help and advise whether this can solve the problem??

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: 11KV overhead line

10/25/2009 1:53 AM

11KV, 1.25MVA

I =1250/11√3 = 65.6A

Fuse rating must be 82A ie 80A is OK as client has suggested. What was the breaker setting ?

Reply Score 1 for Good Answer
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#2
In reply to #1

Re: 11KV overhead line

10/25/2009 11:44 PM

I think I =1250/(11√2) = 83.33A should be taken giving more margin for load based fluctuations and inductive serge build up. Fuse in the range of 85A looks more reasonable for fast fuse.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Reply
Active Contributor

Join Date: Nov 2008
Location: Bangalore
Posts: 22
#3

Re: 11KV overhead line

10/26/2009 12:22 AM

Surge arrester failure was due to defects in surge arrester, microscopic crack may leads to earth fault.

If your transformer loading is up to full load, then recommended fuse rating is fine, otherwise select the fuse rating as per the load pattern.

__________________
Let Noble Thoughts Comes to Us From All The Sides
Reply
Participant

Join Date: Oct 2009
Location: Bangalore
Posts: 2
#4

Re: 11KV overhead line

10/26/2009 6:46 AM

As one of the guest has rightly calculated, the fault current is 65.607A. Therefore the fuse rating of 80A is sufficient

Reply
Active Contributor

Join Date: Mar 2008
Posts: 15
Good Answers: 3
#5

Re: 11KV overhead line

10/26/2009 11:14 AM

Hi,

If you install a fuse of 80A as per your client advice, the problem will not solve.

Why?

The fuse blowing time is higher than the response time of protection relay which is operating the circuit breaker.

From where this line is coming?

Is there any 11KV circuit breaker on the new overhead line befor the starting point?

Can you post the single line diagram?

After checking the single line diagram, a better solution can suggested.

Reply
Anonymous Poster #1
#6

Re: 11KV overhead line

08/04/2014 9:44 AM

If an arrester breaks down in a phase and it is replaced, the other two arresters in the other phases should be also replaced, or they should at least be examined to determine if they have also been damaged. It is thus recommended that all three arresters be sent to the manufacturer for examination.

It bears mentioning that a MO arrester fulfils its protection function even in a case of overloading. The voltage decreases towards zero due to the fact that an earth or short circuit is produced and in this way the devices connected in parallel to the arrester are protected against excessively high voltages. The protection that takes place in an overload case, is deliberately used in some special cases as the last possibility to protect very important and expensive electrical equipment. If the aim is to overstress a rrester at a predetermined point - such as the exterior of a building - this arrester is dimensioned deliberately weaker, from the voltage point of view, than the other arresters in the installation.

Reply Off Topic (Score 5)
Reply to Forum Thread 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); ruk_eee35 (1); Shyam (1); stahir (1); vinukumar (1)

Previous in Forum: RC car circuit   Next in Forum: 3phase to 1 phase
You might be interested in: Fuse Holders, Panelboards and Switchgear

Advertisement