Removal of scale from copper pipe in a cooling tower?

10/30/2009 12:24 AM

we want to remove scale from copper pipe & pipe line of cooling tower.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: amrit

10/30/2009 12:48 AM

OK, go ahead. Where's Vader when you need him?

This may help:

Copper.org: Copper Tube, Pipe & Fittings: Technical References ...

Reply
Commentator
Hobbies - Automotive Performance - New Member

Join Date: Oct 2009
Location: Alabama
Posts: 64
Good Answers: 9
#2

Re: amrit

10/30/2009 12:56 AM

I have used Saf Acid. It has a color indicator and does a good job removing scale, by circulating a solution, or immersing the object (like a heat exchanger) in the liquid and agitating with air or mechanical means. It is user friendly, just take usual precautions. Here's the MSDS for Saf Acid Descaling Compound.

http://hazard.com/msds/f2/byf/byfbp.html

Some more info:

Common problems with copper pipes:

Soft water, or water with a pH below 7, is acidic. This acidity will dissolve copper pipe walls and cause leaks to break through. In hard water, or water with a pH above 8, scale builds up on the walls of the pipe will eventually lead to pitting, which will then lead to pinhole leaks.

Poor quality materials and poor installation can also be a cause of copper pipe leaks. A copper pipe with "cold bending" weakens the copper at the bend and water will erode the pipe material, eventually causing leaks.

Reply
Guru
Engineering Fields - Mechanical Engineering -

Join Date: Sep 2009
Posts: 1651
Good Answers: 71
#3
In reply to #2

Re: amrit

10/30/2009 3:38 AM

Not to question your answer, but could you please explain the ph of soft water?

As I understand from my chemistry class, water dissolves other substances due to the polar nature of H20 molecules. Hard water is already saturated with foreign material that precipitates out to cause scale, doesn't soft water dissolve that scale that built up? I know copper will oxidize, but is it the soft water or something else dissolved in the water that raises the ph level?

Drew

(an engineer in training, definitely not a chemist )

__________________
Question: What is going on with the American's Government? Response: Who is John Galt?
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: amrit

10/30/2009 4:07 AM

The only thing that raises the pH is dissolved alkaline species.

For the origianl poster: softened water is better for cooling tower systems, though not a prerequisite. In the end, it's all about the chemical treatment regime, which needs to be discussed with a specialist locally, for water in one location is never the same as the water in another.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Engineering Fields - Environmental Engineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: May 2007
Location: Anywhere Emperor Palpatine assigns me
Posts: 2774
Good Answers: 101
#6
In reply to #3

Re: amrit

10/30/2009 10:36 AM

Water containing sodium or potassium hydroxide has a high pH but it is still soft. Hard water contains dissolved calcium or magnesium. Hard water always has a high pH, but just because the water is soft does not mean that it has a low pH.

__________________
If only you knew the power of the Dark Side of the Force
Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#7
In reply to #2

Re: amrit

10/30/2009 3:49 PM

Some really good info in this thread. There is soft copper, comes in rolls, you bend it to the job. There is hard copper, comes in straight pipes, doesn't like to bend. Soft copper will work harden, you only get so many tries, then it snaps, or gets so hard you can't bend it easily. How is a guy to know which is best for plumbing what?

__________________
mike k
Reply
Guru
Engineering Fields - Mechanical Engineering -

Join Date: Sep 2009
Posts: 1651
Good Answers: 71
#5

Re: Removal of scale from copper pipe in a cooling tower?

10/30/2009 9:40 AM

I recall my chemistry teacher talking to us about hard water. He said that even if the pipes in your house were really bad off due to scale build up inside that installing a water softener could reverse the process and remove the scale from the pipes. He said that if it took 20 years for the hard water to deposit the scale in the pipes that once you start putting soft water in the pipes they will dissolve the scale. It didn't matter how bad it was, as long as soft water passes scale deposits it will eventually dissolve.

But he also lectured us for 20 minutes on the health benefits of farting, and never once mentioned that farts held in turn into crappy idea!

I am by no means an expert, I like PWSlack's idea of contacting a local expert.

Drew

__________________
Question: What is going on with the American's Government? Response: Who is John Galt?
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #5

Re: Removal of scale from copper pipe in a cooling tower?

11/02/2009 3:58 AM

There are health issues with consuming softened water long-term, owing to the higher-than-usual levels of sodium in the softened water. Also, the calcium level in water for consumption should be maintained above 60ppm or so for health reasons.

