what is wrong here?

11/06/2009 6:57 PM

a open delta supply is supposed to supply a 173 A 480 volt resistive load, the line currents is equal to both phases currents of the open delta, but here the load power is not equal to the supply power . So what is wrong here??

__________________
jinxnao
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#1

Re: what is wrong here?

11/06/2009 7:00 PM

here load is a wye connection resistive load...

__________________
jinxnao
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: what is wrong here?

11/06/2009 7:08 PM

You are saying "the line currents is equal to both phases currents of the open delta". Is the load single phase? What exactly do you mean by "the load power is not equal to the supply power" ? Are you referring to amps or watts? How are you measuring these units?

Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#3
In reply to #2

Re: what is wrong here?

11/06/2009 7:14 PM

no no, an open delta (just two phases) supplies a wye connected resistive load, all the phase phase voltages are 480 volt, line currents are 173 A.An open delta is supposed to have three equal line currents so line currents are 173A, but when you calculate the supply power 2x 480 x173 =166 Kw and load power, 1,73x 480x173 =144 Kw , so this is just a theoretical fact, can we conclude that the phase currents is not equal to the line currents for a open delta xformers??

__________________
jinxnao
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#47
In reply to #3

Re: what is wrong here?

11/10/2009 6:30 AM

Is the primary voltage on the transformer, whose second windings go from "delta" to "open delta," kept

1. the same level in both instances ("delta" and "open delta")?

2. balanced (the same level across all three phases) in both instances?

Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#76
In reply to #3

Re: what is wrong here?

11/12/2009 2:49 AM

The situation depicted on the drawing with V-s and Amp-s is unrealistic. "Delta" "opening" like on the drawing should lead to dramatical voltage disbalance. Instead of 480V 480V 480V there would be 277V 277V 554V - I believe.

Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#77
In reply to #76

Re: what is wrong here?

11/12/2009 2:52 AM

Yuri,

Very good!

Jon

Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#79
In reply to #77

Re: what is wrong here?

11/12/2009 4:21 PM

Hi kuduk,

It appears one or two of the last of jinxnao posts have been wiped?

I have it listed but when I tried to read it the post was not there. End of story?

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#80
In reply to #79

Re: what is wrong here?

11/12/2009 5:32 PM

Interesting!!!

Jon

Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#81
In reply to #80

Re: what is wrong here?

11/12/2009 11:26 PM

Baby,

You calls it as you sees it.

Kuduk

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: what is wrong here?

11/06/2009 9:16 PM

An open delta installations provides 3 phase. If you look at your drawing you will see 3.

Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#5
In reply to #4

Re: what is wrong here?

11/07/2009 5:08 AM

I mean source phase, of course it has 3 phase but only 2 phase will supply power...

__________________
jinxnao
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#7
In reply to #5

Re: what is wrong here?

11/07/2009 6:07 AM

I cant understand, how such a paradox might be? the supply power supplied by open delta is bigger than balanced resistive load so how?? anyone can explain this dilemma ?

__________________
jinxnao
Register to Reply
Anonymous Poster
#6

Re: what is wrong here?

11/07/2009 6:07 AM

Do you mean open delta (where all the three phases will supply) or the scott connection (2 phase to 3 phase?)

Register to Reply
Anonymous Poster
#8
In reply to #6

Re: what is wrong here?

11/07/2009 6:11 AM

Now in this sketch, the load what ever way you put star or delta, the input 3 phase currents are covered as output 3 phhse currents, there are no 2 phases here - unless you are using the neutral (then it is no more open delta connection) the phasor relation will not match, and it will be just a bit complicated center tapped transformer with heavy unbalances on either side.

Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#9
In reply to #8

Re: what is wrong here?

11/07/2009 6:28 AM

I gave a link there(imageshack.us),and although the sketch seems reasonable powers are not equal u see too?? i wonder why?

__________________
jinxnao
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#10
In reply to #9

Re: what is wrong here?

11/07/2009 12:19 PM

THİS is exactly open delta, if you look at the imageshack photo u will see,I have examined all the sources on the net but i couldnt explain how can be an load unbalance between open delta and wye connected load in this picture, it is not sensible if u calculate too the loads, they dont agree, anyone there what i wanna say?

__________________
jinxnao
Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#11
In reply to #6

Re: what is wrong here?

11/07/2009 11:00 PM

Guest,

The Scott-T configuration answer seems to be the logical one since it works both ways.

Most of my experience was using them to go from in and out of phase with variable amplitude to produce 3 phase outputs for Synchros.

Jon

Register to Reply Score 1 for Good Answer
Anonymous Poster
#12

Re: what is wrong here?

11/07/2009 11:19 PM

it appears to me that you are quoting the current in two phases of the source, and the three phase load is getting the third phase from the neutral. The source is supplying the third phase through the neutral and I suspect the source is getting warm in the process. The power (less IR losses) is the same in both ends, you were neglecting the third phase power.

Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#13

Re: what is wrong here?

11/08/2009 7:07 AM

Hi jinxnao,

Are you sure the equipment is not transposing 3 phase to 2 phase? This seems very odd.

