I got a compressor 220VAC, 50/60HZ, 5.575KW 3PH
rated FL/LR Current 20/82 A
Primary 208 VAC, 60A Breaker with disconect and fuse protect, in fact this line fed or on 2 units with the same rating current.
What it is happening from the disconnect to the unit has a 10/4 so cord with tuist lock connenctor and start melted one leg on each unit
Re: Compressor and 60A Circuit Breaker
11/17/2009 5:42 PM
guest; are you starting compressor with head pressure on it , or loose connection at plug/receptacle pinky
07/18/2023 3:42 AM
Consult a qualified local Electrician.
Reply Score 1 for Off Topic
07/18/2023 2:03 PM
You need to increase wire size to probably a #6....the circuit breaker has to be sized for the wire...