Maximum Run of EMT Conduit

11/18/2009 4:24 PM

I am involved in PV design and currently we are running a long feeder inside EMT conduit that will be exposed to temperature changes.

I did my calculation regarding temperature expansion but I would like to ask is there any recommendation for a maximum lenght of EMT conduit between temperature expansion fittings?

Thanks

__________________
Rafal Ptak, Electrical Designer/Engineer
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Maximum Run of EMT Conduit

11/18/2009 6:05 PM

I'd think the limiting factor in EMT length would't be the temperature extremes, which you don't mention, but the length of the delivery truck.

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#2

Re: Maximum Run of EMT Conduit

11/18/2009 6:46 PM

Its not important. The joints, splices, bends, and sags will take up any expansion that occures.

Register to Reply
Participant

Join Date: Nov 2009
Location: Alameda, CA
Posts: 4
#3
In reply to #2

Re: Maximum Run of EMT Conduit

11/18/2009 7:04 PM

This is what I think as well, but...

One of the first/biggest fires of rooftop PV system in USA (I guess at Target store in Fresno, CA) was caused by such issue. The couplings were not tightened enough/equally by installers and conduit popped out of the couplings, cut isolation and created short circuit. If there would be an expansion coupling it could prevent this situation.

So, installing an expansion coupling makes sense, there are different sizes available but I am just trying to get to some literature/code or manufacturer recommendation if there is any…

__________________
Rafal Ptak, Electrical Designer/Engineer
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #3

Re: Maximum Run of EMT Conduit

11/18/2009 9:54 PM

Interesting question. I haven't heard of expansion joints in electrical conduit, but I sure have seen some pulled-apart joints from various causes!

If there are substantial lengths turned 90° at each end of the long run, and if the clips along the run allow some sliding, you might be okay without any other special provisions.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2008
Location: East Tenneesse, USA
Posts: 685
Good Answers: 46
#5

Re: Maximum Run of EMT Conduit

11/18/2009 10:52 PM

Could use some water tight flexible conduit every so often in a loop to break up long runs. Not sure what electrical codes would say about it. "I need to find my code book"

Charles

__________________
Metal is the material, The forge is life, The anvil and hammer bring character and soul.
Register to Reply
Associate

Join Date: Jan 2007
Location: Raleigh, N.C.
Posts: 49
Good Answers: 1
#6

Re: Maximum Run of EMT Conduit

11/19/2009 7:32 AM

There are requirements for compensation of thermal effects on EMT, as well as other metal conduits. If you have a copy of the 2008 NEC, look at 300.7(B). Specifically take note of the footnote. If you don't have a copy, let me know and I'll provide the info.

__________________
"You can fool some of the people all of the time and you can even fool all the people some of the time, but you can never fool all the people all of the time." Abe Lincoln
Register to Reply
Participant

Join Date: Nov 2009
Location: Alameda, CA
Posts: 4
#8
In reply to #6

Re: Maximum Run of EMT Conduit

11/19/2009 11:28 AM

Thanks for referring me to the NEC. This is what I was looking for to. Of course I do have a copy on 2008 NEC.

So, it seems that I just need to do the math, but I agree with the next post that the 200' to 400' would be the thumb of rules.

__________________
Rafal Ptak, Electrical Designer/Engineer
Register to Reply
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#7

Re: Maximum Run of EMT Conduit

11/19/2009 7:35 AM

They do make expansion couplings for EMT. The UPC number is 0403* (* = 1 for 3/4, 2 for 1", Etc). They should be used any time an expansion joint occurs in the structure where the EMT is rigidly secured to. If the EMT is floating such as hanging from the structure by all-thread, you do not have to install expansion couplings.

Rule of thumb pulling distances in EMT vary from 200' to 400'. The real determining factor is the tensile strenght of the conductors being pulled. For that you need to calculate the friction of the conduit vs the weight and friction of the conductor. Look up a conductor manufacture site on the web they should have the calculations available. Okanite used to have a really nice section on calculations.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Nov 2009
Location: Alameda, CA
Posts: 4
#9
In reply to #7

Re: Maximum Run of EMT Conduit

11/19/2009 11:56 AM

I definitely agree with you comments. After doing the math 200' – 400' sounds about right, but in order to get better distribution of the tension I would prefer to use more couplings with small expansion instead of large one. Other words, the shorter the better.

__________________
Rafal Ptak, Electrical Designer/Engineer
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#10

Re: Maximum Run of EMT Conduit

11/19/2009 10:06 PM

I like Tornado's answer. If you put a 90 degree bend, even two in a straight run the conduit can stretch and shrink back and forth and not pull the conduit out of the connectors.

I see this on steam pipes for the same reason. Have you ever noticed large steam pipes doing an inchworm hump? Betcha it is to allow expansion and contraction without stressing welds. I was looking at the power plant nearby, and the pipes never seem to go straight to their destination, always do a bend or two on the way for no apparent reason.

__________________
mike k
Register to Reply
Power-User
Hobbies - Target Shooting - New Member Hobbies - Model Rocketry - New Member Safety - ESD - New Member

Join Date: Jan 2008
Location: here
Posts: 109
Good Answers: 5
#11

Re: Maximum Run of EMT Conduit

11/23/2009 12:13 AM

Here is a copy of the Target fire and what went wrong, Sorry so long. http://www.green-fire.org/content/targetrooftop.pdf

Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bfmickl (1); EV1guy2004 (1); GRAY HAIRED OLD GOAT (1); lyn (1); metalSmiths (1); mike k (1); rptak (3); tcmtech (1); Tornado (1)

Previous in Forum: Surface Heater Suppliers   Next in Forum: Surface Coating for Copper Busbar

Advertisement