Does your system work or are you testing it because it does not work or is not reliable?

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#14
In reply to #13

Re: what is wrong here?

11/08/2009 7:29 AM

you all examined the scheme i sent??? i mean imageshack.us link..

so there is a illogical situation if u look from the point of powers, but as a source load relation the case seems logical, i cant differ them....

__________________
jinxnao
Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#16
In reply to #14

Re: what is wrong here?

11/08/2009 7:42 AM

Hi jinxnoa,

Sorry to be pushy, but is the system you have working, or have you meassured it or tested it to see how 'good' it it?

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#18
In reply to #14

Re: what is wrong here?

11/08/2009 11:08 AM

open delta is when you still got 3 windings, not just two, but two of them are not connected.

Your image does not represent an open delta

__________________
The time is ......now
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#15

Re: what is wrong here?

11/08/2009 7:41 AM
__________________
jinxnao
Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#21
In reply to #15

Re: what is wrong here?

11/08/2009 3:56 PM

Jinx,

Your link says:

Which means:

Restricted Page

You have reached your viewing limit for this book (why?).

You have to buy the book. Jon

Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#17

Re: what is wrong here?

11/08/2009 8:07 AM

Hi jinxnoa,

I went to your second link and it makes sense as described.

If the phases are as say unbalanced and do not add up to what you expect they should, are you getting a line leak to earth or ground?

Is there another piece of equipment attached that you may have forgot or perhaps even do not know about? If in the the last instance, double check for other connections which are drawing power from one of two phases.

Do you need normal single (domestic) and three phase as the example you give on your last link suggests?

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#19
In reply to #17

Re: what is wrong here?

11/08/2009 11:41 AM

thank u for u care but i think i cant make understand what i mean, there is no an exceptional case considered at that book, it just says with an open delta connection u can feed the same load if u increase ur load 1,73 times, but as u see the power supplied is not equal to the power consumed...

__________________
jinxnao
Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#20

Re: what is wrong here?

11/08/2009 1:29 PM

Hi jinxnoa,

I went to another site and list the site and the definition of 'open delta', which may help.

http://www.toolingu.com/definition-460320-34157-open-delta.html

What is the definition of open delta?

  • A transformer connection that does not complete the triangle, using only two of the three sides. An open delta is used when full power is not needed.
  • Learn more about open delta in the class "Distribution Systems 320" below

Good luck

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#22

Re: what is wrong here?

11/08/2009 4:21 PM

Jinx,

Considering that a Δ configuration can operate satisfactorily missing one winding, some power system designers choose to create a three-phase transformer bank with only two transformers, representing a Δ-Δ configuration with a missing winding in both the primary and secondary sides:

This configuration is called "V" or "Open-Δ." Of course, each of the two transformers have to be oversized to handle the same amount of power as three in a standard Δ configuration, but the overall size, weight, and cost advantages are often worth it. Bear in mind, however, that with one winding set missing from the Δ shape, this system no longer provides the fault tolerance of a normal Δ-Δ system. If one of the two transformers were to fail, the load voltage and current would definitely be affected.

So what IS wrong.

Jon

Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#36
In reply to #22

Re: what is wrong here?

11/09/2009 2:04 PM

On the diagram phase A and phase C are short circuited.

Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#37
In reply to #36

Re: what is wrong here?

11/09/2009 3:49 PM

Thanks Yuri,

That goes to show that people who create stuff for posting on serious websites need to have their material reviewed by others.

Jon

Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#39
In reply to #36

Re: what is wrong here?

11/09/2009 4:03 PM

Here is an unshorted one:

Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#23

Re: what is wrong here?

11/08/2009 4:38 PM

okey i think no one knows what i ask, what u explain is all practical things, what I ask is this;

we have a 100 Kva THREE transformer, in delta we connect and feed a 3 phase wye connected resistive load, now if one of the transformers is gone in any way, so to be able to feed the same load we need to have not "150 KVA " but 173 Kva transformers (two piece ) , this means a %15,5 overload....

now here what i ASK İS this:
why two 150 kVA is not enough ??? if we need to connect two 173 KVA transformer in open delta, so what about the 46 kva EXCESS load?? why there is an excess ???

__________________
jinxnao
Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#24
In reply to #23

Re: what is wrong here?

11/08/2009 5:48 PM

Jinxnao,

Because each of the two transformers have to be oversized to handle the same amount of power as three in a standard Δ configuration.

You may notice that I mentioned this before.

Where is your schematic?

Jon

Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#25
In reply to #24

Re: what is wrong here?

11/08/2009 6:44 PM

yes but i think u havent read the sample i gave, i ask you of the excess power, as u see there is a power in excess of what is needed by the load...

__________________
jinxnao
Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#27
In reply to #25

Re: what is wrong here?

11/08/2009 7:16 PM

Jinxnao,

The load determines the real power drawn from the source. If you could measure the heat dissipation of the load you would have an accurate power figure to work with.

