Reduction in current capacity by half of any 2 pole MCB

11/15/2009 11:10 AM

Halo everybody

Is it possible to reduce the current capacity by half of any 2 pole MCB by connecting phase from one pole, opposite side & it's adjascent side looped, and again taking out the same phase from previous pole's adjascent pole. Will this reduce current capacity of any 2 pole MCB by half. i.e. That means , by this connection

Current capacity of any 2 pole 2Amp MCB reduces to 1Amp

Current capacity of any 4 pole 2Amp MCB reduces to 2Amp

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Reduction in current capacity by half of any 2 pole MCB

11/15/2009 12:43 PM

No.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Reduction in current capacity by half of any 2 pole MCB

11/15/2009 2:01 PM

No! Paralleling MCBs to share current is NOT an acceptable way of providing protection even if you can mechanically join the two mechanisms together to get them to both trip simultaneously.

Please, PLEASE read your local electrical standards and regulations as they are quite clear on this point!

Buy the correct sized MCBs for your application, they are not expensive.

__________________
jack of all trades
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Reduction in current capacity by half of any 2 pole MCB

11/16/2009 2:55 AM

Are you meaning to connect the MCB Poles in series? From what you have described, I understand that you are connecting the poles in series. (Incoming-Pole No. 1 Top Terminal-Pole No.1 Bottom Terminal-Pole No.2 Bottom Terminal-Pole No2 Top Terminal-Outgoing). In series connection how would the current rating come down?

But, one advantage definitely will be there. That of arc quenching. Inseries each pole contact would only see half the voltage and thus half the arc strength. So, damages to contacts due to arc will be reduced comparatively. IN DC applications, we do connect the MCB poles in series.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Reduction in current capacity by half of any 2 pole MCB

11/16/2009 3:06 AM

No. All it does is provide two chances of tripping on the same overcurrent instead of one.

If the breaker rating is too high, substitute a breaker with the correct rating.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#5

Re: Reduction in current capacity by half of any 2 pole MCB

11/17/2009 7:53 AM

From yr question,i can understand that u are connecting the 2 pole breaker in series.Thesame current flows thru the two breakers thus providing u with what i call double protection.In this case,it is not double protection,but single protection bcos d two breakers are nt seperate,but are linked together at d switch handle as a unit protection device,so thesame fault current trips the 2pole or 4pole breaker,whichever is applicable.

NO CURRENT IS REDUCED,but for advantage of arc quenching,tests could be carried out with extreme care to determine the issue of half voltage and half arc strength as stated by electricalexpert.

If u want to reduce yr current capacity,pls calculate and buy d appropriate single,double,tripple or four pole MCB.Be careful in making electrical connections.

Patrick Whowha

Reply
Anonymous Poster
#6

Re: Reduction in current capacity by half of any 2 pole MCB

11/17/2009 1:30 PM

Thanx all of you for your precious info. & making me confident about my doubt/guess about the same i.e. the answer is NO.

Actually this information was given to us VERY CONFIDENTLY (& tried technically by him as he says) by our the most superior/highest authority in our company that you might guess we couldn't challenge him for the same.

Reply
Reply to Forum Thread 6 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); electricalexpert65 (1); jack of all trades (1); JohnDG (1); PWSlack (1)