Cable Calculations

11/04/2009 11:09 AM

Hello,

I am having problems working out the correct SWA size for an installation and was hoping someone can help.

The problem is as follows:

I will need to run a SWA cable from the consumer unit within in a house to a brink building used as a shed, total distance 10.5 Meter (cable suspended in open air). In the shed there will be a consumer unit fitted for the following items:

Ring main: 2 x twin sockets used to supply 2 x fridge freezers plus occasionally an extension lead fitted to power a strimmer

1 x light circuit: 3 x halogen security light (wattage rating unknown)

1 x light circuit: 1 x 100 Watt bulb

Secondly from the shed consumer unit there is supply require to run a water pump feature at the bottom of the garden, total distance 36 meters (cable under the ground). Again sorry I do not know the wattage rating water feature but it is only small.

Thirdly again from the shed consumer unit a supply is required to supply an outside office (cable under the ground). Distance from shed to office is 19 meters. The office has:

1 x light circuit: 3 x 50 watt pot lights

1 ring main: Used to supply two x laptops and a printer

Could someone tell me the correct size cable of the SWA between the house and shed? Also the correct size of the SWA between shed and the outside office?

The water feature has 6mm SWA already fitted.

Thanks,

Alun

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Cable Calculations

11/04/2009 11:32 AM

→ British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Nov 2009
Posts: 5
#2
In reply to #1

Re: Cable Calculations

11/04/2009 12:33 PM

I beleive that 4mm SWA between the Office and the shed will be fine but my main concern is the size of the cable between the house and the shed.

Do you think 4mm SWA will be sufficent or would it be best to increase to maybe 6mm?

Regards,

Alun

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3
In reply to #2

Re: Cable Calculations

11/04/2009 1:26 PM

We could take a guess but you really need to consult your electrical regulations applicable to your country (and state) to see what is legally required (especially when building-to-building wiring and water are involved) as requirements vary from country to country (and even state to state in some cases).

The electrical regulations will also indicate correct circuit protection and cable installation and mechanical protection (which is just as important as cable sizing in this application).

What country (and state if applicable) are you in?

__________________
jack of all trades
Register to Reply
Member

Join Date: Nov 2009
Posts: 5
#4
In reply to #3

Re: Cable Calculations

11/04/2009 3:34 PM

Im in the UK

Register to Reply
Active Contributor

Join Date: Dec 2008
Posts: 13
#5
In reply to #2

Re: Cable Calculations

11/05/2009 1:35 AM

6mm cable will do considering in future a welder may need power from shed

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #2

Re: Cable Calculations

11/05/2009 3:09 AM

→ British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: May 2009
Location: India
Posts: 38
#7

Re: Cable Calculations

11/05/2009 4:51 AM

see the details at-

http://myelectrical.com/pages/welcome.aspx

open the site and enter at TOOL option and choose your option.

Register to Reply
Power-User

Join Date: Mar 2009
Location: O'er looking the silvery Tay
Posts: 255
Good Answers: 18
#8

Re: Cable Calculations

11/05/2009 12:17 PM

Hi Alun,

Your application appears to have quite a high diversity factor and therefore the feeder to the shed will not be of any great size. I've 'guessed' your load to be in the region of 6 Amps and by using one of the convenient 'on line' sizing services, doncastercables.com and selecting a 3% volt drop you will see that for an11 metre route that the selected cable is 1.5mm2. Volt drop is calculated as 2.2V.

You can play about with this selector to your hearts content!

Be aware that you must employ a qualified Electrical contractor for external installations of this type in England or contact your local Authority and get the system tested and submitted for their approval.

For your own protection the consumer unit in the shed should include a 30mA RCD, this will then protect all the connected equipment.

Hope this is of assistance.

Massey.

__________________
If it ain't broke,leave it well alone .........until it comes looking for you!
Register to Reply
Power-User
Engineering Fields - Systems Engineering - Member for some time now, see my profile.

Join Date: Aug 2007
Location: Essex, UK
Posts: 364
Good Answers: 3
#9

Re: Cable Calculations

11/07/2009 5:49 AM

Alun,

I am trying to answer your questions and provide some advice. I am an MIEE but I am not a practising Electrician. I know, broadly,what I can do and what I am not allowed to do. UK Law. BUT SEE BELOW.

1 I assume that you have adeqaute provsion in your Main Consumer Unit to provide your external circuits. Preferably RCD protected. BUT SEE BELOW.

2 Your 3 outside cables must all carry the total load that you are providing. Theoretically this amounts to 1 Ring Main, 1 Light circuit, 1 Water pump - unspecified load, 1 light circuit,, office, 1 further ring main. A total of 2 Ring Main circuits, 2 Lioghting circuits and one unknown water pump supply.

Subject to the Water Puimp load we are talking about 2 13 A ring Main circuits nd 2 5 to 10A lighting circuits plus the water pump all to be RCD protecred the lights to be protected in case you decide to add an external light over each door!

How do you intend to keep warm in the office environment? Electrics, propane or??

3 In my book you need a Consumer unit with RCD protection for both buildings, the water pump to run from one of these consumer units. Your choice.

4 SWA outside should be 2.5mm, you can only use 1.5mm for light circuits. I am not sure why you chose to use 6mm for the water pump as this would be adequately sized for 30 plus Amps! You will need to size the fuse rating for this circuit to an adequate point .

5 The consumer unit here requires a 3 way connection, minimum, to cope with lights, power and water pump. It is always advisable, if possible to have a spare way on each consumer unit.

6 As someone else has said all external electrical connections may need to be checked by a competent engineer who can sign of Part P wiring - he will also measure all circuits. You need to check the regs. I have not put in outside circuits since the regs changed!

7 On the advice front, i would run all cables underground, if at all possible. U'ground cables ahould have a visual cover Black/Yellow tape to warn the itinerant digger! I try and cover such cables with a line of bricks - that is just me being cautious.

8 I would like to run cables to the 2 outhouses separately to avoid the problem of one issue affectimg both. That would mean 2 separate ways on your consumer unit one to driive each outhouse.

9 When running SWA between buildings I prefer to put the termination boxes inside the respective buildings and then take the internal connevction from there.

Finally I would always err on the side of the things that are yet to be thought of, I have over engineered my electrics but have lots of spare capacity - I hate using reel extension leads around the garden and have consequently fitted an external ring main for power tools, heaters, etc

I have lights round the house and am contemplating a circuit around the garden to put lights in bushes etc with a controller in one of the sheds. The garage and the two sheds are all run from the main consumer unit in the house 18 way, with a 12 way in the Garage and 3 ways in each shed.

One thing that I found out the hard way is that you should not fit RCDs in tandem as after some recent works - given to a practisibng electrician due to time constraints, I found that the system became unstable, he had taken the wiring to the garage from the RCD side of the House circuit, and the garage Consumer unit had a number of RCD circuits, moving the Garage feed to a non RCD circuit on the House Consumer Unit cured that!

Good Luck with your endeavours if you need any further advice I can supply you with direct ciontact details.

Sleepy