If there is more power drawn from the source than used by the load it is due to the characteristics of the transformers and and how they are used to compensate for the missing power of a third phase.

Jon

Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#28
In reply to #27

Re: what is wrong here?

11/08/2009 7:28 PM

Hi kuduk,

Can you tell me whether ohms law applies here to Transformers producing power as well as to current drawn? Just to answer a question which I think should be yes! But am not sure.

With thanks

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#29
In reply to #28

Re: what is wrong here?

11/08/2009 7:58 PM

Hi Baby,

Ohms law applies to the resistive loads with no problem.

With the phases and reactive parts it becomes a little more complicated but it all comes out okay after the math wiz gets his hands on it.

Jon

Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#30
In reply to #29

Re: what is wrong here?

11/08/2009 8:23 PM

Hi kuduk,

Cheers my friend.

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#31
In reply to #30

Re: what is wrong here?

11/08/2009 8:26 PM

Baby,

Back atcha.

Jon

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#32
In reply to #31

Re: what is wrong here?

11/08/2009 9:38 PM

Hi kuduk,

No probs!

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply Off Topic (Score 5)
Anonymous Poster
#34
In reply to #28

Re: what is wrong here?

11/09/2009 7:26 AM

BB: Transformers do not produce power. They are only devices (not machines) that change the current/ voltage.

The ohmic losses do take place in the transformer- and that is decided by the so called equivalent circuits - ie the transformers when put in the circuit is treated as an ideal transformer with a series impedance (ie R & L)

And more interesting (or complicated) is that if you look from primary side it is different from when you look from secondary side. (Like V & I the impedance also is transformed)

Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#40
In reply to #34

Re: what is wrong here?

11/09/2009 4:12 PM

Hello Guest,

I appreciate your reply post to me, many thanks!

I would like to thank you for the 'ohmic' detail and bits on the workings of Transformers.

I am by no means an electrical wizard as it seems you are.

But, as a Transformer of the size mentioned is usually the receiver of the power from the Grid and or power plant, it does 'supply' or redirect it by means of windings, shunts etc. I should have made that more clear.

I was finding it hard yesterday to actually put down in an understandable way what I knew was happening, but that is my problem. I was trying to get over my meaning to the OP (Original Poster). If I was an Electrician I would have 'had it off pat', knowing the names of the internals and external parts and configurations of all and any power Transformer, but, as I am keen to point out, I am no electrician and was just trying to get over the principles of the workings of these 'two' 'for three' types of configuration of Transformers.

I thank you sincerely for your kind post.

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Active Contributor

Join Date: Oct 2009
Posts: 24
#33
In reply to #27

Re: what is wrong here?

11/09/2009 6:01 AM

The reason to oversize the 2 transformers is to make up for the missing phase.

Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#26
In reply to #23

Re: what is wrong here?

11/08/2009 7:05 PM

Hi jixnao,

I think the previous post may have answered you but I will give you what I think you mean, even if I do get it wrong! LOL!

I may be coming at this from the wrong direction, but, hey whats new.

Having read details on a couple of sites, it seems although you have very little to fall back on if something goes badly, IE you may not have enough power. These Transformers are built using several basic sizes. grouped in threes or twos, but each in that group is the same size, so you can't have a 50KVA and a 100 KVA. they are either 70 Kva x 2, or 100 Kva x 2. Just for instance, OK.This is in the open delta mode.

There is a 2x 70 Kva and you have to supply 130 Kva which, means you have 10 Kva more than enough.

I may have it wrong but does ohms Law rule still apply, when producing power, and when using it? If so you have 140 Kva capability, so this gives you 10Kva over capacity. But if ohms law applies the current actually used will be the current which has to be produced?

Is this right or not?

Bear in mind that although you may have over capacity, you have bought only two parts of a potentially three part Transformer, so you are saving on that.

If someone can tell me if this is not true, please put me right.

I am not an electrician, so forgive me for possibly screwing this up.

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Anonymous Poster
#35

Re: what is wrong here?

11/09/2009 7:41 AM

Hi jinxnao, I could not have a look in your image attached, sine my firewall stops all the peer-peer sharing sites for obvious reasons.

However as I can understand you are getting confused by the magnetic flux balances.

Try to understand this way, The energy transfer in transformer is by the flux linkages. For same energy to transfer the flux density is to be maintained.

The 3 transformers are working - a flux of Φ is generated. Now one transformer is removed.

Assuming the load is same, it demands the same power and hence same flux. This flux linkage requirement now is to be met by the rest of the two phases.

Since they are connected and on 3 phase lines, the calculations will involve the sqrt(3) factor.

If you do the analysis on this line and try to visualise from this angle you will see what is happening.

Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#38
In reply to #35

Re: what is wrong here?

11/09/2009 4:00 PM

hi guest, yes what u tell about is true but i think all the magic can be tucked into a few words nevertheles...

__________________
jinxnao
Register to Reply
Anonymous Poster
#41

Re: what is wrong here?

11/09/2009 10:21 PM

Seems to me that the quality of the questions has been getting lower and lower. One wonders why the figures don't add up.

