Scalable Chilled Water Plant?

11/23/2009 10:23 AM

Has anyone ever designed a 'scalable' chilled water plant? Here's my reason for the question.

I am currently in DD for a local regional museum. Their criteria has required us to provide tight environmental controls for one gallery of the museum that must be kept on an emergency power source. This gallery, divided into 4 separate rooms, amounts to approximately 20% of the total load for the building. In order to down size the gen set to something that the museum can afford, I've been asked to investigate some way of keeping the gallery environmental requirments for power down.

These emergency power requirements were just established. Currently, I'm using a single 300 ton chiller / cooling tower, with a primary secondary pumping arrangement. The gallery in question is served by a single constant volume AHU with a dessicant wheel, and 4 zones of humidifiers to keep the humidity tolerances in the required range. The system is fine, until we need to go on emergency power. Then I have to start up a 300 Ton chiller, 300 ton tower, approx. 50 hp worth of humidifiers, and 60 hp worth of pumps and ahu fans.

I'm now looking at some sort of system, possibly with the use of modular chillers, to where I only need to run one of the modules when the space is on emergency power, thus cutting back on the required start up and running current coming from the generator. I plan on using VFD's on all motors to minimize the start up power required, and to match the load to the equipment.

Can anyone provide me with any 'lessons learned' from an existing similar system, or point me in the proper direction to some information regarding the design of such a system.

Many thanks!

Twangy....

Register to Reply
Pathfinder Tags: Chiller museum
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Scalable Chilled water plant?

11/23/2009 10:58 AM

If I understand your system correctly, it seems that you could add a 60-ton chiller, tower, and pump. The refrigerant should be a separate circuit from the existing chiller(s), but the chilled water would be in parallel. You might need some actuated valves to shut off chilled water to other zones than the critical gallery, during times of power outage.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Nov 2007
Posts: 18
Good Answers: 1
#2
In reply to #1

Re: Scalable Chilled water plant?

11/23/2009 11:11 AM

I think you've got it. I don't have the room for an additional tower, thus the use of VFD's on everything, along with the 'modular' typ of chillers. I'm hoping to be able to turn down the tower fan to help match the condenser load from a single chiller.

Looking at two scenarious right now.

1) build a chiller 'plant' with 5 modular chillers of 60 tons each, running a separate secondary to the critical gallery ahu, with control valves shutting off the other secondary loop. When on Emergency power, only a single chiller would operate depending on the load. I'd try to maintain the primary chiller loop at a constant temp, and only run the critical zone secondary loop on emerg. power., letting the chiller controls stage additional chillers on or off as required by the load.

2) Use a separate chiller and loop on the critical gallery ahu. This approach would add pumps and make the Condenser water loop a parallel loop to the tower.

The tower is a BAC chiller, and i've been told by the rep that we could run the fan on a VFD along with the bypass to drop the capacity to match a single smaller chiller. I'm always 'suspicious' of rep information and was looking for some confirmation.

Register to Reply
Commentator

Join Date: Jul 2009
Posts: 63
#3
In reply to #2

Re: Scalable Chilled water plant?

11/23/2009 5:03 PM

Id suggest forget the rep and speak to the techies at BAC.I would always check with the drive manufacturer when connecting existing kit to a VFD,due to subtle differences in motor characteristics and their suitability.

With regard to the capacity reduction of the system when emergency gens are connected I cannot grasp the revised system you are suggesting,a drawing or P&ID would be useful.

My initial suggestion would be to confirm the following:

1.Available power from emergency source,this will dictate whether d/x may be a more suitable option......another coil into an AHU isnt costly,especially when its only a fraction of the overall duty+You will benefit from more Kw cooling per Kw input.Refrigerant selection also important,R410A or similar good option at Te of 0C to 10C.Consider also integrating Copeland Digital scrolls,VFD control as standard,this technology can also be fitted in chillers as well as d/x.Aim for the maximum COP achievable and work back to confirm cooling capacity that can be provided.

2.What are the ambient extremes,is free cooling a likely option? Fitted on chillers it can save alot of energy.

3.Is the system providing ventilation as well as conditioning? If so,re-cycling during emergencies will also cut down the load considerably + reduce the humidity fluctuations from external air.

It all depends on how far you want to take it..........

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Nov 2007
Posts: 18
Good Answers: 1
#4
In reply to #3

Re: Scalable Chilled water plant?

11/23/2009 10:32 PM

My initial suggestion would be to confirm the following:

1.Available power from emergency source,this will dictate whether d/x may be a more suitable option......another coil into an AHU isnt costly,especially when its only a fraction of the overall duty+You will benefit from more Kw cooling per Kw input.Refrigerant selection also important,R410A or similar good option at Te of 0C to 10C.Consider also integrating Copeland Digital scrolls,VFD control as standard,this technology can also be fitted in chillers as well as d/x.Aim for the maximum COP achievable and work back to confirm cooling capacity that can be provided.

... I hadn't thought of adding a DX coil to the unit, but that is a possibility. Not sure where I can put the condensing unit.... but Thanks!

.... We'll be using the system power demand to help size the GenSet. So we've got whatever we need. Just trying to contain the size of the Gen Set.

2.What are the ambient extremes,is free cooling a likely option? Fitted on chillers it can save alot of energy.

....The museum is more interested in maintaining the contractually required criteria than in energy savings, at least in this one wing.

3.Is the system providing ventilation as well as conditioning? If so,re-cycling during emergencies will also cut down the load considerably + reduce the humidity fluctuations from external air.

.... Normally yes, but this is a 'Smithsonian" exhibit space, i.e. very tight humidity and temperature control. we're going with minimum required outside air at all times, with no o/a during emergency operation... 100% recycling.

thanks leon.. more to 'chew' on in my head!

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Scalable Chilled Water Plant?

11/23/2009 11:44 PM

I suspect that the tower on which the VFD is contemplated uses a centrifugal fan. Unless the VFD incorporates braking, slowing down the frequency may make the fan "overdrive" the VFD. Also, the motor will need to be inverter rated in the first place. In any case, be sure that the motor and VFD are properly matched.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

_Leon_ (1); Tornado (2); Twangmaster (2)

Previous in Forum: VS4 Pumps - Shaft Length Limitation   Next in Forum: What is the English Word for This Machining Activity?
You might be interested in: Emergency Call Systems, Emergency Stop Switches

Advertisement