If the scaled-up system is not intended for consumption then softened water is not an issue. Over time, the scale may redissolve.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Mar 2009
Location: O'er looking the silvery Tay
Posts: 255
Good Answers: 18
#8

Re: Removal of scale from copper pipe in a cooling tower?

11/01/2009 7:22 AM

Hi Guest,

Good advice in general, it all depends on how desperate you are to remove the scale. If it is impeding flow then it must have reached a substantial thickness, can you comment?

Having had dealings with water treatment specialists down the years I am rather sceptical of their 'solutions' in respect of eliminating this problem. I've paid a lot of money and seen only mediocre results BUT there is one product (not for the faint hearted) which really does work. Its called 'Clensol' and is basically hydrochloric acid which converts lime scales into the chloride plus CO2; you circulate the brew for long enough to clear the thickest deposits. As a guide when the water returning to the break-tank loses its milky appearance either the pipes are clean or the acid is spent. Dip tests can confirm the residual pH. Do not use in any system which has galvaised surfaces or they will go as well.

Clearly once you've chosen a product and then got things improved you will want to keep it that way and therefore a water treatment regime to avoid the deposition of scale is essential.

I am surprised that as part of your 'Legionella' control measures that this issue has not been addressed. I would insist that the water management regime addressed this issue as you are otherwise at risk of creating the ideal environment for the proliferation of this bug.....V.nasty consequences potentially!

Anyway check out a strong acid cleaning agent but be aware of consequences for some of the metals in your system.

Regards,

Massey.

__________________
If it ain't broke,leave it well alone .........until it comes looking for you!
Reply Score 1 for Good Answer
Anonymous Poster
#10

Re: Removal of scale from copper pipe in a cooling tower?

07/22/2010 8:59 AM

The following scale removal treatment may be of interest, as we have found to be effective on copper pipe. The ECO 2000 Mineral Binding System (electronic descaler) creates an induced signal that increases the electrical charge of the positive (e.g. calcium carbonate) and negative (e.g. calcium bi-carbonate) ions. Increasing the positive and negative charges cause these molecules to bind together forming seed crystals, which lose their natural tendency to adhere to the walls of the plumbing system and machinery. In addition, these crystallized molecules fall out of suspension, refreshing the water's capacity to reabsorb calcium carbonate. This renewed capacity allows the water to methodically clean out existing scale formations. Although non-chemical water treatment has a controversial history, we've conducted a number of independent chiller audits and demonstrated energy savings of 10% - 40%. This is accomplished with non-chemical treatment in conjunction with other technologies such as high-efficiency filtration. There was also 75% water savings. In most cases, there was less than a 12 month payback. I'd be happy to email case studies if interested.

Reply
Guru
Engineering Fields - Mechanical Engineering -

Join Date: Sep 2009
Posts: 1651
Good Answers: 71
#11
In reply to #10

Re: Removal of scale from copper pipe in a cooling tower?

07/22/2010 2:22 PM

I don't want o see case studies, I want you to explain how electricity can affect the electron bond of a dissolved mineral in water. I understand how electricity can break the bond of water and hydrogen (sort of) but not how an induced signal can have anything to do with dissolved minerals.

Save the 'case studies' and testimonials for the infomercials.

Drew

__________________
Question: What is going on with the American's Government? Response: Who is John Galt?
Reply
Anonymous Poster
#12

Re: Removal of scale from copper pipe in a cooling tower?

01/16/2011 5:37 AM

Sorry! I cant help you with removal of scaling in your pipes, and as such this post may be worthless to you, but I can tell you how to prevent it. A product called descal-a-matic uses magnets to prevent scaling. The magnets are aligned in such a way as to have the molecules that cause scaling to flow right through the pipes without a problem. It has been proven to work by the US Department of Energy and NASA, and the product is actually in the WWII memorial in Washington DC. Needless to say, it will save you a lot of time and money. It is my grandfathers company, and I can back up all these claims. We also have a similar product that uses zinc, silver, and copper to eliminate bacteria, legionella, and viruses in water. If anyone is interested please email me at iahwhite88@gmail.com

Reply Off Topic (Score 6)
Reply to Forum Thread 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Dr Tom (1); Drew K (3); DVader1000 (1); lyn (1); Massey 726 (1); mike k (1); PWSlack (2)