There are 2 transformers doing the work of 3. Therefore the current/work produced through the 2 have to be equal to the 3 transformers they take the place of. That means the windings have to handle the increased current or they overheat and blow up.

The sum of the phase angle current drawn from the three transformer circuit should equal the phase current drawn from the two transformer circuit.

The only difference is the heat produced being greater for 2 transformers, hence the degrading of the ratings to overcome the extra heat produced.

And this kind of question and harrasment from a commentator.

Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#42
In reply to #41

Re: what is wrong here?

11/10/2009 5:27 AM

ı think you think that all the thing is so easy that you can say only "there occurs an overload in the windings cooz there are now only two winding instead of three.."

i think it is not so simple, yes it is very obvious that there will be an overload but i want that everybody does see the real situation here, as i said before ;
there is three 100 kva xformer, feeding a 300 kva load, now one of the windings is gone and now the power which one of the two winding should supply is not 150 but 173 kva, so i ask you all the engineers here till i get a satisfactory answer,,, WHY???

__________________
jinxnao
Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#46
In reply to #42

Re: what is wrong here?

11/10/2009 5:39 AM

Hi jinxnao,

I refer you to post 17. Please answer this.

Thank you

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#43
In reply to #41

Re: what is wrong here?

11/10/2009 5:29 AM

Hi Guest,

Are you the sender of post 42? And if so was your last line which mentioned harassment aimed at me from my request for you to join (Because you sound like a clever bloke) in post #41.?

The problem with me trying to answer a 'Guest' is, unless you are following the thread carefully it may not be obvious as to which person or 'guest' I am replying to.

I am not saying sorry because I was very careful in sending you that post and thanking you for your help with the 'ohmic' query, and asking you to join.

If you wish to complain to the management of the site about my post please do so. Here is the person to whom you should send your complaint:


And you will get an answer if you join.

Or you can just click the Report button and just say in a few words what you are complaining about, OK?

42
Re: what is wrong here? 11/10/2009 3:21 AM

Seems to me that the quality of the questions has been getting lower and lower. One wonders why the figures don't add up.

There are 2 transformers doing the work of 3. Therefore the current/work produced through the 2 have to be equal to the 3 transformers they take the place of. That means the windings have to handle the increased current or they overheat and blow up.

The sum of the phase angle current drawn from the three transformer circuit should equal the phase current drawn from the two transformer circuit.

The only difference is the heat produced being greater for 2 transformers, hence the degrading of the ratings to overcome the extra heat produced.

And this kind of question and harassment from a commentator.

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Anonymous Poster
#50
In reply to #43

Re: what is wrong here?

11/10/2009 8:27 AM

No #41 is a regular, on sabbatical as guest , and since a regular, doesn't insult the forum (some times sarcastic yes)

But I am surprised by OP, he mentioned he is an EE, but then EE is supposed to have it in the fingertips (we had studied long back the effect of fault - open circuits included- not only short circuits, inter turn faults...) on the performance. How the load and output parameters affect....

(You are excused since you mention that you are not EE).

OK Only for you (I don't know how much you are aware of the machines- In long long ago we have learnt something called something like universal theory of machines- not very universal, since these related only the Electromagnetic ones - still )

To put it very simple

Across a coil you apply a voltage - it creates magnetic flux (a bit of current) - this flux creates a back voltage (or EMF- back Electromotive Force ) This stops the current to grow. The EMF is voltage dependent.

Now you put a second coil (that may be transformer, electrical motor, alternator, DC Motor any thing having a coil)

This flux now links to the second coil and creates a voltage (EMF) across it - again the EMF is dependent on the flux passing through it.

A tiny current in primary is required to maintain the flux is the no load current (theoretically inductive, but due to the losses, ha a resistive element - eddy loss, hysteresis loss etc)

So far so good.

Now you try to draw some current from it - this current now weakens the flux and the primary (connected to source) has to pump in more flux to compensate it (by pumping in more current over and above the no load current)

Obviously more current drawn by secondary, more current is to be pumped from primary.

This is the principle by which the Electromagnetic power exchange takes place (as I said it is through the magnetic flux balance)

So in the end the secondary power (or Volt Amperes) are to be balanced by the primary VAs

If you remove a primary coil/ or a transformer, the Load demands are to be met by the remaining (of course if it is a demanding load ) else based on circumstances, she it may demand less.

These are all the aspect we have studied, in the undergraduate classes (the universal theory along with the transforms of course were in the post graduation) but that was ages ago, now I presume all these may be part of the undergraduate syllabus.

(Though as the other guest mentions, though the tone I don't approve of, I some times have my doubts, whether the children are getting overstuffed and thereby losing the understanding of the mechanism and getting bogged by the mathematics (and also important questions from exam point of view ).

Recently there were some recruitments (well it is always annual story for us). This year at least we had quite a few intelligent youngsters, but then due to recession, the top institute students have come over. Else my experience is not that good with the youngsters.

The question is never what you know or not know. I don't expect them to understand the real mechanism of a machine building (well I am more in mechanical field) When you study in college, yo put a few bearings in shaft and everything goes well on paper, and you have a running machine.

In actual life you work with constraints and they make the previous machine fail in no time. That difference do exist. But except this batch I saw the basics missing and that's what worries me.

In our school days (now in our area all are objective questions with grades ) we used to have some chunk of questions - prove by first principles....

That not only does make you to understand but makes you to pause and think similar conditions.

Give you an example -

x Kg of ice at -50C + y kg of water at 300C= ?call these students could solve

x Kg of water at 200C + y kg of steam at 1200C= ? all these students could solve

the problem was faced when

x Kg of ice at -100C was mixed with y kg of steam at 1100C

Similar quite a few episodes were seen personally and the attempt to make them understand was not very successful (I feel from the blankish faces) - these were when I was requested to help some students for exams. Still they did clear the exam, but then...

This exactly may be the reason of the quality of questions in the forum. missing foundation.

A long long post ?

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#51
In reply to #50

Re: what is wrong here?

11/10/2009 11:25 AM

Hi Guest,

I appreciate the explanation but doubt if the OP will. A trained EE should not need to ask for advice that is for sure. He is also a little shy when giving out information and details. I and others pretty much agree in our answers, but it seems the OP is still ignorant of the facts he was after................... We can only answer the question requested. If he does not phrase the question correctly, it does not need to be perfect English, but a professionally set question.

I thank you for your post, most kindly!

I still do not know to whom I am talking, but, I wanted to make it clear that I was trying to help not insult.

Do not worry about the long post!

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply Off Topic (Score 5)
Anonymous Poster
#61
In reply to #43

Re: what is wrong here?

11/10/2009 10:54 PM

My comment was not aimed at the guru, but the commentator that started the question. The questions seem to me to be comming from students that need the assignment questions answered. After the question had been answered 4 or 5 times differently saying the same thing, I think one is dense of worse when they keep hounding others to explain it.

I have seen commentators put out a question (as a question) as to how something works and those are good learning even for me. That's why I read this blog almost every day although I read every forem for articals.

Please accept my appoligy, but harrasment was not aimed at you, but the commentator that would not let well enough alone about the oversized transformer. I am not an electrician, but know some that have stated "national code" dictates that the transformer will be oversized by a certain amount. I would have remembered 1.5 times but if 1.73 is the factor, then so be it. It's a fact, national code, accepted practice that has been tried and true for years.

No, I was not 42.

Signed guest Karl Mavis

Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#62
In reply to #61

Re: what is wrong here?

11/10/2009 11:27 PM

Hi Guest Karl,

No problem, no worries.

You are not the first to have mentioned that actually.

I tried to explain to the OP that an EE standard in one country, does not necessarily mean the same as it does in another........... I think you can see where I am going here?

In reply to what you say about "National Code"............ That fact is and I am not at all sure if this will make sense, but, Surely there has to be at least a slightly higher feed to the Transformer, to allow for a certain amount, a known quantity of demand? I have several building type transformers just small one wire in and two sockets out. There cannot be the same in as out or it would not be a transformer. But these have only two 110volt out, with 220volt in. There has to be a little 'spare to allow for the likely current drawn.

Well thats how I see it. I am not an EE but can understand some basic layouts and certainly know whats going on with most single phase stuff. No expert on it though.

I still think you should join though. You are a clever person and they are always needed.

Good luck.

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#44
In reply to #41

Re: what is wrong here?

11/10/2009 5:30 AM

Hi Guest,

I just wondered whether you mean quality of questions, or quality of replies?

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#45
In reply to #44

Re: what is wrong here?

11/10/2009 5:36 AM

by the way, i am an electrical engineer , and some of u think that i ask annoying questions since they think that they do say true whenever they speak but i see that they do err; i will explain why later....

__________________
jinxnao
Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#49
In reply to #45

Re: what is wrong here?

11/10/2009 7:01 AM

Hi jinxnao,

I am pleased you posted to explain you are an Electrical Engineer, thank you!

But I have to say, as far as I can see there has been no one trying to put you down or insulting you. I realise you did not say this but I am trying to guess what the part of the post you left off was going to say.

Good luck.

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#48

Re: what is wrong here?

11/10/2009 6:52 AM

Hi jinxnao

I have just reread your OP (Original Post) shown in bold below.

What is the supply power and where is this power coming from? Is it the 'GRID' or your own generator?

Please read and check you have not missed out a word in your OP.

I may be stating the obvious, and I am sorry for that but, you have the

power supply in--->>>---Transformer--->>>---power supply out to sockets.

Would you find it easier perhaps to follow these simple steps and list the current or supplied power for each? This is only a suggestion, OK?

This is not intended to be any kind of insult, OK.

a open delta supply is supposed to supply a 173 A 480 volt resistive load, the line currents is equal to both phases currents of the open delta, but here the load power is not equal to the supply power . So what is wrong here??

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#52
In reply to #48

Re: what is wrong here?

11/10/2009 6:08 PM

hello friends, i think i repeated my question so many times that it reached a perfection grudgingly:)

i think this is very difficult to explain ( i am sure that u can explain if u can understand) such a simple question to understand :(i dont claim that the answer is so easy to understand in first looking..)

There is a delta- wye transformer of which primary consists of three 100 kva single phase and this supplies a three phase wye pure resistive load ok?? is there a question? nooo ?? okey lets go on...

now if one of the phases (here single phase transformers) is (burnt gone whatever u say) now these two one will go on supplying the same load okey? is there a problem?

no?? lets go on again:)

now on the contrary of the simple urging of our intuitions ; one of these two phases will not get loaded 150 kva per phase but 173 kva okey? is there any objection?

is there real engineers who care about my question?? if u can stop talking about some funny and needless theories which have nothing to do my question as form and contents i plead you to focus on these simple datas so as to answer my question simply in the same manner, any way dear Engineers;

now the simple question is this ; why an excess power of 23 kva is absorbed ???

i have repeated this question so many times that this is the last one, i think u dont focus on the question enough! otherwise i am sure u will make the answer slip instantly lol....

__________________
jinxnao
Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#60
In reply to #52

Re: what is wrong here?

11/10/2009 8:00 PM

Hi jinxnao,

Just a few words to congratulate you on your comic jokey writing.

At first I really thought you were joking from the start. I wonder if you are still joking, as you seem to say near the end of your post that you actually do understand what is happening. I just wonder what your motives are now. I for one do not think this is a game. And I think if you do know the answer to your own request, then you should tell us so others who may be looking for that answer.

Good luck.

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply Score 1 for Good Answer
Anonymous Poster
#63
In reply to #60

Re: what is wrong here?

11/11/2009 4:55 AM

Do you remember there was a similar thread some 6-7 months back from cnpower ? this thread is also gooin on same line - it was something to do with geometry- I don't remember - but it has moved along exactly same lines, and the end answer was not very interesting.

BTW: Cnpower also is not visible- or he is like me? let us wait if he is, he is going to explode over this

Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#53

Re: what is wrong here?

11/10/2009 6:17 PM

also it is a big ill-luck for us to be not able to see the link afterwards, there explains many in detailed way, if u cant answer still , i will make an explanation simply, i just want to see what u will say, if it is still not obvious for u i will ignore all the written here and forget about it...

__________________
jinxnao
Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#54
In reply to #53

Re: what is wrong here?

11/10/2009 6:20 PM

Jinx,

If you knew trhe answer why did you ask?

Jon

Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#56
In reply to #54

Re: what is wrong here?

11/10/2009 6:28 PM

i did not knew, but i think i know now and i will explain after your answers...

__________________
jinxnao
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#57
In reply to #56

Re: what is wrong here?

11/10/2009 6:29 PM

i am still so amazed about the amount of the turmoil which this op have created...

__________________
jinxnao
Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#59
In reply to #57

Re: what is wrong here?

11/10/2009 7:00 PM

Jinx,

It seems that some folks think CR4 Electrical Engineering is more fun with the added turmoil.

Jon

Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#55

Re: what is wrong here?

11/10/2009 6:27 PM

note: i name the secondary of a three phase transformer, which is connected delta in first case and ofterwards its one phase is gone as supply and the three phase wye resistance block as load ,as u can see from the imageshack.us link, i had thought the image was explanatory enough...

__________________
jinxnao
Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#58
In reply to #55

Re: what is wrong here?

11/10/2009 6:56 PM

Jinx,

The open delta transformer configuration has big power losses when it supplies a load intended for the missing aid of a 3rd phase.

Jon

Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#64
In reply to #58

Re: what is wrong here?

11/11/2009 6:18 AM

no this is not the answer, i am waiting still someone to answer correctly........

__________________
jinxnao
Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#65
In reply to #64

Re: what is wrong here?

11/11/2009 12:29 PM

Jinx,

You may notice that I am just throwing stuff out to keep the thread alive while we all wait for the climactic answer.

Did you like the drawing where the transformers had shorts across the supply lines? Talk about excess power draw! Pow!! Only one person mentioned it.

And what's with the Turkish website you put in one of your posts with a page that doesn't open? That was funny! Like you were trying to sell that guy's book so folks could read the restricted page you were directing them to. There are better books.

I can't wait to see what you come up with next.

Jon

Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#66
In reply to #65

Re: what is wrong here?

11/11/2009 4:02 PM

first of all the web site i have given was not a turkish website but it was google books portal, i think u did not read the link even superficially dear guru:)

secondly what i mean with excess power should be clear to u if u are guru really but u dont seem to be so till now! excess power is also seen on the first link i gave, i think u can at least see through this drawing and find me right in just a 30 second, just P = 1.73xI.V not so difficult u must try a bit...

and finally dear guru, i think to be able to find an answer to problems here is not so simple what a pity, if u want to learn the real answer u should search at least 100 book if necessary, if u cant let me know and i will tell u the secret of all...

(it is really amazing that i couldnt get the answer since 10 days and u are trying to make fun of me still, i think u should give up waiting for my next bombs and instead try to focus on the question...)

__________________
jinxnao
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#67
In reply to #66

Re: what is wrong here?

11/11/2009 4:20 PM

also dear guru this link works here, if it doesnt condescend to work there in your country i cant do anything...

__________________
jinxnao
Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#69
In reply to #67

Re: what is wrong here?

11/11/2009 5:01 PM

Jin,

If you leave "tr" out of the address it would have worked here too. You could have responded to the reported problem and tried to fix it for the people who you wish to entertain.

It is still Turkish Google but the page does open for viewing.

The page does explain what I have alluded to previously but why would I want to spoil it for the rest by revealing your secret.

Kuduk

Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#68
In reply to #66

Re: what is wrong here?

11/11/2009 4:42 PM

Jinx,

"first of all the web site i have given was not a turkish website but it was google books portal, i think u did not read the link even superficially dear guru:)"

I clicked on your big long http: link and copied the webpage you offered from Google and put it in here <http : / / books . google . com. tr> is certainly a Turkish language Google Books portal.

"secondly what i mean with excess power should be clear to u"

"Excess power" is the nature of the broken third phase called configuration called open delta.

if u are guru really but u dont seem to be so till now!

Guru simply means I have gone beyond 500 entries in CR4. I don't think it has much meaning beyond that.

(WARNING: If your implication is intended to insult it is a violation of the terms of service on CR4.)

"excess power is also seen on the first link i gave, i think u can at least see through this drawing and find me right in just a 30 second, just P = 1.73xI.V not so difficult u must try a bit..."

You mathematics works good in the DC world but not in the ac and multiphase transformer invironment. That is what is wrong.

"and finally dear guru, i think to be able to find an answer to problems here is not so simple what a pity, if u want to learn the real answer u should search at least 100 book if necessary, if u cant let me know and i will tell u the secret of all...

Ah yes, key words: Want and can't. Asumptions.

"The Secret". Sounds like a good title for another Dan Brown fiction novel.

(it is really amazing that i couldnt get the answer since 10 days and u are trying to make fun of me still, i think u should give up waiting for my next bombs and instead try to focus on the question...)

Most of the more serious minds had already looked over your stuff and passed on it without making a comment here. Most of them don't like stuff that looks like it is from a homework assignment.

Jon

Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#70

Re: what is wrong here?

11/11/2009 5:12 PM

dear guru!

if u think that the extension tr is enough for a google books portal to be a turkish site so i trust in u, and i must thank google managers for feeling themselves as turks, i love them all..

excess power is not supposed to be the match for the extra load taken charge of by the two transformers from the missing transformer but the 23 kva (from my example)which has no match with regard to the load part, i think u havent understood still what i mean lol...

i think guru means in reality much more than ur definition...

in my example and question the load side is pure resistive and u dont need cos phi so i think u should evaluate the cases more meticiliously....

yes assumptions since i cant talk about realities and magnificience regarding u....

yes i think more of them thought that they had 100 books to read to be able to give an decent answer to my question and give up in advance , but what makes me amazed is that u still go on wrong way...

NOTE : İ DONT MEAN İNSULT ANYONE, İf u felt so i am sorry...

__________________
jinxnao
Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#71
In reply to #70

Re: what is wrong here?

11/11/2009 6:19 PM

Jin,

Google is cool. Make you feel at home wherever you are.

Sometimes it is just a cultural thing that makes people seem like they insult. No worry.

Excess power is what the two remaining transformers must be able to handle to make up for the missing third transformer to satisfy the load. That's a lot of heat for those remaining two.

Guru is not MY definition. It is what happens to you in CR4 when they exceed 500 posts. It is a title related to participation.

Participant, Active contributer, Associate, Commentator, Power User, Guru etc. You may notice that Baby has 4031 posts and 70 good answers and is a Guru. Another person has more than 10000 posts and 210 good aswers and is a Guru. Another person has almost 600 posts and no good answers and is a Guru. Nothing much to do with the good answers or smarts.

Kuduk

Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#72
In reply to #70

Re: what is wrong here?

11/11/2009 8:47 PM

Baby,

You speak from my heart.

Kuduk

Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#74
In reply to #72

Re: what is wrong here?

11/11/2009 10:58 PM

Hi kuduk,

You say I speak from your heart!........... I like it!!!

I also speak from mine and one or two other as well me thinks?

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#75
In reply to #74

Re: what is wrong here?

11/11/2009 11:12 PM
Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#73
In reply to #70

Re: what is wrong here?

11/11/2009 10:56 PM

Hi Guest,

you can still give me a BA if you want!

I may not have explained the detail I found very well, and these were details from the links given from jinxnao. If I could understand the 'principle' why could not he/she? I know not.

Excuse me Guest but allow me to say this.

Jinxnao, did you notice that there is not exactly a preponderance of Gurus fighting to answer your request, did you?............... Yes I heard a faint noise, maybe jinxnao? Why do you think there is hardly anyone responding, (apart from being not as stupid as me and so not wanting to waste there time), it is because this subject has run its course........................

I see jinxnao has 100 posts. I would bet must are on the thread!

I just said in the post you replied to what most people glancing at this thread are thinking. Jinxnao obviously thinks a lot of himself............... Nuff said!

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#78
In reply to #73

Re: what is wrong here?

11/12/2009 2:51 PM

Hi jinxnao,

From what you said in a few of your posts, it seems you have realised the answer?

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply Off Topic (Score 5)
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#82
In reply to #78

Re: what is wrong here?

11/13/2009 8:26 AM

i am responsible for my deeds as a human being, so i accept as virtue to be able to apologize for my nuisant writings if they really exist, so i am sory for everybody if this thread is out of order because of me(hey guys kududkweller and baby you are my chaps ok? are we friends from now on?)...

secondly, i dont claim that i am superior to u , this questions tickles my mind, what i could found is just a few scrabbling on the net

i think the real answer is this;there will be a 30 degree phase shift between phase voltage and current and even if the load is resistive the power factor will be % 86 and this explains why there is a 23 kva excess load ok? this is all i know about the real answer this is for sure...

thank u for all ur strugglings...

__________________
jinxnao
Register to Reply Off Topic (Score 5)
Anonymous Poster
#83
In reply to #82

Re: what is wrong here?

11/13/2009 8:41 AM

That explains Load VA not equal to Supply VA but the question still remains

Why "load power is not equal to the supply power ."

Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#84
In reply to #83

Re: what is wrong here?

11/13/2009 9:14 AM

Hi Guest,

I like it!

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#85
In reply to #82

Re: what is wrong here?

11/13/2009 9:25 AM

Hi jinxnao,

There is no need to say sorry. The thing which was making me and I think kuduk as well was you appeared to say you knew the answer but would wait and see?...........

I got notification of a post you sent yesterday or the day before, and when I went to read it the post was not there. That usually mean admin have pulled it from the thread for some reason. I do not know why it was removed because I was not able to view it. That all.

The last couple of posts have been me pulling your leg, and I get that done to me as well, it is part of what this community does, just as they would do in real life. I noticed you have been making jokes as well, so there is no problem, unless you have a personal problem with admin. Which if you do I do not want to know the details.

As you say we are friends and will be. No problems!

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#86
In reply to #82

Re: what is wrong here?

11/13/2009 10:36 AM

Jinx,

See post 87 from Babybear. I agree with those statements.

Kuduk

Register to Reply Off Topic (Score 5)
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#87
In reply to #86

Re: what is wrong here?

11/13/2009 6:59 PM

okey, i am joking much of the time, i just wanted to tease u up, pls dont get angry with me ,i never hide my knowledge from this society, i like this cr4 very much, you are all my friends, thank u for ur helps...

__________________
jinxnao
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#88
In reply to #87

Re: what is wrong here?

11/13/2009 11:28 PM

Jinxnao,

Thanks for clarifying that.

There is appropriate teasing and inappropriate teasing. I am glad that you are learning the difference.

Kuduk

Register to Reply Off Topic (Score 5)
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#89
In reply to #88

Re: what is wrong here?

11/14/2009 11:15 AM

i dont need learning such a concept, it has to do with the people in front of u, so i esteem friendships always, if u cant bear such teasings i wont ever do i promise, it is all the same for me, i think i will play the stern guy from now on:) good lucks.

__________________
jinxnao
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#90
In reply to #89

Re: what is wrong here?

11/14/2009 1:32 PM

Jinxnao,

Somewhere between is good.

Kuduk

Register to Reply Off Topic (Score 5)
Anonymous Poster
#91
In reply to #89

Re: what is wrong here?

11/15/2009 12:51 AM

We all like light banter no don't try to be a tough guy, if you aren't .

The difference here was simply (may be our misinterpretation) of being unable to differentiate between a quiz and a serious discussion.

(So somewhere try to lighten the atmosphere and make clear about this aspect)

Quizzes are always welcome.

Register to Reply Off Topic (Score 5)
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#92

Re: what is wrong here?

11/15/2009 5:46 AM

of course banter! so i think hence this affair is done, i thank all my friends for trying to help me, see u in the other threads...

__________________
jinxnao
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - Not so new Member Popular Science - Weaponology - New Member Hobbies - Fishing - New Member, old hobby.

Join Date: Nov 2008
Location: Windhoek, Namibia, South west africa
Posts: 410
Good Answers: 23
#93
In reply to #92

Re: what is wrong here?

02/19/2010 8:29 AM

Tee Hee Hee! all that made for an entertaining thread. Stuff like this adds the appropriate amount of 'intellectual' sparring to keep it fun as well, thanks all.

__________________
tHe days of good inglisH haz wented.
Register to Reply
Register to Reply 93 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (11); babybear (23); jinxnao (27); joseph sithole (1); kudukdweller9 (24); Leonf (1); nikolay (1); wareagle (2); Yuri B. (3)

Previous in Forum: replacing motor of an old rc car.   Next in Forum: Electrical Harmonics

Advertisement